UI-4 Expansion module will not work with i2 controller
  • UI-4 Expansion module will not work with i2 controller
  • Alan_Wood
    Alan_Wood
‎2018-09-06 02:26 PM
UI-4 Expansion module will not work with i2 controller. Points cannot be controlled.
  • UI-4 Expansion modules
  • i2 Controller
The firmware of the controller is less than what is required. The compatibility matrix indicates that to use the ui-4 expansion module that the firmware must be at version 3.3x.
Uprev the firmware to version 3.3x. Read through Technical Bulletin #1361 to ensure that the bootloader flash is at the correct version.
  • 3969