Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,840
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 329
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 68
    • 69
    • 70
    • …
    • 507
  • Next »

Mass firmware upgrade on multiple MPMs (bulk upgrade)

Issue How to upgrade remote MPMs with a Canbus, Zigbee network. Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi-Purpose Manager MPM Cause Cannot connect to an MPM directly to perform a firmware upgrade Resolution This procedure explains how to perform a firmware upgrade on multiple remote devices at once, in order to save time and standardize the firmware versions across your deployment. This process will induce traffic on the network, therefore it is recommended that this procedure be performed after-hours or when it is less likely to disrupt normal operations. Step 1: Verify your monitor Manager's firmware version Ensure monitor MPM has the same or higher firmware version than the the version intended to be installed on the remote MPMs. Highlight the MPM in the Network Panel on the left side of your screen and either click on the "About" button or navigate to CFG1 object to verify firmware version. Step 2: Download and rename the firmware file The firmware can be downloaded from the Exchange then firmware file must be renamed "upgrade.bp" Step 3: Upload the firmware file to your Manager Choose the File Manager tab and click on the “Upload File” icon. A dialog box will open to select the firmware file on your local PC. Browse to the correct file and select it. Click the “Upload” button to send the file from your computer to the controller. When the file upload is completed, the file will be shown in the Upload Manager list.   Step 4: Initiating the remote upgrade Inside the File Manager panel, either right-click on the firmware file that was just uploaded and select “Add to all” to copy the same file to all the remote nodes, or drag and drop the file from the left panel onto the desired Manager on the right panel. The file will be displayed under each of the remote nodes (or a single node if the file was copied using drag and drop) under the Network panel, on the right side of the window.   In order to initiate the file transfer to the remote nodes, click the Start button. The status will change to “In Progress” and you will be able to follow the progress of each node in the Network panel. Once the file transfer is complete, the remote nodes will reset and perform the firmware upgrade. Step 5: Verify the firmware version of the remote nodes You can verify that the upgrade process completed successfully by highlighting the remote node in the left panel and then select the “Controller Configuration” (CFG1) object. The version # will be displayed in the bottom section.
View full article
Picard Product_Support
‎2018-09-10 06:53 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 09:50 PM

Labels:
  • EcoStruxure Building Expert
1764 Views

Is it possible to integrate Continuum with Active Directory for access control purposes?

Issue A prospective customer requires their active directory be integrated into Continuum to eliminate duplication of data entry. Product Line Andover Continuum Environment CyberStation Active Directory LDAP Personnel Import Utility (PIU) Cause How can Continuum be integrated to an existing active directory for access control cardholder purposes? Resolution Yes, it can be integrated. The Personal Import Utility is a CyberStation application based on Active Directory.  Active Directory is a Microsoft Windows directory service that provides a unified view of complex networks.  Active Directory is installed on a Microsoft Windows Server, known as the domain controller.  CyberStation uses the Lightweight Directory Access Protocol (LDAP) to read and extract Active Directory user information. The above is from the CyberStation v1.93 Help System, a portion of which is attached here for reference.
View full article
Picard Product_Support
‎2018-09-10 05:22 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 09:44 PM

Labels:
  • Andover Continuum
1621 Views

TACOS startup delay utility

Issue It is possible to have a timing issue with the start up of the license server as it relates to the start up of the TACOS.exe.  If TACOS starts before the license server the license server may not be able to read the license file and access to the your Vista products may be denied. Sometime the Workstation or other components can be launched, but all the points are offline. An error "No license for LonWorks communication" will show up. Product Line TAC Vista Environment Vista License Server TACOS.exe Cause TACOS.exe starts before the license server fully started.  When this happens, the License Server may not be able to read the license file properly and access to the your Vista products may be denied. Resolution This tool is a part of TAC Vista Run Mode TACOS Startup Delay is developed to help you set the startup delay for TAC Vista Server, whether it is running as an application or a service. You might find it necessary to delay the startup of TACOS to ensure that the license server or 3rd party software is fully started, before TAC Vista server starts. NOTE: This program allows you to set a delay from 0 to 240 seconds. Click Here: TACOS Startup Delay Utility Download the .zip file by clicking the link above Double click the TACOS Startup Delay 1.0.0.2 Application file When the window pops up you can enter up to 240 seconds into the delay field   Click "Set" button Reboot PC
View full article
Picard Product_Support
‎2018-09-10 01:39 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 09:41 PM

Labels:
  • TAC Vista
1906 Views

Sensor Calibration certificate, Veris portfolio

Issue   A calibration certificate is sometimes requested by the end customer Product Line Field Devices Environment Veris sensors Cause   To ensure that a sensor is keeping measurement values within specification, a certificate is sometimes requested by the end customer. Resolution Calibration certificates are available for some Veris models and must be requested at the time of ordering by selecting  “N” in NIST block for 1% and 2% humidity transmitters. Temperature transmitters can be ordered with 1 or 2 point calibration certificates by selecting 1 or 2 in the in the Temp Cert Block. The following example shows how the model numbers are built up: As can be seen in the second example above the model HD2NVCTC2 has a 2% accuracy RH element with a NIST traceable certificate, it also has a 1K platinum RTD with a 2 point  calibration certificate. For information on NIST traceability see the National Institute of Standards and Technology website
View full article
Picard Product_Support
‎2018-09-11 02:48 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 09:39 PM

Labels:
  • Field Devices
1779 Views

Windows Firewall or Anti-Virus causes Controllers to go Off line.

Issue The Domain was upgraded to Windows Server 2008 and now the Workstations Windows firewall causes Andover  Controllers to go Off line. Product Line Andover Continuum Environment Windows 7, Windows Server 2008 R2 9680,9640 CX 75XX  9900, 9200 Cause Enhanced Security in the MS Server 2008 series domain enforces port blocking above ports 5000  and above. Resolution Add components , ports to the firewall exception list for Windows Firewall and for Anti-Virus Download List:
View full article
Picard Product_Support
‎2018-09-11 03:57 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 09:31 PM

Labels:
  • Andover Continuum
2598 Views

How to configure Alarm Escalation in Security Expert.

Issue Alarms need to be sent to specific Workstations and then escalated to other Workstations if they have not been acknowledged within a specific amount of time. Product Line EcoStruxure Building Expert Environment Security Expert Cause Documentation does not describe specific steps for how to configure alarm escalation. Resolution You will be able to do the alarm escalation with Security Expert by using the Alarm Routing options under the Events Menu. 1. Create your Workstations by going to Events | Workstations. The name of the new Workstation object in Security Expert will need to correspond to the actual Windows PC name for alarms to be routed properly. 2. After you have created all of the Workstations you will need to create Workstation Groups under the Events menu. One group for each level of alarm routing that you want to do. If you have three workstations and want to route from one to the next to the next, then you would need to create three Workstation Groups and add one Workstation to each of them. 3. Next you will need to create an alarm routing list under Events | Alarm Routing. On the Workstation Groups tab add the time for Transfer After (this is in seconds) which is when the alarms will be routed to the Workstations in the next Workstation Group. Set the Routing Order for those groups, the first group is 0. Next set the Transfer Priority if you have specific alarms that are to be routed to these Workstation Groups, leave blank if all alarms are to be routed. Set the routing group active to enable routing. 4. The last bit is to go to your Alarms that you want to route and add the routing list you created in step 3 to the Alarm Routing List field. This will now route these alarms to the Workstations you've configured.
View full article
Picard Product_Support
‎2018-09-10 07:22 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 08:39 PM

Labels:
  • EcoStruxure Security Expert
1969 Views

Access Expert V3 Accessibility

Issue How and where to get the API client for V3 Product Line EcoStruxure Access Expert Environment Access Expert V3 Premise Hosted Cause Need to know where to go to get the API file for V3.  Remember, it is only supported on Win 8.1 and above. Resolution Version 3 (V3) does not use a URL to access the instance but an Application Programming Interface (API). In order to get this file, the user would follow these steps: Complete the V3 Online Training by Feenics From the course go to the last section named Downloads,  https://www.feenics.com/training/lesson/downloads/ Select the Access Expert (USA) and click on Download Save the file and then install it on a Win 8.1 or above PC When the Connection Details come up, insert the respective credentials to access your instance Once logged in, now program the system accordingly.
View full article
Picard Product_Support
‎2018-09-10 10:11 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 08:28 PM

Labels:
  • EcoStruxure Access Expert
1857 Views

TGML Webstation graphic text and values are not correctly aligned

Issue When viewing a TGML graphic from Webstation the text and values are not aligned correctly. In Workstation the text and values are aligned fine. Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation 1.5 Cause In the Control Panel\Appearance and Personalization\Display it is possible to change the size of text and other items on your screen. If this is set  to larger than 100% the text and Values will not be aligned in in the TGML graphic in Webstation. Resolution Set the value for Control Panel\Appearance and Personalization\Display to 100% and not more. Windows 10 Right click or press and hold on your desktop, click/tap on Display settings. Click/tap on Display on the left side. If you have more than one display connected to your PC, then select a display at the top on the right side that you want to change the DPI of. Under "Change the size of text, apps, and other items", select the DPI percentage and set it to 100% and not more. Windows 7 Open Control Panel Open Appearance and Personalization Set Display to 100% and not more
View full article
Picard Product_Support
‎2018-09-11 09:08 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 08:22 PM

Labels:
  • EcoStruxure Building Operation
1810 Views

SEC-TE/SED-0 does not join the MPM’s ZigBee network and does not go online

Issue SEC-TE (TE2) smart terminal controller / SED-0 (DA2) smart wireless actuator will not come online in an MPM controller. Product Line EcoStruxure Building Expert, Field Devices Environment SmartStruxure Lite Multi-Purpose Manager Smart Controllers Cause The Zigbee network configuration parameters in the MPM have been entered incorrectly. Resolution The application version of the SEC-TE/SED-0 must be determined before proceeding forward. Sticker on device should read V13 or V14. To check/modify the current settings, navigate to the "ZigBee Configuration" object (ZBC) under the MPM. For Application Version 13: Stack profile should be set to "Custom" and Security profile should be set to "None." For Application Version 14: Stack profile should be set to "ZigBee Pro" and Security profile should be set to "Home Automation."
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 08:18 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
1989 Views

[Dev File] Xenta 5/7/9xx Modbus RTU Integration to Cummins ModLon 2 Gateway

Issue Integration to the Cummins ModLon 2 gateway with the Xenta 500 / Xenta 700 / Xenta 900 and Modbus RTU Product Line TAC Vista Environment Xenta 511, 527, 701, 711, 721 (5.1.5 up) Xenta 731, 913 (all versions) XBuilder Cummins ModLon 2 Gateway Cause Disclaimer: This device template is intended to provide a starting point for an integrator, and is in no way written to be the mandatory points list for your integration effort. Product Support Services-Dallas has written this device template in an effort to give our customers a starting point and solid example of how to develop a device template for the above product. The integrator will be responsible for any additions or modifications to this device template. Please report any problems to PSS Dallas at product.support@buildings.schneider-electric.com Resolution Please us the following .dev files as a starting point and a guide to the integration. This .dev file contains a set list of registers that PSS assumed would be seen as critical and important to the integration process. If any other data is needed please see this supported document to make the necessary changes. One generator: .dev file Two generators: .dev file   To use these files in Xbuilder please follow these steps: Extract the .dev file from the .zip file in the link above, and place it on your harddrive. In Xbuilder, right click on the Modbus Master device and chose Add Device Browse to the needed .dev file and choose Open. Rename the newly added device to a unique name within the Modbus Master network.
View full article
Picard Product_Support
‎2018-09-07 03:33 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 08:15 PM

Labels:
  • TAC Vista
5300 Views

How to change setpoint from a BMS and SE8000 vice versa

Issue Unable to change set point from the thermostat when adjusting the value from a BAS Product Line EcoStruxure Building Expert Environment Smart Struxure Lite Cause Misconfiguration of the object and BACnet priority level Resolution 1)     When discovering the object from the BMS, it will integrate as; type: numeric point | Property ID: Present value | Name: Occupied cool Setpoint as an example. The variable will be for reading only the actual value set.   2)     To change values from the BMS and thermostat, the object shall be configured as follow: ·        Type: numeric WRITEABLE ·        Enabled: True ·        Property ID: RELINQUISH DEFAULT   From the thermostat, If the value is highlighted in RED by going to set point page 1/2, the object is misconfigured repeat step 2  
View full article
Picard Product_Support
‎2018-09-10 10:21 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 08:03 PM

Labels:
  • EcoStruxure Building Expert
2791 Views

Uploading Database files to an MPM (Cloning)

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue How can I clone an MPM? How can I upload config.db to an MPM? Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi-Purpose Manager Cause Unable to upload config.db to an MPM Resolution An MPM can be cloned from Building Expert by exporting default.db from one MPM and importing it to another (using the "Export Database" and "import Database" buttons) Note: Allow MPM a few minutes before attempting to access Building Expert. MPM will reboot automatically and install Database files. If it is necessary to clone the system configuration objects as well, refer to the procedure below: This procedure show you how to upload the Database to an MPM. To download a backup of the database, refer to MPM database information. Power up the MPM and ensure either its IP address can be pinged or Building Expert is accessible. In address bar of browser, enter 10.50.80.3/test.html. (assuming IP address of MPM is set to default) In Remote Path field of File Upload section, enter config.db. Click Browse and Navigate to the backup config.db file and select it. Click Submit Query. Wait for {“success”: true} to show before you proceed. Note: Uploading the config.db file first does not cause the MPM to reboot; which is why it is uploaded first On Browser, click to return to previous page. In Remote Path field of File Upload section, enter default.db. Click Browse and Navigate to the backup default.db file and select it. Click Submit Query. Wait for {“success”: true} to show before you proceed. Allow MPM a few minutes before attempting to access Building Expert. MPM will reboot automatically and install Database files. Note: MPM must not powered off during this time In address bar, enter 10.50.80.3 to connect to Building Expert and validate Database upgrade is correct.
View full article
Picard Product_Support
‎2018-09-10 06:57 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:57 PM

Labels:
  • EcoStruxure Building Expert
2143 Views

SER8000 series room controllers communications options

Issue SER8000 series room controllers communications options Environment SER8000 series room controllers Cause Integration to SER8000 room controllers via Modbus is required.  Resolution Currently, the SER8000 series room controllers communications options are Zigbee Pro or BACnet MS/TP. Refer to the SER8300 datasheet.  To communicate on Modbus RS-485, an option would be to use the multi purpose manager (MPM-UN) as a gateway device.    * Updated July 2015 As per Product Annoucement PA-00428, the SE8000 with firmware 1.3 can now act as a Modbus slave using the RS-485 port. 
View full article
Picard Product_Support
‎2018-09-11 06:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:49 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
4816 Views

Unable to connect to Infinet Roam IO 2 tool using Windows 7 / Update fix

Issue When using the Roam IO 2 tool, you are unable to connect to the controller using the infinet tool, but you can connect using the BACnet tool. Bluetooth has connected fine using both tools. Environment Windows 7 Roam IO 2 Infinet BACnet Cause This issue is due to a firmware mismatch. Resolution There is a new version of the RoamIO tool firmware available,  You must update to this version for the tool to connect correctly. Download the update RoamIO tool here. Using a 3rd party unzip program, Unzip the file. Update the Roam IO 2 tool with the Roam IO 2 connected Using the BACnet RoamIO software, goto tools and then update. Select the update .UPD file you have just downloaded, this will flash upgrade the Roam IO 2 to the latest firmware
View full article
Picard Product_Support
‎2018-09-10 01:38 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:46 PM

Labels:
  • Andover Continuum
2039 Views

VisiSat version 2.1 Build 196 service pack 2

Issue Service Pack 2 provides the following correction: MicroNet VisiSat import file replaces all non-ASCII chars with replacement character( Defect 31467). Fix applied so that the characters are converted correctly.  Fix applied so that points with alarms and trends results in the import file being generated. Product Line Satchwell MicroNet Environment VisiSat 2.1 Build 196 201 Cause Correction of raised defects. Resolution This Service Pack should only be added to VisiSat 2.1.196 or 2.1.200 if service pack 1 has been installed. Note: When installed, the VisiSat 2.1.96 or 200 installation (200 if service pack 1 has been installed), the build number increases to 2.1.201. (due to one of the files in 'Program Files'). VisiSat will still show as Build 2.1.196 in Control Panel - Programs - Programs and Features - Uninstall or change program. Installing VisiSat Service Pack 2 =============================== Shutdown VisiSat and the VisiSat-Server. Run "VisiSat 2.1.196 Service Pack 2.exe". Extract to VisiSat installation root drive. (or extract to another location and move the Satchwell folder, created when extracted to the root of the C: drive). To the question 'Would you like to replace the exiting file', select 'Yes to All' Restart VisiSat. Download VisiSat 2.1 Build 196 Service Pack 2. See VisiSat version 2.1 Build 196 service pack 1 where information on VisiSat 2.1 Build 196 Service Pack 1 can be found and the service pack downloaded.
View full article
Picard Product_Support
‎2018-09-11 04:53 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:45 PM

Labels:
  • Satchwell MicroNet
2183 Views

SSL and Graphical Programming

Issue Issue1: Unable to use some of the function blocks in the Graphical Editor when creating a graphical program. Issue2: Unable to find some of the function blocks in the Graphical Editor Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi-Purpose Manager Cause Description of each function block is not available in Building Expert Resolution Resolution 1: A detailed explanation of each function can be found in the StruxureWare Building Expert Graphical Block Programming User Guide. Resolution 2: Upgrade MPM firmware to 2.16
View full article
Picard Product_Support
‎2018-09-11 12:28 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:38 PM

Labels:
  • EcoStruxure Building Expert
1926 Views

Replacing Xenta 400 series I/O Modules With Xenta 400A series I/O Modules

Issue Replacing an older style 400 I/O with 400A series hardware, the Digital Inputs need changed to reflect the newer style of Universal Input. Product Line TAC Vista Environment Xenta 400 I/O Xenta 421, 422, 451, 452 Xenta 421A, 422A, 451A, 452A LonMaker Replace Cause Hardware changes in the Xenta 400 "A" series I/O will not function as a replacement to a non-"A" series without additional changes to Menta and LonMaker. Resolution Part 1- Changes needed within Menta Open the controller’s application (a Menta file). For ES projects, this file should be stored within C:\TAC\Vista\Applications. Note the I/O module that needs to be replaced. A list of I/O modules can be found under the Options menu on the Device Specification page:   Find and record all input points on the I/O module to be replaced. This list is found in the I/O Configuration Table under the Options menu. For example, write the "Name" and "Bound To" address for every point referencing M2.   After you have noted all of the addresses for input points on the I/O module that will be replaced, you can edit the device type for the I/O module to reflect the new type (421A or 451A). Making this change WILL remove all DI mappings (421: X1-X4) and all thermistor mappings (451: B1-B4) affected by the change in module type.   Double-Click on each DI block from the 421 (X#) or on each AI thermistor input block from the 451 (B#) that you are updating to a 421A or 451A.   The following window will appear. Click the Bind button.   Update Menta FOR 421A POINTS: The controller’s DI points are now UI points. Select the Terminal Ref based on the old mapping: X1-U1, X2-U2, X3-U3, X4-U4 After selecting the new Terminal Ref, click the OK button and then the OK button again for the Edit Block window. FOR 451A POINTS: The controller’s thermistor inputs (B#) are now additional Universal Inputs. Select the Terminal Ref based on the old mapping: B1-U5, B2-U6, B3-U7, B4-U8 After selecting the new Terminal Ref, click the OK button and then the OK button again for the Edit Block window. **Repeat step 7 for all affected points on the I/O module you’ve updated. Repeat steps 2-7 for every I/O module that needs to be replaced by a 421A or a 451A. PART II - Integration Within LonMaker locate the controllers that you want to change out for a 421A or 451A   Right click on them one by one, a click "Delete."   Open the Vista System Plug-In. Right click on the controller in which you want to change the .MTA application. Click "Configure."   Click "Browse," and locate the updated .MTA file you saved   Click "NO" when asked if you want to remove the devices   Click "Add and Match"   Click "Apply"   Re-Synchronize LonMaker   Your controllers should now be 421As or 451As
View full article
Picard Product_Support
‎2018-09-07 01:43 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:33 PM

Labels:
  • TAC Vista
3057 Views

How does time sync function in AS-P react with BACnet MSTP devices?

Issue Customers question the time sync function in AS-P for BACnet devices Environment SE8650, Viconic, SBO, AS-P, SmartStruxure, Room Controller, MSTP, 3rd Party BACnet Devices Cause It is important to understand what happens when AS-P or Room Controller lose power. Resolution SE8650 firmware version 1.7.1-56d and SBO 1.9.3.24 were used in the test. The testing was done with the fieldbus speed at both 38400 and 76800 baud. 1. The first test was to confirm AS-P sends out time sync signal 38 minutes after each hour periodically. A review of all the timeSync data packets during the capture reveals that the time sync packets are sent every hour when the time in AS-P is 38 after the hour minutes mark. 2. The second test was to confirm that the AS-P will send out a timeSync data packet if a device comes back online after a power outage. First the time was synchronized between the SE8650 with AS-P. SE8650 was then powered down and the AS-P server time changed so that the times in the two devices would not match.   A review of the time synchronization packets in the packet capture confirms that the AS sends out a time synchronization once the SE8650 is powered and boots up. 3. If the AS-P and SE8650 both lost power the SE8650 will boot up before the AS-P. The AS-P will then sends out a timeSync once the BACnet communication is settled.
View full article
Picard Product_Support
‎2018-09-10 06:31 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:12 PM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
2808 Views

Display values/objects from a remote MPM on dashboard of the monitor MPM

Issue Cannot select data points of remote nodes to be references in a graphic on the monitor MPM Environment SmartStruxure Lite Multi-Purpose Manager MPM-VA MPM-UN MPM-GW Cause Feature not built-in Resolution When building dashboards on monitor MPMs, only local points can be used in the graphics. To be able to select points of remote MPMs, The Object_Copy script must be used. The script will copy points from the remote nodes to the monitor and make them local to that monitor MPM. This method can be used in ZigBee, Canbus and UDP networks. For example, to copy a point from each of the remote MPMs to the monitor, the script would have to be modified as follows object_list[1] = {tag = "zone1", source_device = "DEV200", source_point = "AV11", destination_device = "ME", destination_point = "AV1"} object_list[2] = {tag = "zone2", source_device = "DEV300", source_point = "AV22", destination_device = "ME", destination_point = "AV2"} object_list[3] = {tag = "zone3", source_device = "DEV400", source_point = "AV33", destination_device = "ME", destination_point = "AV3"}   Important notes: This script increase the monitor's CPU % usage and increases the traffic on the network. Therefore, depending on the size of the network, it is critical not to use more than a couple of points per remote MPM
View full article
Picard Product_Support
‎2018-09-10 01:55 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:02 PM

Labels:
  • EcoStruxure Building Expert
2548 Views

SE(R)8000 series short and long messages

Issue SE(R)8000 series short and long messages Product Line EcoStruxure Building Expert, EcoStruxure Building Operation Environment SE8000 Series Room Controllers SER8000 Series Room Controllers Ex. Viconics branding VT8000 Series EcoStruxure Building Operation Cause Configuration of the SE(R)8000 series short and long messages Resolution The short and long messages are set via BACnet. Take note that the short and long messages do not hold when power to the SE8000 is turned off. This is because currently, the messages are stored in RAM. The workaround is to change the name (from the AS) and back again then save to get it to display on the unit again. Below is the procedure to change the short and long messages in EcoStruxure Building Operation. Short Message: The Short Message can be written to the SE8000 room controller by populating the "Location" Property with the message   Long Message: The Long Message can be written to the SE8000 room controller by populating the "Description" Property with the message The message however will not get displayed until the "Display Long Screen Message" has been activated. Optional: you can also choose the color of the long message background by changing the "Long Message Background Color".     Discrepancy on the text written to the device, and the text shown on the device In some cases when using non-English characters in the messages, the text on the SE8000 will not be rendered as expected. The issue is caused by SE8300 not conforming to BACnet standard in string encoding and decoding. The workaround is to set "BACnet string encoding" property of the device to "ISO 8859-1(Latin-1)", or other encoding the device supports. SE8300 claims to support BACnet protocol revision 10, which requires the conforming device to interpret Character Set 0 as UTF-8 string. In 1.9, SBO started to write to devices using Character Set 0 for unicode strings, but the SE8300 fails to decode it. Setting the "BACnet string encoding" to Latin-1 for the devices fixes the problem. 
View full article
Picard Product_Support
‎2018-09-11 01:54 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:57 PM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
2344 Views
  • « Previous
    • 1
    • …
    • 68
    • 69
    • 70
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of