Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to configure SevenReports on a Remote Client or for Third Party Access

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to configure SevenReports on a Remote Client or for Third Party Access
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2063 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to configure SevenReports on a Remote Client or for Third Party Access

Product_Support
‎2020-09-16 04:50 PM

Last Updated: ContentModerator Explorer ‎2025-09-25 02:45 AM

Issue

Can a Remote Client run I/NET Reports (SevenReports) from the I/NET Seven Server's SQL database?

Product Line

TAC INET

Environment

  • I/NET Seven
  • SevenReports

Cause

In a Remote Client configuration, the local SQL database is not used and is typically blank.  To enable the local SevenReports engine to connect to the I/NET Server the ODBC data source must be configured to successfully connect to this server workstation. 

Resolution

To download more detail instructions please Click Here

Remote Client:

The following procedures describe how to configure the local I/NET Seven ODBC data source to communicate with the SQL server on another I/NET Seven workstation.


  1. Open the ODBC Data Source Administrator editor. (Control Panel / Administrative Tools)
  2. In the ODBC Data Source Administrator editor, click the System DNS tab, highlight the Seven ODBC data source, and click Configure....
  3. In the DSN Configuration editor, use the Server field to specify the name of the I/NET Seven workstation and SQL Server instance that will be used as the server for this workstation.
  4. Click Next and enter the third-party Login ID and Password appropriate for the selected server. If the server is using the default settings for these parameters, the Login ID will be INetThirdParty and the Password will be passinetdb3p_SE.
  5. Click Next two more times and then click Finish.
  6. In the resulting window, review the summary of settings. If necessary, you can use the Back button to return to previous screens and make changes to the configuration.
  7. Click the Test Data Source... button to test the connection.
  8. Click OK to close the Test Results window.
  9. Click OK to close the DSN Configuration editor.
  10. Click OK to close the ODBC Data Source Administrator editor.

Third-Party Applications

Use the following procedures to create a new ODBC data source on a PC that is not running I/NET Seven. The purpose of this task is to allow local third-party applications to communicate with I/NET Seven running on another PC.

  1. Open the ODBC Data Source Administrator editor. (Control Panel / Administrative Tools)
  2. In the ODBC Data Source Administrator editor, click the System DNS tab and click Add....
  3. In the resulting window, scroll through the list and highlight the driver appropriate for the version of SQL Server installed on your PC: 
    - For MSDE/SQL Server 2000, select SQL Server.
    - For SQL Server 2005, select SQL Native Client.
    - For SQL Server 2008, select SQL Native Client 10.
  4. Click the Finish button.
  5. In the DSN Configuration editor, make the following settings: 
    - Define the data source Name as “Seven ODBC”. 
    - Define the Description as “ODBC Connection for I/NET Seven”. 
    - Use the Server field to specify the name of the I/NET Seven workstation that will be used as the SQL server for applications on this PC.
  6. Click Next and make the following settings: 
    - Select the With SQL Server authentication using a login ID and password entered by the user option.
    - Near the bottom of the editor, enter the third-party Login ID and Password appropriate for the selected server. If the server is using the default settings for these parameters, the Login ID will be INetThirdParty and the Password will be PassInetDb3p_SE.
  7. Click Next two more times and then click Finish.
  8. In the resulting window, review the summary of settings. If necessary, you can use the Back button to return to previous screens and make changes to the configuration.
  9. Click the Test Data Source... button to test the connection.
  10. Click OK to close the Test Results window.
  11. Click OK to close the DSN Configuration editor.
  12. Verify that the new ODBC data source has been added to the list of System Data Sources.
  13. Click OK to close the ODBC Data Source Administrator editor.

More detailed information is also available on Extranet in TCON301 Chapter 2 - ODBC Driver Interface section.

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (4)
  • Find more articles tagged with:
  • 7334
  • Remote Client
  • RobertAndriolo20
  • Seven Reports
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore