How to update a modified Xenta 5/7/9xx XIF file in LonMaker

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to update a modified Xenta 5/7/9xx XIF file in LonMaker
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2099 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to update a modified Xenta 5/7/9xx XIF file in LonMaker

Picard Product_Support
‎2018-09-07 07:08 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-17 11:09 AM

Issue

Error when commissioning a Xenta 5/7/9xx indicates an out-dated or mismatched XIF (device template).

Program IDs do not match. There is an incorrect or out-of-date program version. (Subsystem: NS, #38) on a Xenta 5/7/9xx LON device

NS38.png

 

If this error occurs on any other device besides a Xenta 5/7/9xx, please reference Program IDs do not match. There is an incorrect or out-of-date program version. (Subsystem: NS, #38) for resolution.

Product Line

TAC Vista

Environment

  • LonMaker 3.X
  • Xenta Servers
  • Xenta 511, 527, 701, 711, 721, 731, 913
  • XBuilder

Cause

The Program ID inside the controller does not match the Program ID specified for that controller inside the LNS environment resulting in a Program ID mismatch. Program IDs are unique identifiers created for use in device templates and are based on the XIF.

Resolution

Resolve the Program ID mismatch by making the Program ID in the controller match that in the LNS environment.

  1. Download the controller using XBuilder. Send project to target.
  2. Generate the latest XIF for the XBuilder project.
    • In the Network Pane, right-click on the root (TAC_Xenta_511 in this example)
    • Select Generate XIF File
      Generate XIF.png

       

  3. Find the new XIF that has been generated in the XBuilder Project directory: targetimage\configdb\lon\TAC_Xenta_511.xif
    • Default XBuilder locations
      • XBuilder 5.1.3 and prior:
        C:\Documents and Settings\All Users\Application Data\TAC\TAC XBuilder Projects
      • XBuilder 5.1.4 and later:
        C:\Documents and Settings\All Users\Application Data\Schneider Electric\TAC XBuilder Projects
      • Windows 7:
        C:\ProgramData\Schneider Electric\TAC XBuilder Projects
    • A good practice is to view details of the folder to confirm the time stamp of the XIF file. It should match the time that the file was generated in XBuilder.
    • This file will be selected later, so another good practice is to rename the file to something more meaningful -- the name does not matter. "WebServer.xif" may be easier to find later and confirm it is the correct file.
    • It is also perfectly acceptable to move this file to a new location -- Device Files of your overall project, for example. That can also help in later steps, especially if the default XBuilder Project location is used.
  4. In LonMaker, right-click on the device, and choose "Replace" (Not in System Plug-In)
    Replace Device Wizard.png

     

  5. Browse to the newly generated XIF file. Give the new device template a name. Select Finish.
  6. Commission the Xenta 5/7/9xx into the network. The Program IDs now match and the error is cleared.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3975
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now