Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 470
    • 471
    • 472
    • …
    • 509
  • Next »

Error message: "Bad Subcommand"

Issue When trying to access the NPR configuration editor, why does an error message stating "bad subcommand" display? Environment NPR configuration editor Cause There is no BIN file within the NPR. Resolution Perform a Software Restore.
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
932 Views

Will Niagara applications run on Dual Core / Duo Core / multiprocessor computers?

Issue Will Niagara applications run on Dual Core / Duo Core / multiprocessor computers? Environment Niagara Computer with (Dual Core / Duo Core / multiprocessor) Cause Knowing the processor spec requirement helps assess existing computer for installing Niagara applications. Resolution Currently, Workplace Pro / Enterprise Server and Workbench / Enterprise Network Server will run on Dual Core / Duo Core  / multiprocessor computers. These programs were designed to use only one of the processors, leaving the other processor(s) available for other applications. Other software (i.e. WorkPlace Tech) has not been validated on these types of computer systems. Therefore, these systems should be avoided since there would be no way to confirm proper functionality for each application. It is recommended that dual-processor and multi-processor computers as well as computers utilizing Intel Pentium 4 processors supporting Hyper-Threading Technology (when this processor feature has been enabled in the computer BIOS) be avoided for all company software for both server and client workstation applications. For more information read Technical Bulletin TB04-07-01
View full article
Picard Product_Support
‎2018-09-07 02:13 AM

Labels:
  • TAC IA Series
929 Views

The MNB-1000 mounting base, manufactured before January 2009, does it comply with the UL 864 standard?

Issue The MNB-1000 mounting base, manufactured before January 2009, does it comply with the UL 864 standard? Environment MNB-BASE-1000 UL 864 Cause Information on MNB-1000 compliant with the UL 864 standard. Resolution The MNB-BASE-1000 has electronics on it that cannot be used for smoke control if it has a manufactured date prior to receiving UL 864 certification (January 2009).
View full article
Picard Product_Support
‎2018-09-06 02:36 PM

Labels:
  • TAC IA Series
935 Views

UI-4 Expansion module will not work with i2 controller

Issue UI-4 Expansion module will not work with i2 controller. Points cannot be controlled. Environment UI-4 Expansion modules i2 Controller Cause The firmware of the controller is less than what is required. The compatibility matrix indicates that to use the ui-4 expansion module that the firmware must be at version 3.3x. Resolution Uprev the firmware to version 3.3x. Read through Technical Bulletin #1361 to ensure that the bootloader flash is at the correct version. 
View full article
Picard Product_Support
‎2018-09-06 02:26 PM

Labels:
  • Andover Continuum
942 Views

Sigma - Using an Analogue Input card to display Digital Inputs.

Issue Using an Analogue Input card to display Digital Inputs when no Digital Input channels are available. Environment Sigma Analogue Input cards. Cause There are no Digital Input channels available. Resolution An Analogue Input card cannot be used directly as a Digital Input card. A work around for this is to configure an Analogue Input to act as a Digital Input. Programme an Analogue Input object in Sigma. In Sigma System Manager create a lookup table, using an appropriate free number. Input Output 0 1 15 0 20 0 Add the above Lookup table to the Analogue Input object. In Sigma System Manager create a Short Text such as On/Off =%2.f Add the new short text number to the Analogue Input object. Across the Analogue Input channel fit a 1000 ohm resistor, this will be in parallel with the Digital Input connections. When the Digital Input changes state, Sigma will display either 1 or 0.
View full article
Picard Product_Support
‎2018-09-06 02:05 PM

Labels:
  • Satchwell BAS & Sigma
937 Views

Error (time date)(alarm) Cannot write alarm

Issue The following error is showing up in the Application Director of the ENS: ERROR (09:45:06 26-Jul-11 EDT)(alarm) Cannot write alarm. java.lang.NullPointerException… Environment G3 (Niagara) ENS Cause The number of alarms in the system have exceeded the capacity defined in the AlarmService. Resolution By default the “capacity” for the AlarmService is set to 500.  Increasing this to a value greater than the number of alarms in the system will correct the error, however consider doing periodic Alarm Db Maintenance to keep the number of alarms at a manageable level.
View full article
Picard Product_Support
‎2018-09-06 01:28 PM

Labels:
  • TAC IA Series
948 Views

Powering OP7 with 24VDC

Issue Is it possible to use 24VDC as power supply to the OP7? Environment OP7 power supply adapter included in package. Cause The documentation only recommends using 24VAC as power supply. Resolution Usage of 24VDC is not tested, and therefore not recommended or supported.
View full article
Picard Product_Support
‎2018-09-06 01:22 PM

Labels:
  • TAC INET
  • TAC Vista
953 Views

How do I order a BACnet MS/TP licence for an ENC-410?

Issue Needs to add two MNB-300 controllers under an ENC-410.  How do I order the license? Environment ENC-410 Cause Needs to add some MNB-300 controllers under an existing ENC-410. Resolution According to our published literature, the ENC-410 does not support BACnet MS/TP because the RS-485 port is not isolated. If it becomes absolutely necessary to license an ENC-410 for BACnet MS/TP, you must submit a written or emailed request to the I/A Series G3 product marketing manager.  The product marketing manager may approve or deny the request based on the information contained in your request.  If approved, he will provide ordering and pricing information.
View full article
Picard Product_Support
‎2018-09-06 12:26 PM

Labels:
  • TAC IA Series
938 Views

Attempting to link from one I/A Series G3 station to another using a pop-up link and getting an error when using the browser. The error indicates - javax.baja.license.FeatureNot...

Issue Attempting to link from one I/A Series G3 station to another using a pop-up link and getting an error when using the browser.  The error indicates - javax.baja.license.FeatureNotLicensedException: tridium:brand. Environment I/A Series G3 (all versions) Cause Created a PxFile with a bound label pop-up binding to open another link outside the station environment (e.g. history).  The link works properly when using and viewing in Workbench but does not work with IE browser. Resolution The pop-up link through the browser currently does not support links to another station (supports only links within the same station).  Recommend the graphic be located with the associated history in the same station if pop-up link required.
View full article
Picard Product_Support
‎2018-09-06 12:22 PM

Labels:
  • TAC IA Series
928 Views

What mode should be used in a zone when the area is not in use?

Issue What operation modes should be used in zone control then the area is not being used? Environment Xenta 121 FC Xenta 121 HP Cause The TAC Xenta 120 device does not have any internal clock. The actual operation modes has to be sent from another device such as a Xenta 401. The following values could be sent to the nviManOccCmd SNVT: 0=OC_OCCUPIED 1=OC_UNOCCUPIED 2=OC_BYPASS 3=OC_STANDBY other values=OC_NUL 255=OC_NUL Resolution Normally, OCCUPIED mode is used when there are people in the zone. During night time, or short periods without people in the zone STANDBY may be used. If someone enters the area and triggers a motion detector or presses the Bypass button, the mode changes to BYPASS. UNOCCUPIED mode is most appropriate if the area is no longer rented or during some other long period without anyone in the area.
View full article
Picard Product_Support
‎2018-09-06 12:08 PM

Labels:
  • TAC Vista
931 Views

Creating an Email Notification in Access Expert

Issue Creating an email notification within Access Expert can be challenging if the correct steps are not followed.  Product Line EcoStruxure Access Expert Environment Access Expert Premise Software Cause If you don't follow specific steps, email notifications can be very difficult to write. Following the steps below, you can use pre-canned expressions which help to automate your notifications based on specific parameters. Resolution *Note* though you can add the Expressions tab by customizing the ribbon, no expressions can be found or used without following the process below. If you need to edit the notification to add more parameters then you will need to create a new template as editing an existing one will not expose the expressions. Trigger an event or alarm for what you would like a notification on. Right-click on the event or alarm in Event Viewer or Live Monitoring and select Add Email Template This will open up the template editor for you where you then will be able to select the necessary expressions based on your needs  Type the email message you would like to receive when the alarm triggers, click save    Type in the name you would like to use for the template and what you would like in the subject line of the notification you receive        Click on Alarm Actions, Add Alarm Action, and then Notification  Within the next dialogue box: Create a label for the notification Check the box next to "Send Email" Select the appropriate template Select Add Recipient Type in the name of the recipients you would like to receive the notification Click Save
View full article
Commander JonGreen Commander
‎2022-05-31 10:06 AM

on ‎2022-05-31 10:06 AM

Labels:
  • EcoStruxure Access Expert
958 Views

Does the oBIX service in I/A Series R2 require the web services license feature to operate?

Issue Does the oBIX service in I/A Series R2 require the web services license feature to operate? Environment I/A Series R2, UNC, oBIX Cause Licensing requirements for I/A Series oBIX Resolution The web services and associated license feature (webUi) is not required to run the oBIX service in an I/A Series R2 station.  The feature line in the R2 license must include obix. UNC example ... features=coreRuntime;bacnet;lonworks;obix If the license does not include the obix feature, purchase part number IA-DRV-OBIX for each Enterprise Server / UNC that needs to function as an oBIX server.
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Labels:
  • TAC IA Series
928 Views

Expansion board P8UI8DO is used on which controllers?

Issue Can the expansion board P8UI8DO be used on a 7716 or a 7718? Environment 7716 7718 P8UI8DO Cause Expansion Module for controllers Resolution The expansion board P8UI8DO can be used on a 7716 and the 7718
View full article
Picard Product_Support
‎2018-09-06 03:13 PM

Labels:
  • TAC INET
937 Views

Analog inputs are reading too high or too low on a 7780

Issue The Analog inputs are reading too high or too low on a 7780. Product Line TAC INET Environment 7780 Cause Resistor configuration errors, damaged power supply, or the circuit may have been shorted. Resolution Several things could be contributing to this. Check the resistor configuration installed for the input and make sure it is correct. Check is the analog power supply (+15 VDC) has been damaged. Make sure a sensor does not have an open circuit in it (sensor is shorted).
View full article
Picard Product_Support
‎2018-09-06 03:12 PM

Labels:
  • TAC INET
923 Views

Output relays will not control on a 7780

Issue The Output relays will not control on a 7780, how can I fix this? Environment I/NET site Cause Output relays will not control on a 7780 Resolution First, check the matrix relay interface cable and make sure it is correctly connected. Secondly, make sure the matrix straps are not set incorrectly. Finally, Fuse F2 maybe blown. Fuse F2 is located near the top edge of the base card, directly above the LEDs. Fuse F2 is plugged into positions A and B of receptacle J20. This is a 0.5 amp pico fuse.
View full article
Picard Product_Support
‎2018-09-06 03:12 PM

Labels:
  • TAC INET
912 Views

Removing Trend Log before Upgrading to Vista 4.3

Issue Removing Trend Log before Upgrading to Vista 4.3 Environment Vista upgrade Cause During the addition of digital signatures to the log values, as required when upgrading to Vista 4.3, the PC may experience excessive demand of the processor and take a significant amount of time. Resolution If you do not require these trend log values you can follow these steps to avoid this potentially lengthy process. In the version of Vista that you are upgrading from create a full Vista backup by accessing the $Backup_FVB object found in you Operator Unit. Make sure that the "Include trend log files" selection is not checked before you start the backup. Upgrade to Vista 4.3 and specify a different database path then the one your old Vista database resides in. Start Vista Server and manually log in. Select "Restore Database" from the File menu in Vista Server. Browse to the backup file and specify the path you want to restore this database to. (The path to restored database must be different from the current Vista database path being used by Vista Server) Shutdown Vista Server and using Vista Server Setup change the database path to the directory you restored the backup into. Start Vista Server and the database will be upgraded without having to wait for the trend logs to get digital signatures. Once you have verified the upgrade completed made another backup of your database.  
View full article
Picard Product_Support
‎2018-09-06 03:08 PM

Labels:
  • TAC Vista
920 Views

Using TOAD with Vista 4.3

Issue Using TOAD with Vista 4.3 Environment Vista 4.3 TOAD Cause The release notice for Vista 4.3 recommended the use of TOAD which is a free program that allows users to view and query SQL databases. This can be a very powerful tool to assist in database verification, exploration of the database for creating Crystal Reports, and running scripts. Resolution Warning: Care should be taken before making any changes to the SQL database since damage could break Vista To setup TOAD to work with the Vista database: Run Vista Server Setup and check the "SQL Server" tab and write down what is filled into the Instance and Database fields. Run TOAD_SS.exe. At the Server Login screen select "Add". Give your connection a name. Select "Use Connection String" and click "Build". Select "Microsoft OLE DB for SQL Server". Click "Next". In section "1" use the dropdown menu to select the Instance name found in Vista Server Setup. Typically the PC name or PC Name\TACVISTA. Select "Use Windows NT Integrated Security". In section "3" verify that "Select the database on the server" is selected and with the drop down menu choose the database name found in Vista Server Setup. Typically "taclogdata". Click "Test Connection" to verify it is working and click "Ok". Click "Ok" in the Data Link Properties window. Click "Ok" in the Add Registration window. Select the line your server was added to and click "Connect". You should now be connected to the server and you can use the Data Browser window to view the tables, views, procedures, and users of the database among other things. The SQL Editor window will allow you to run queries as well as other administrative tasks. Remember that all changes should be carefully considered before made to avoid breaking the database.  
View full article
Picard Product_Support
‎2018-09-06 03:08 PM

Labels:
  • TAC Vista
907 Views

Using Lonmaker to replicate settings in a specific function block from one Lonworks unit to others of the same type

Issue Using Lonmaker to replicate settings in a specific function block from one Lonworks unit to others of the same type Environment LonMaker LON Devices Cause It is very time-consuming to configure VAV controllers and other Lonworks units in large systems. Fortunately, it is possible to configure the settings in one controller and then replicate those settings to all of the other controllers. This can be accomplished by using "ResynchCPs" but that applies to all settings in a controller. Using this function can replicate the settings in only one function block. For example, maybe you want to change all of the temperature setpoints and heating configuration but not the duct area and other airflow settings. Resolution First, make sure that each controller in the Lonmaker drawing has a functional block of the same type, e.g. "VAV Controller." To quickly create multiple functional blocks, drop a functional block onto the drawing; in the dialog box, give the FB a name, and where it says "Number of FBs to Create," enter the number of VAV controllers in the subsystem. Use the plug-in or browser to configure the parameters in one of the controllers. Make sure the parameters get downloaded to the controller. Next, right-click on the functional block for that controller and select "Replicate Settings." Select the parameters that you want to copy and then click Next. Under "Target Subsystems," select the subsystems that contain the same type of controllers. Under "Target FB Selection" select "Matching FB Type", then click Next. It will show you a list of qualifying targets, including the current value and new value of the parameters. Highlight any settings you don't want to be changed and select remove. Click Finish to replicate the settings
View full article
Picard Product_Support
‎2018-09-06 03:07 PM

Labels:
  • TAC Vista
904 Views

File Equalization on a new PC with SP4.

Issue Running Equalization on a PC that has SP4 (Service Pack 4) and the clients are unable to connect to the File Master Environment PC that has SP4 Cause There is a protocol setting that needs to be enabled for this to occur. Resolution The following steps show the path to MSQL Server where the protocol resides and how to get it enabled. Open Windows Explorer and go to C:\Program Files\Microsoft SQL Server\80\Tools\Binn\SVRNTCN.exe. Double click on this file and enable the following files, Named Pipes and TCP/IP. Apply the changes and then close the editor SQL Server Network Utility.  
View full article
Picard Product_Support
‎2018-09-06 03:04 PM

Labels:
  • TAC INET
907 Views

Entering values less than 1 in Zbuilder

Issue Entering values less than 1 in Zbuilder results in red error indication. If you enter ".05" or ".2" into a field in Zbuilder it won't accept it. Environment Zbuilder Xenta 121 Cause A period cannot be the leading digit in a numerical input. Resolution The first digit must be a number,  so you must enter fractional values with a leading zero. Example: "0.05" or "0.2"
View full article
Picard Product_Support
‎2018-09-06 03:01 PM

Labels:
  • TAC Vista
925 Views
  • « Previous
    • 1
    • …
    • 470
    • 471
    • 472
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of