Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Satchwell MicroNet
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,825
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "satchwell micronet"

View in: "Building Automation Knowledge Base" | Community

252 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • 2
    • 3
    • 4
    • …
    • 13
  • Next »
Label: "Satchwell MicroNet" Show all articles

Xenta Server webpage logs out waiting for Java

Issue After successfully logged into Xenta Server web pages, java loading icon will be displayed as shown below. However, after a while it will automatically log the user out as shown below. Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Servers 5.1.6 (Xenta 511, Xenta 515, Xenta 527, Xenta 701, Xenta 711, Xenta 721, Xenta 731, Xenta 913) Java 1.6 update 29 Note: This behavior may happen on other Xenta Server versions with different Java versions. Please refer to the Cause section for the reason. Cause Vista may not support the newest Java versions. For Vista 5.1.6, the recommended Java version is Java 1.6 update 20. Please refer to Recommended Java version for TAC Vista 5 for recommended Java version details. Resolution Go to Start > Settings > Control Panel > Add or Remove Programs. Find Java application (in this example is Java(TM) 6 Update 29), and select “Remove”. Reload the Xenta Server webpage, will find the Java icon will not be displayed this time. Instead, “Download Java” request link will be displayed. Click on the link and download the supported version of Java. The issue should be solved after the recommended version of Java is installed.
View full article
Picard Product_Support
‎2018-09-10 05:00 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:16 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
2343 Views

Verifying Serial Port Communications with loopback test.

Issue Verifying the Com Port on a PC is working properly by using "Loopback" test in Terminal Emulator. Product Line Andover Continuum, Field Devices, Other, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Hyperterminal RS-232 serial port Cause The following test writes to the serial port and reads from the same port. This will verify the Full duplex operation of the RS-232 communication. Resolution Short the TX and RX pins of the cable (pins 2 and 3) following the pinouts below. Gender is determined by pin type.                Male DB9 (Left) and Female DB9 (right)   Launch Hyperterminal by selecting Start>>Programs>>Accessories>>Hyperterminal. If you do not have Hyperterminal, please read Hyperterminal on Microsoft Windows Operating Systems. If you are asked if you would like to install a modem, select No. Choose any icon and name the session, select "OK". In the next Pop-Up menu, choose direct to COMx (where x is the number of the COM Port you are testing.) Set the flow control setting to None. Leave the other settings to default settings, select "OK" Select File » Properties from the menu bar, select the Settings tab, and then push the ASCII Setup button. Check the option for Echo typed characters locally. Type something. If you see double characters the serial port is setup correctly and is functional. The display is showing characters that are sent out and what is read in. The Emulator will send and display the TX and immediately read and display  RX. If you see exactly what you are typing, you have a communication issue. which could be: Bad Com Port Bad cables Pins not shorted correctly If you are out of physical ports to try, use a USB Serial Port converter. If you are using a USB, use Reassigning a USB Serial Adaptor to a desired COM port for instructions of assigning Com to another port.
View full article
Picard Product_Support
‎2018-09-10 05:10 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:15 PM

Labels:
  • Andover Continuum
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
2867 Views

"Error code 401 - Unauthorized" in XBuilder

Issue When trying to download a 5/7/9xx in XBuilder you get "Error code 401 - Unauthorized". Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Server Xenta 511, 527, 555, 701, 711, 721, 731, 913 XBuilder Cause Password in XBuilder project does not match the password in the Xenta device. Resolution Select the 5/7/9xx in the Network panel The password is in the right hand panel of XBuilder under the TCP/IP Settings section. Change this to match the password in the 5/7/9xx. If the password is not known then refer to Receive a temporary session password for a Xenta 5/7/9xx if the password has been lost.
View full article
Picard Product_Support
‎2018-09-06 11:44 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:37 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
2264 Views

How to configure the Windows Time Service to use an internal clock

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue Time synchronisation is often an issue on large BMS installations. A central time signal is normally required to make sure all controllers, terminals or workstations have the correct time. If there is no internet connection available then the time has to be synchronised from a central source. Product Line Andover Continuum, EcoStruxure Building Operation, Satchwell MicroNet, Satchwell Sigma, TAC Vista Environment Sigma Continuum Vista SmartStruxure Windows XP Windows 7 Server 2003 Server 2008 R2 Cause No internet connection available to synchronise the system time. Resolution Important The methods below contain steps that tell you how to modify the registry. However, serious problems might occur if you modify the registry incorrectly. Therefore, make sure that you follow these steps carefully. For added protection, back up the registry before you modify it. Then, you can restore the registry if a problem occurs. If using Windows XP, please use the following link - http://support.microsoft.com/kb/314054 If using Server or Windows 7 OS, please use the following link - http://support.microsoft.com/kb/816042 This has been tested for Time updates to an AS by simply using the PC IP address as the primary NTP Time Server. If the firewall is turned on you also need to make sure UDP 123 is open. Please note that Windows will add a dispersion to the time that may cause issues with time synchronization, please see Automation Servers ignore time sync message sent from Windows NTP server that uses local internal clock for details.
View full article
Picard Product_Support
‎2018-09-11 01:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:56 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
2329 Views

Understanding the FILE part of a XIF file

Issue When having issues with a specific NCI (SCPT or UCPT) in a XIF file it can be hard to understand the FILE definition in the XIF file in order to troubleshoot a given issue For information regarding NCI's that are not part of a FILE definition, refer to Understanding the NVVAL part of a XIF file Product Line EcoStruxure Building Operation, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC Vista Environment LonWorks XIF Cause The FILE definition can be somewhat cryptic - here is an example   FILE template 0 2 "1.1;" "2,23.24.25.26.27.28.29.30.31.32.33.34.35.36.37.41.42.43.45.46,0\x80,49,2;" "1,1,0\x80,60,12;" "1,1,0\x80,52,2;" "2,0.2.3.5.6.7.8.9.10.16.17.18.19.20.21,0\x80,48,2;" "1,0,0\x80,17,31;" "1,1,0\x80,34,2;" "1,1,0\x80,23,2;" "1,1,0\xA4,169,1;" "1,1,4\x80,3,8;" "1,1,4\x80,5,17;" "1,1,3\x80,1,2;" "1,1,4\x80,4,9;" "1,1,4\xA4,13,1;" "1,1,4\xA4,14,1;" "1,1,4\xA4,15,1;" "1,1,4\xA4,16,1;" "1,1,4\xA4,17,1;" "1,1,4\x80,18,1;" "1,1,0\x80,42,2;" "1,1,0\x80,36,2;" "1,1,0\x80,193,2;" "1,1,4\x80,8,2;" "1,0,3\x80,2,2;" "1,0,0\x84,165,1;" "1,0,0\xA4,166,1;" "1,1,6\xA4,2,8;" FILE value 1 1 116 0x0B, 0xB8, 0x09, 0x1D, 0x09, 0xFB, 0x0B, 0x80, 0x08, 0x77, 0x07, 0x98, 0x06, 0x13, 0x00, 0x02, 0x23, 0x28, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x78, 0x7F, 0xFF, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x80, 0x80, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x01, 0x00, 0x00, 0x00, 0x00, 0x00, 0xFF, 0xFF, 0x7F, 0xFF, 0x7F, 0xFF, 0x13, 0x88, 0x00, 0x00, 0x02, 0x0B, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00 Resolution The FILE section describes the configuration variables (or SCPT's and UCPT's) for a device. Here is an explanation of the various parts of the FILE section.
View full article
Picard Product_Support
‎2018-09-11 03:06 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:46 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC Vista
2854 Views

VisiSat version 2.1 Build 196 service pack 1

Issue VisiSat 2.1 Build 196 Service Pack 1 provides the five following corrections: In the ARCnet debug Excel spreadsheet, the property editor can now be run. (Defect 1633) Exporting points to MNView or XBuilder, now allow up to 32 characters for the name and up to 50 characters for the description. (Defect 1706) In StruxureWare Building Operation WorkStation, MicroNet Interfaces can no longer be exported/imported. All MicroNet engineering should be done in VisiSat first and then imported into StruxureWare. (Defect 1765) Newly created blank points lists can now be saved without production an error message. (Defect 1784) Exports to StruxureWare no longer produce Memory leaks. (Defect 1808) Product Line EcoStruxure Building Operation, Satchwell MicroNet Environment VisiSat 2.1 build 196 StruxureWare Building Operation Version 1.4 Onwards Cause Correction of five known defects. Resolution This Service Pack should only be added to VisiSat 2.1.196 Note: When installed, the VisiSat 2.1 Build version/build number increases to 2.1.200. (due to one of the files in 'Program Files'). VisiSat will still show as Build 2.1.196 in Control Panel - Programs - Programs and Features - Uninstall or change program. Installing VisiSat Service Pack 1 =============================== Shutdown VisiSat and the VisiSat-Server. Run "VisiSat 2.1.196 Service Pack 1.exe". Extract to VisiSat installation root drive. (or extract to another location and move the Satchwell folder, created when extracted to the root of the C: drive). To the question 'Would you like to replace the existing file', select 'Yes to All' Restart VisiSat. Download VisiSat 2.1 Build 196 Service Pack 1. See VisiSat version 2.1 Build 196 service pack 2 where information on VisiSat 2.1 Build 196 Service Pack 2 can be found and the service pack downloaded.
View full article
Picard Product_Support
‎2018-09-11 07:50 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:07 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell MicroNet
2708 Views

Can a LON PCC-10 PCMCIA card work in a laptop with an express card slot?

Issue Laptops are now being supplied with an express card slot instead of a PCMCIA card slot. The LON PCC-10 cards are PCMCIA cards and will not fit in an express card slot. Product Line Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC Vista Environment Using the Lon PCC-10 Card in a laptop that has an express card slot and not a PCMCIA card slot. Cause The latest laptops are being supplied with express card slots. The option of a PCMCIA card slot is becoming harder to specify. Resolution Although the slot in the laptop appears to be the same as a PCMCIA card, the Express card slot differs in many ways to the PCMCIA slot the PCC-10 card requires. Express card slot to PCMCIA card converters are available but not all support the PCC-10 card. Some express card to PCMCIA card converters only support 32 bit PCMCIA cards. The PCC-10 is a 16 bit card. Basic testing has been carried out on an express card to PCMCIA card converter with a LON PCC10 card from Roalan Ltd. You can purchase the EC1632 converter direct from Roalan Ltd. website by credit card through the Sagepay secure web server. Alternatively, you can phone your order to +44 (0)1202 861512 or fax it to +44 (0)1202 891454. The product is plug and play on Windows Vista and Windows 7 with a downloadable utility for Windows XP. (Only required on some computers. It was not required on the Dell E6420 when testing the card.) You can download the utility here: EC1632.zip, or from Roalan's website. Further information on the converter is available on Roalan's website. You may also download the EC1632 Installation Guide. The card should be plug and play. If your PCC-10 card does not work when using the express card converter, check the PCC-10 card installation using under the control panel. If the card is not working correctly review The Echelon LonTalk PCC-10 PCMCIA Network Adapter will not work with a Dell E6410 laptop. If you need to order a LON PCC10,PCMCIA card, they are available through Schneider Electric specification number WPA-LON-2.
View full article
Picard Product_Support
‎2018-09-10 12:13 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:04 PM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC Vista
3406 Views

Echelon Node Utility with Loytec NIC-USB Network Interface

Issue Echelon Node Utility with Loytec NIC-USB Network Interface Product Line EcoStruxure Building Operation, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC Vista Environment Microsoft Windows 7 32-bit Echelon Node Utility 2.04 Echelon OpenLDV 4.0 Loytec NIC-USB network interface Loytec NIC driver version 4.1.3 Cause There is a need to run Echelon Node Utility using Loytec network interfaces. Resolution The easiest way to accomplish this, is to use the NodeUtil Launcher. This program scans the registry for known interfaces. It was created by an active Community member. * Do take note Schneider Electric Product Support does not provide support for the NodeUtil Launcher - for support please write the developer of the tool. Below are two methods to manually achieve this if you don't want to use the tool. Here are 2 methods to run Node Utility using Loytec NIC-USB network interface. Method 1 involves accessing the Windows registry to check the path name of the Loytec network interface. We are not modifying any entries in the registry but as always, we should be careful when we access the Windows registry. Using Windows registry incorrectly can cause serious problems that may require you to reinstall Windows. Method 2 will configure the Loytec NIC-USB to use LON1. If you have used an Echelon LonWorks interface as LON1, you will need to detach it before you can use this method. Method 1 Run Loytec LConfig tool. With the Loytec NIC-USB network interface connected, go to the 'USB' tab and test the connectivity Run Windows registry editor (Start > Run > regedit). Navigate to the path HKEY_LOCAL_MACHINE\SOFTWARE\LonWorks\DeviceDrivers. The interfaces will be shown here. Look for the interface with '_LDV'. Run Windows Command Prompt and navigate to the Node Utility software directory (whichever directory you have put Node Utility) and run NodeUtil using the command nodeutil -D"". See example below. Method 2 Run Loytec LConfig tool. With the Loytec NIC-USB network interface connected, go to the 'USB' tab and test the connectivity. Click on the 'Advanced' button. Check the option 'LON1 Support for device' and select the appropriate device in the drop down list. You will need to reboot the computer for this to take effect. Once the computer has restarted, run Windows Command Prompt and navigate to the Node Utility software directory (whichever directory you have put Node Utility) and run NodeUtil. Node Utility should now run.
View full article
Picard Product_Support
‎2018-09-11 03:23 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 08:56 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC Vista
3084 Views

MicroNet 50 series controller MLi's and Data sheets

Issue To assist locating data sheets if you do not have access to The Exchange or other Schneider Electric storage areas Product Line Satchwell MicroNet Environment MicroNet 50 series Controllers Micronet Touchscreens Micronet LCD SLink sensor Cause To assist customers that do not have access to our internet or partner websites. Resolution Updated June 2019 The MicroNet 50 series range MN350, 450, 550, 650 LCD and Touchscreen have been withdrawn from sale. The IAC 420, 600 and Touchscreen have now also been withdrawn from sale. No direct replacement is offered. Further information on these changes can be found in PA-00495 - Notice of Withdrawal - Satchwell Sigma and PA-00528 - End of Commercialization - Satchwell Sigma. ---------------------------------------------------------------------------------------------------------------------------------------------------------- Links below to download: MLi and data sheets for MicroNet LCD Displays MLi and data sheets for MicroNet Touch Screens User Guide for MicroNet Touch Screen User Guide MLi and data sheets for S-Link Sensors Data sheets for MN 50 Series MicroNet Manager Interfaces Mli for MN Trunking kits (MN-TK) MLi for MN Wall Mounting Kits (MN-DK) MLis for Plug-In Cards MLi and data sheets for Satchwell MicroNet MN350 Controllers MLi and data sheets for Satchwell MicroNet MN450 Controllers MLi and data sheets for Satchwell MicroNet MN550 Controllers MLi and data sheets for Satchwell MicroNet MN650 Controllers Download all of the above (file size 12.0 MB) Data sheets for MicroNet 100 series controllers ETC can be downloaded from MicroNet 100 series controller MLi's and Data sheets.
View full article
Picard Product_Support
‎2018-09-07 11:42 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:50 PM

Labels:
  • Satchwell MicroNet
4281 Views

Webstation graphics not working after Java updated to Java 7 update 51

Issue After updating the computers Java version to Java 7 update 51, graphics are not displayed when using Webstation. Then a security warning is displayed. Missing required Permissions manifest attribute in main jar: http://xxx.xxx.xxx.xxx:/com.SE.webstation.Main/applet/applet-1.4.1.68.jar If you don't see the error above, but just get a blank window, please refer to Webstation graphics not working after updating to Java 7 Update 65. Product Line EcoStruxure Building Operation, Satchwell MicroNet, TAC Vista Environment Webstation Cause From Java 7 Update 51 and onwards, Java has enhanced the security model to make user system less vulnerable to the external exploits. The new version of Java does not allow users to run the applications that are not signed (Unsigned), Self signed (not signed by trusted authority) and the applications that are missing permission attributes. Risks involved in running each kind of applications: Unsigned applications An application without a certificate (i.e. unsigned apps), or missing application Name and Publisher information are blocked by default. Running this kind of application is potentially unsafe and present higher level of risk. Self signed application (Certificate not from trusted authority) An application with self-signed certificate is blocked by default. Applications of this type present the highest level of risk because publisher is not identified and the application may be granted access to personal data on your computer. Jar file missing Permission Attribute Permissions Attribute verifies that the application requests the permission level that developer specified. If this attribute is not present, it might be possible for an attacker to exploit a user by re-deploying an application that is signed with original certificate and running the application at a different privilege level. Resolution As a workaround, the user can use Exception Site list feature to run the applications blocked by security settings. By adding the URL of the blocked application to the Exception Site list allows it to run with some warnings. Steps to Add URL to the Exception Site list: In control panel go to the Java Control Panel Click on the Security tab Click on the Edit Site List button Enter your site details (This example http://www.SBO-Site.com) Click the Add in the Exception Site List window. Select continue Repeat the process until all the sites AS/ES have been added. Then select OK to complete and OK on the next window to exit the Java control panel. Next time you use Webstation to access the AS/ES you will be asked if you want to run the application. Tick the box so this is not displayed again. Then select Run. The graphics should now be displayed. You will need to repeat this process on any computer you which to use Webstation on.
View full article
Picard Product_Support
‎2018-09-11 05:22 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:40 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell MicroNet
  • TAC Vista
3147 Views

Recommended Java version for TAC Vista 5

Issue TAC Xenta Server webpage does not work smoothly. A typical example is when you try to change a value. The small dialog that should pop up to change a value might pop up and immediately disappear. Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment TAC Xenta Severs Xenta 511, 527, 701, 711, 721, 731, 913 TAC Vista 5 Webstation Cause Using unsupported version of Java may cause various issues. For example, Xenta server webpage does not display smoothly, time schedule does not show up or can not be edited, etc. Resolution Below is the Java compatibility matrix of TAC Vista 5.   5.1.9 5.1.8 5.1.7 5.1.6 5.1.5 5.1.4 5.1.3 5.1.2 5.1.1 5.1.0 5.0.3 5.0.2 5.0.1 5.0.0 Java 1.5 update 06               X X X X X X X Java 1.6 update 11           X X               Java 1.6 update 17            X 1                 Java 1.6 update 20 X X X X X                   Java 1.7 update 51 X                           1  TAC Xenta Server 5XX/7XX/913 SP1. Log into The Exchange and then click here to download the full Vista Compatibility Matrix. To uninstall an unsupported version of Java and install the supported version, refer to Xenta Server webpage automatically logs out while waiting for Java to load.
View full article
Picard Product_Support
‎2018-09-07 03:09 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:05 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
3116 Views

Xenta Server (Xenta 5/7/913) serial cable guide

Issue If the Xenta Server IP address is unknown or lost, how can the user retrieve or reset the IP address? Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Servers Xenta 511, 527, 555, 701, 711, 721, 731, 913 Cause Once the Xenta Server IP address is lost, the user has to use a serial connection cable to connect the Xenta Server to the HyperTerminal in order to retrieve the IP address. The serial cable is a RS-232 to RJ10 cable which can be purchase from Schneider Electric order entry (Part number: 00730920). For some reason, if the cable need to be home made, please follow the steps below to connect correct pins. Note: some third party IP search/scan software can be used to search all IP addresses in a range. User can also use this type of software to retrieve Xenta Server’s IP addresses. Resolution Xenta Server serial cable guide: Connect RJ10 pin 1 to RS232 pin 2. Connect RJ10 pin 2 to RS232 pin 3. Connect RJ10 pin 4 to RS232 pin 5. Connect RS232 pin 1, 6, 4 together. Refer to IP setup for a Xenta server (Xenta 5/7/9xx) through serial communication for how to set up HyperTerminal in order to retrieve/setup Xenta Server IP address.
View full article
Picard Product_Support
‎2018-09-10 05:15 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:38 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
4398 Views

"There is a problem with this website's security certificate." when logging in to Xenta web server using Internet Explorer 8

Issue When logging into Xenta server using Internet Explorer 8 a certificate error is displayed as displayed below: When logging into the web server of a Xenta controller using Internet Explorer 8 an error message is shown stating that there is a problem with the website's security certificate. The error reads: There is a problem with this website's security certificate. The security certificate presented by this website was issued for a different website's address. Security certificate problems may indicate an attempt to fool you or intercept any data you send to the server. We recommend that you close this webpage and do not continue to this website. Click here to close this webpage. Continue to this website (not recommended). More information How to install a self signed certificate. Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Internet Explorer 8 Xenta 511, Xenta 527, Xenta 555, Xenta 701, Xenta 711, Xenta 721, Xenta 731, Xenta 913 SSL Cause The default certificate in the Xenta web server is a self-signed certificate. Since the certificate is not issued by a recognized Certificate Authority the web browser (in this case Internet Explorer 😎 cannot validate the authenticity of the certificate and suggests that the user not continue to the website each time the user tries to access it. Resolution Click "Continue to Website" to continue to the screen shown below. Click on "Certificate Error" which is found on the right side of the address bar at the top. A dialog similar to the one below will open. Click "View certificates". The certificate dialog will appear. Click "Install Certificate." The Certificate Import Wizard will open. Click Next. Allow Windows to automatically select where to store the certificate. Proceed to Finish the Certificate Import Wizard. A notification appears indicating that the certificate was imported successfully. Restart Internet Explorer for the change to take effect. Note: The certificate will need to be installed in each client computer that accesses the Xenta server but once this complete it does not need to be done again. The exception to this is if the web address of the Xenta server is changed or if Internet Explorer is uninstalled then reinstalled. The alternative is that a certificate issued by a Certificate Authority (CA) may be purchased. These certificates are pre-installed into the web browser and will automatically prevent certificate errors from occurring on all client computers that access the web server. Note that these can be quite expensive and unless the Xenta web server is being hosted on the internet they are not necessary. See "This Connection is Untrusted" certificate error when logging in to a Xenta Server using Firefox for information on installing certificates into Firefox. Update: Starting in September 2014, all major browsers will be disabling 1024-bit roots within their trusted roots stores. Any SSL certificates chained to a 1024-bit root will no longer work on any browsers that takes this action or one that relies on another's root store (the self-signed certificate is 1024-bit). This means that you will still get the security warning even if you have installed the self-signed certificate.
View full article
Picard Product_Support
‎2018-09-07 10:56 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:28 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
3510 Views

Xenta Server "Run" light is solid red with no communication via Ethernet

Issue Xenta Server reports it is in FAILSAFE mode without shorting out terminals 9 and 10. After connecting via HyperTerminal, restarting and trying to reset the IP address, the screen continues to scroll back to dsh/> Xenta Server has gone offline and can not connect directly to it using Ethernet. The Run light is flashing Green on first start up but then reverts to red and the LON light also flashes red. During boot up it pauses and reports an error (via HyperTerminal) in loading the RAM disk.  IP Address is set to 172.22.1.5 and can not change it.  Not able to load any firmware into the device – error received. "Error: Could not create remote directory." Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Server 527, 511, 555 Xenta Server 701, 721, 731 Cause Unknown corruption of the Xenta Server hard drive / flash drive, possibly due to electrical noise. Resolution To attempt to recover this device, try to format the device’s flash drive. To achieve this you can follow these steps using HyperTerminal or an equivalent application: (For further assistance with connecting to Xenta Servers and HyperTerminal refer to Connecting a serial cable to a Xenta 5/7/9xx controller).   Login and type the command FORMAT.  (May require device to be placed physically into the fail-safe mode by shorting terminals 9 and 10). The format command can take up to 3 minutes to complete but you should see the confirmation through HyperTerminal while this is occurring. If you have placed the device into Fail-safe mode, remove the link on terminal 9 & 10. Restart the device, by either cycling the power or typing the command RESTART through HyperTerminal. Set the IP address and IP settings (command SETIP). Install the latest firmware. You can download the latest firmware from The Exchange Extranet; ensure that you use the correct version since there various versions for the Xenta Servers. Run the firmware download to the device. During the download you may receive an error regarding "Failure to get the hardware version from the target device…", select OK Continue the installation The download will then occur, it will take some time and may appear that the software is not responding but this is normal. Be patient and if you don’t receive any errors then all should be ok. The device should now restart, after a 1-2 minute window the “RUN” LED should be a solid green. If after following these procedures, the device is still not responding as expected please send into Repairs via your normal repair process.
View full article
Picard Product_Support
‎2018-09-07 12:34 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 05:58 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
4045 Views

"Could not create remote directory" or "Failed to establish connection with the target device" when upgrading/downgrading a Xenta 5/7/9xx

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Error: "Could not create remote directory" or "Failed to establish connection with the target device" when trying to upgrade/downgrade a Xenta 5/7/9xx controller     Product Line TAC INET, TAC Vista, Satchwell MicroNet Environment Xenta Servers Xenta 511, 527, 527-NPR, 555, 701, 711, 721, 731, 913 XBuilder Cause This error can be caused by any of the following reasons: Trying to downgrade a Hardware version 2.x Xenta Server device to System Program version 2.10 or older Internet Options are configured to use a proxy server IP communication is not properly established due to incorrect IP settings, a bad cable or a faulty device The controller is 5.1.8 or lower and Microsoft KB 2661254 or KB 2661254-V2 is installed on the PC. In this upgrade Microsoft has changed the criteria for the certificate Key. Service packs are available on the extranet to correct this issue. Download blocked because of other Windows updates SSL 2 and 3 is not activated Resolution First, establish that the System Program that you are attempting to load is compatible with hardware version of the device. The older HW 1 versions can be upgraded to System Program 5.1.2 or older. Only system program versions 2.2.0 and newer can be loaded into devices that are hardware version 2.X. Hardware Version System Program 1.0 5.1.2 or older 2.X 2.2.0 or newer 3.X 5.1.6 SP1 or newer Note: Hardware version 1 devices are not labeled as HW 1 since only one version of hardware existed at the time. Hardware devices can be identified by the lack of any hardware version printed on the Neuron ID sticker. Note: If running the firmware update software, ensure you are running as an administrator. Next, check to verify that IP communications are configured properly and are functional: Check the IP address defined in XBuilder Verify a good connection to the IP port of the controller (10Base-T port on the far right) with a crossover cable. If that is all good, then a reformat of the controller may be necessary. Connect via Hyperterminal to the unit and at the dsh> prompt type format and press enter command . This will recreate the directory structure of the controller and allow you to attempt the upgrade/downgrade again. Finally, verify that the Internet Options are not configured to use a proxy server or, if they are, temporarily change them as follows: To temporarily change this setting follow these steps: In Internet Explorer select the Tools Menu and select Internet Options. Or select Internet Options from your Control Panel. Go to the Connections tab. Click the LAN settings button. Uncheck the Use a proxy server for your LAN box. Click Ok in the LAN settings window and the Internet Options window. Complete the System Program download. Return to the Internet Options window and re-check the Use a proxy server for your LAN box in the LAN Settings found in the Connections tab. Another Matrix explaining the compatibility of each with Vista versions can be found in Xenta-Server-firmware-versus-Vista-Server-versions If you have the Xenta FW 5.1.8 or lower and KB 2661254 or KB 2661254-V2 were installed during a Windows Update you will need install the service packs. These new service pack builds have been released and are available on the extranet. See TPA-VSTA-12-0028.00 - TAC Xenta Servers, Not Possible to Download Firmware for more info. Another issue has been reported to support relating to the bit length of the Xenta server boot certificate. The Xenta server installer uses a 512 bit key length of the boot certificate, and Windows in some instances can be configured for a 1024 bit length certificate. If the issue still exists after removing the above mentioned Windows Updates, or if you are getting this error and the Windows Updates are not on your machine. Download the attached tool, Allow Weak Certificates.zip, and execute the file, chose "Allow Weak Certificates", and "Update".   Here is what the tool set: Windows Registry Editor Version 5.00 [HKEY_LOCAL_MACHINE\SOFTWARE\Microsoft\Cryptography\OID\EncodingType 0\CertDllCreateCertificateChainEngine\Config] "EnableWeakSignatureFlags"=dword:00000002 "minRSAPubKeyBitLength"=dword:00000200 If taking the preceding steps fails to resolve the issue then see the following articles for additional steps that can be taken: Xenta Server "Run" light is solid red, with no communication via Ethernet,  Fail to upgrade the TAC Xenta Server system software (firmware)  An unexpected error occurred while downloading using a Xenta Server
View full article
Picard Product_Support
‎2018-12-02 04:25 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 05:54 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
3730 Views

Setting the IP address of a Xenta 5/7/9xx through serial communication

Issue How to set the IP address of a Xenta 5/7/9xx through serial communication. Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Servers Xenta 511, 527, 555, 701, 711, 721, 731, 913 Cause If the IP address of a Xenta 5/7/9xx is not known initially, then no configuration can be done through the IP interface. The IP address must be set through serial communication. Resolution IP setup for a Xenta server (Xenta 5/7/9xx) through serial communication for step-by-step instructions for this process.
View full article
Picard Product_Support
‎2018-09-07 02:25 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:50 AM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
4012 Views

Where can VisiSat software and license be purchased and what Version/Build is supplied

Issue (2019-06) The current version supplied is 2.1 build 196 Also available for VisiSat 2.1 Build 196: Service pack 1 (Build 200) Service pack 2 (Build 201) Product Line Satchwell MicroNet Environment MicroNet controller programming IAC controller programming MMC controller programming.  VisiSat MN-VSCORE Cause Different versions of VisiSat must be used with specific Windows operating system and Microsoft Visio versions. The latest version/build of VisiSat may not be compatible with the users current system.. Resolution Updated June 2019 The MicroNet 50 series range MN350, 450, 550, 650 LCD and Touchscreen have been withdrawn from sale. The IAC 420, 600 and Touchscreen have now also been withdrawn from sale. No direct replacement is offered. Further information on these changes can be found in PA-00495 - Notice of Withdrawal - Satchwell Sigma and PA-00528 - End of Commercialization - Satchwell Sigma. ---------------------------------------------------------------------------------------------------------------------------------------------------------- VisiSat 2.1 Build 196 (MN-VSCORE) is available to download from the Exchange Extranet , since January 2018, VisiSat can be freely used without the need for a license. Refer to PA-00597 - MN-VSCORE End of Commercialization - Satchwell MicroNet for further details on the availability of the VisiSat Configuration Tool . The VisiSat data sheet provides information on operating system and Microsoft Visio compatibility for different builds of VisiSat 2.1. SOFTWARE VisiSat 2.1 Build Number Windows Operating System Visio Release 185/196 Windows 7 2003/2007/2010 XP Professional 2003/2007 148 Vista Ultimate 2003/2007 XP Professional 2003 137 XP 2002/2003 17 XP 2002 14 Two service packs are available for VisiSat version 2.1 Build 196. Service pack 1 provides the following corrections: In the ARCnet debug Excel spreadsheet, the property editor can now be run. Exporting points to MicroNet View or Xenta Xbuilder, now allow up to 32 characters for the name and up to 50 characters for the description. In SBO (StruxureWare Building Operation) or EBO (EcoStruxure Building Operation) WorkStation, MicroNet Interfaces can no longer be exported/imported. All MicroNet engineering should be done in VisiSat first and then imported into SBO/EBO. Newly created blank pointslists can now be saved, without production an error message. Exports to SBO/EBO no longer produce Memory leaks. Adding service pack 1 takes the VisiSat 2.1 build number of 196 to 200 Service Pack 1 is available to download from the Exchange Extranet and VisiSat version 2.1 Build 196 service pack 1 Service pack 2 provides the following correction: Import file replaces all non-ASCII chars with replacement character. Once added the characters are converted correctly and points with alarms and trends results in the import file is generated. Adding service pack 1 takes the VisiSat 2.1 build number of 196/200 to 201. Service Pack 2 is available to download from the Exchange Extranet and VisiSat version 2.1 Build 196 service pack 2 Further information on VisiSat installation and operation can be found in Download latest VisiSat Data Sheets, Engineering Guides, Installation and User Guides, and Release Notes.
View full article
Picard Product_Support
‎2018-09-07 06:57 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:38 PM

Labels:
  • Satchwell MicroNet
8378 Views

IP setup for a Xenta server (Xenta 5/7/9xx) through serial communication

Issue How to set the IP address of a Xenta 5/7/9xx through serial communication. Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Servers Xenta 511, 527, 555, 701, 711, 721, 731, 913 Cause If the IP address of a Xenta 5/7/9xx is not known initially, then no configuration can be done through the IP interface. The IP address must be set through serial communication. If the device is new out of the box, or has attempted recovery after a format command, please see Default IP address following Xenta Server "format" command is different than from factory for the known default IP addressing. Resolution Preparation: You need to have an RS-232 serial cable (TAC Xenta Programming Serial Kit 0-073-0920-0). Plug the RS-232 cable in to the RS-232 B port. The RS-232 B port is the second left port at the front. Then connect the other end to the computer. Configuration steps: Go to Start > All Programs > Accessories > Communications > HyperTerminal, and open the HyperTerminal. In Connection Description Windows, type any name you like in the Name box. Click OK. In the Connect to window, choose the correct COM port that the RS-232 cable is using. If you do not know which COM port it is using. Go to your computer device manager. (Right click on “My computer” icon, and choose “Manage”. Then under “System Tools”, choose “Device Manager”. Find “Ports (COM & LPT)” and expend it Find the COM port number that is used by the RS-232 cable. Click OK. In the COM Properties window, type 9600 for “Bits per second”, 8 for “Data bits”, “Parity” is None, “Stop bits” is 1, and “Flow control” is None. Click OK. Options: you can save this setting for future use. Click on File Menu and Save. Press ENTER to activate the command prompt. Default username and password is both “root”. Type “root” and press ENTER for both the username and password. Type “setip” and press ENTER. Type the appropriate information for DHCP, IP-address, Subnet mask, Default gateway, DNS, Website name, Domain name, and Host name. Type “yes” for “Do you want to restart the IP interface”. Quit HyperTerminal when the restart is finished. See [Video] Setting the IP address of a Xenta 5/7/9xx through serial communication to watch a video of this process.
View full article
Picard Product_Support
‎2018-09-07 04:07 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:35 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
6112 Views

"This Connection is Untrusted" certificate error when logging in to a Xenta Server using Firefox

Issue When logging into the web server of a Xenta controller using Mozilla Firefox 4 an error message is shown stating that the website is using an invalid security certificate.  When logging into Xenta server using Firefox 4 a certificate error is displayed as displayed below: The complete error screen reads as follows: This Connection is Untrusted You have asked Firefox to connect securely to 192.168.1.152, but we can't confirm that your connection is secure. Normally, when you try to connect securely, sites will present trusted identification to prove that you are going to the right place. However, this site's identity can't be verified. What Should I Do? If you usually connect to this site without problems, this error could mean that someone is trying to impersonate the site, and you shouldn't continue. Get me out of here! Technical Details (IP Address of Xenta) uses an invalid security certificate. The certificate is not trusted because it is self-signed. The certificate is only valid for (IP Address of Xenta) (Error code: sec_error_ca_cert_invalid) I Understand the Risks If you understand what's going on, you can tell Firefox to start trusting this site's identification. Even if you trust the site, this error could mean that someone is tampering with your connection. Don't add an exception unless you know there's a good reason why this site doesn't use trusted identification. Add Exception... How to install a self signed certificate. Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Mozilla Firefox 4 Xenta 511, Xenta 527, Xenta 555, Xenta 701, Xenta 711, Xenta 721, Xenta 731, Xenta 913 SSL Cause The default certificate in the Xenta web server is a self-signed certificate. Since the certificate is not issued by a recognized Certificate Authority the web browser (in this case Firefox 4) cannot validate the authenticity of the certificate and suggests that the user not continue to the website each time the user tries to access it. Resolution There are two possible resolutions: Install the self-signed certificate using the following steps: Expand the "I Understand the Risks" bullet then click the "Add Exception" button. Firefox will automatically retrieve the certificate from the Xenta server. Make sure to check "Permanently store this exception" and then click "Confirm Security Exception" The certificate is now installed and the warning screen will no longer show up when logging into the server. It may be necessary to restart Firefox for the changes to take effect. Note: The certificate will need to be installed in each client computer that accesses the Xenta server but once this complete it does not need to be done again. The exception to this is if the web address of the Xenta server is changed or if Firefox is uninstalled then reinstalled. Update: Starting in September 2014, all major browsers will be disabling 1024-bit roots within their trusted roots stores. Any SSL certificates chained to a 1024-bit root will no longer work on any browsers that takes this action or one that relies on another's root store (the self-signed certificate is 1024-bit). This means that you will still get the security warning even if you have installed the self-signed certificate. Purchase a certificate issued by a Certificate Authority (CA): These certificates are pre-installed into the web browser and will automatically prevent certificate errors from occurring on all client computers that access the web server. Note that these can be quite expensive and unless the Xenta web server is being hosted on the internet they are not necessary. Please see TAC Xenta Server - TAC Networks - Technical Manual for more information. See "There is a problem with this website's security certificate." when logging in to Xenta web server using Internet Explorer 8 for information on installing certificates into Internet Explorer.
View full article
Picard Product_Support
‎2018-09-07 10:07 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:27 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
5193 Views

Default IP address following Xenta Server "format" command is different than from factory

Issue The Xenta 7xx from factory it has the default IP address 192.168.255.2, which also is stated in the manual. But when you run the “format” command on a Xenta 7XX, you will get IP address 172.22.1.5. Product Line Satchwell MicroNet, TAC INET, TAC Vista Environment Xenta Servers Xenta 511, 527, 527 NPR, 555, 701, 711, 721, 731, 901, 911, 913 Cause The format command will wipe all memory from the Xenta Server. Its IP address will need to be reset, system program will need to be reloaded, and XBuilder project will need to be redownloaded. Resolution The Xenta from factory has the default IP address 192.168.255.2 subnet mask 255.255.255.0 After the “format” command it will have IP address 172.22.1.5 subnet mask 255.255.255.0 See IP setup for a Xenta server (Xenta 5/7/9xx) through serial communication for instructions on setting the IP address to the desired address.
View full article
Picard Product_Support
‎2018-09-07 01:58 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:24 PM

Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
6508 Views
  • « Previous
    • 1
    • 2
    • 3
    • 4
    • …
    • 13
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of