How to configure the I/A Series R2 LON Tunnel for use with the WorkPlace Tech Tool software.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to configure the I/A Series R2 LON Tunnel for use with the WorkPlace Tech Tool software.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2629 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to configure the I/A Series R2 LON Tunnel for use with the WorkPlace Tech Tool software.

Picard Product_Support
‎2018-09-10 06:40 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:45 AM

Issue

How do you configure the I/A Series R2 LON Tunnel for operation with the WorkPlace Tech Tool software?

Environment

I/A Series (Niagara) R2 software, release 4.31 or later

WorkPlace Tech Tool Software release 5.x

Cause

Need information on the entire process of configuring the I/A Series R2 LON tunnel software to work with the WorkPlace Tech Tool software running on Windows XP.

Resolution

There are four parts to configuring LON Tunneling.

A. UNC configuration

  1. The UNC must be licensed for vlon (in the features line)
  2. Install the VLON jar file into the UNC using the Configure Modules function within the Admin tool Installation Wizard.
  3. There are no configuration requirements for the VLonService in the UNC.

B. Check for an available LON port in WorkPlace Tech

  1. Open WorkPlace Tech but do not open a project.
  2. From the "Tools" menu, select "Configure Communications"
  3. Select the Lonworks radio button then click [Change]
  4. Click the pulldown arrow in the "Select a network interface device driver" selection box.
  5. Make a note of the LON ports currently defined.  This list will be used when configuring the tunnel on the PC.
  6. Click [Cancel] to close the communications configuration process then close WorkPlace Tech.

C. Niagara LON Tunnel configuration on PC

  1. Download the "NiagaraLonTunnel.exe" module from The Exchange
  2. Install the NiagaraLonTunnel service on the Windows XP PC by running the downloaded NiagaraLonTunnel.exe program.
  3. From the Windows Control Panel, open the "Niagara App Tunnel" applet and select the LON tab if more than one tab is displayed.
  4. In the LON port name field, select a value not identified in step B.5, above.
  5. In the Host Address field, enter the IP address of the UNC.
  6. You may enter a UNC station User Name and Password in the two fields or those fields may be left blank.
  7. If you have entered a User Name and Password, the Silent Mode checkbox may be checked to prevent the LON Tunnel connection window from being displayed each time the connection is established.
  8. Click [OK] to close the Niagara Application Tunneling window.
  9. In the Windows Control Panel, double-click on Administrative Tools then double-click on "services".
  10. In the displayed list, locate "Niagara LON Tunnel", right click on that entry and click "Restart" in the displayed list.
  11. Wait for the Service to restart.  If Windows reports that it cannot restart the service, it will be necessary to close all application windows and restart Windows.  After restarting Windows, continue with part D, below.
  12. After the service restarts, close the Services window and close the Windows Control Panel.

D. Configure WorkPlace Tech Communications.

  1. With the WPT application open,  select the "Tools" menu, then select "Configure Communications".
  2. Select the Lonworks radio button then click [Change].
  3. Click the pulldown arrow in the "Select a network interface device driver" selection box
  4. Select the LON# port name entered in step C.4, above.
  5. Check the "This is a VLon device" checkbox.
  6. Click [OK] to save the settings.
  7. When you attempt to establish communications with the LON network, the "Niagara Lon Tunneling Logon" window will be displayed if "Silent Mode" was not selected in step C.7.
  8. If "Silent Mode" was selected in step C.7 and the UNC login failed, the "Niagara Lon Tunneling Logon" window will be displayed to allow entry of a different user name & password.
  9. The connection via the LON tunnel is available for use. 
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5882
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore