Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Using Lonmaker to replicate settings in a specific function block from one Lonworks unit to others of the same type

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using Lonmaker to replicate settings in a specific function block from one Lonworks unit to others of the same type
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
897 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using Lonmaker to replicate settings in a specific function block from one Lonworks unit to others of the same type

Picard Product_Support
‎2018-09-06 03:07 PM

Issue

Using Lonmaker to replicate settings in a specific function block from one Lonworks unit to others of the same type

Environment

  • LonMaker
  • LON Devices

Cause

It is very time-consuming to configure VAV controllers and other Lonworks units in large systems. Fortunately, it is possible to configure the settings in one controller and then replicate those settings to all of the other controllers. This can be accomplished by using "ResynchCPs" but that applies to all settings in a controller. Using this function can replicate the settings in only one function block. For example, maybe you want to change all of the temperature setpoints and heating configuration but not the duct area and other airflow settings.

Resolution

  1. First, make sure that each controller in the Lonmaker drawing has a functional block of the same type, e.g. "VAV Controller." To quickly create multiple functional blocks, drop a functional block onto the drawing; in the dialog box, give the FB a name, and where it says "Number of FBs to Create," enter the number of VAV controllers in the subsystem.
  2. Use the plug-in or browser to configure the parameters in one of the controllers.
  3. Make sure the parameters get downloaded to the controller.
  4. Next, right-click on the functional block for that controller and select "Replicate Settings."
  5. Select the parameters that you want to copy and then click Next.
  6. Under "Target Subsystems," select the subsystems that contain the same type of controllers.
  7. Under "Target FB Selection" select "Matching FB Type", then click Next. It will show you a list of qualifying targets, including the current value and new value of the parameters.
  8. Highlight any settings you don't want to be changed and select remove.
  9. Click Finish to replicate the settings
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 1975
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of