Xenta Server "Run" light is solid red with no communication via Ethernet

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Xenta Server "Run" light is solid red with no communication via Ethernet
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4550 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Xenta Server "Run" light is solid red with no communication via Ethernet

Picard Product_Support
‎2018-09-07 12:34 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:30 AM

Issue

  • Xenta Server reports it is in FAILSAFE mode without shorting out terminals 9 and 10.
  • After connecting via HyperTerminal, restarting and trying to reset the IP address, the screen continues to scroll back to dsh/>
  • Xenta Server has gone offline and can not connect directly to it using Ethernet.
  • The Run light is flashing Green on first start up but then reverts to red and the LON light also flashes red.
  • During boot up it pauses and reports an error (via HyperTerminal) in loading the RAM disk. 
  • IP Address is set to 172.22.1.5 and can not change it. 
  • Not able to load any firmware into the device – error received. "Error: Could not create remote directory."

Product Line

Satchwell MicroNet, TAC INET, TAC Vista

Environment

  • Xenta Server 527, 511, 555
  • Xenta Server 701, 721, 731

Cause

Unknown corruption of the Xenta Server hard drive / flash drive, possibly due to electrical noise.

Resolution

To attempt to recover this device, try to format the device’s flash drive. To achieve this you can follow these steps using HyperTerminal or an equivalent application: (For further assistance with connecting to Xenta Servers and HyperTerminal refer to Connecting a serial cable to a Xenta 5/7/9xx controller).
 

  1. Login and type the command FORMAT.  (May require device to be placed physically into the fail-safe mode by shorting terminals 9 and 10). The format command can take up to 3 minutes to complete but you should see the confirmation through HyperTerminal while this is occurring.
  2. If you have placed the device into Fail-safe mode, remove the link on terminal 9 & 10.
  3. Restart the device, by either cycling the power or typing the command RESTART through HyperTerminal.
  4. Set the IP address and IP settings (command SETIP).
  5. Install the latest firmware.
    1. You can download the latest firmware from The Exchange Extranet; ensure that you use the correct version since there various versions for the Xenta Servers.
    2. Run the firmware download to the device. During the download you may receive an error regarding "Failure to get the hardware version from the target device…", select OK
    3. Continue the installation
    4. The download will then occur, it will take some time and may appear that the software is not responding but this is normal. Be patient and if you don’t receive any errors then all should be ok.
  6. The device should now restart, after a 1-2 minute window the “RUN” LED should be a solid green.
  7. If after following these procedures, the device is still not responding as expected please send into Repairs via your normal repair process.
Labels (3)
Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4626
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore