Analog inputs are reading too high or too low on a 7780
  • Analog inputs are reading too high or too low on a 7780
  • Cody_Failinger
    Cody_Failinger
‎2018-09-06 03:12 PM
The Analog inputs are reading too high or too low on a 7780.
TAC INET
7780
Resistor configuration errors, damaged power supply, or the circuit may have been shorted.
Several things could be contributing to this.
  • Check the resistor configuration installed for the input and make sure it is correct.
  • Check is the analog power supply (+15 VDC) has been damaged.
  • Make sure a sensor does not have an open circuit in it (sensor is shorted).
  • TAC INET
  • 1684