How many LonWorks devices can be installed under a Xenta Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How many LonWorks devices can be installed under a Xenta Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1805 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How many LonWorks devices can be installed under a Xenta Server

Picard Product_Support
‎2018-09-07 06:38 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:44 AM

Issue

  • LonWorks point count recommendation for the Xenta 5/7/9xx series controllers
  • What is the device limitation on the FT-10 LonWorks channel installed on a Xenta Server

Product Line

TAC Vista

Environment

  • Xenta 500
  • Xenta 700
  • Xenta 900

Cause

The load point table can be found in Vista version Release Notes on The Exchange Download Center.

When Xenta 700 was released the Product Announcement had a table with the recommended number of LonWorks devices attached to Xenta 5/7/9xx. Below you can see a small revision of the recommendations. The list applies to devices which the applications in the Xenta 5/7/9xx are interchanging data with. Other devices that are completely handled by TAC Vista through the LTA port of Xenta 5/7/9xx are not included in this calculation. These devices will influence the LonWorks network performance in a similar way as if they were connected through a Xenta 911 and have to be considered.

Not following the design recommendations and adding too many LonWorks devices to a single channel will cause poor Xenta Server performance.

Resolution

Each device uses "load points" according to the table. As a general guideline the total "load points" on the network shall stay under 100 to get a reasonable performance. In reality the e.g. intensity of the traffic also has an influence as well as, of course, the expectations on response time.

Type of device Load points
I/O module 5
Xenta group master 280/300/401      20
Additional Xenta 280/300/401      in the group 2
Standard LonWorks device, including Xenta 100, polled 2
Standard LonWorks device, including Xenta 100, bound 0.75

Refer to The Exchange Download Center for future releases of Vista / Xenta Release Notes containing software and updated load calculations

This information is usually found in the Appendix B - Engineer Information, and look for section titled

LonWorks recommendation for the Xenta 500 and 700 series

Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4001
  • PeterLarsen23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore