Output relays will not control on a 7780
  • Output relays will not control on a 7780
  • sesa139513
    sesa139513
‎2018-09-06 03:12 PM
The Output relays will not control on a 7780, how can I fix this?
I/NET site
  1. First, check the matrix relay interface cable and make sure it is correctly connected.
  2. Secondly, make sure the matrix straps are not set incorrectly.
  3. Finally, Fuse F2 maybe blown. Fuse F2 is located near the top edge of the base card, directly above the LEDs. Fuse F2 is plugged into positions A and B of receptacle J20. This is a 0.5 amp pico fuse.
  • TAC INET
  • 1686