Issue
When trying to download a 5/7/9xx in XBuilder you get "Error code 401 - Unauthorized".
Product Line
Satchwell MicroNet, TAC INET, TAC Vista
Environment
- Xenta Server
- Xenta 511, 527, 555, 701, 711, 721, 731, 913
- XBuilder
Cause
Password in XBuilder project does not match the password in the Xenta device.
Resolution
Select the 5/7/9xx in the Network panel The password is in the right hand panel of XBuilder under th...