Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

How to de-bounce a noisy sensor signal.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to de-bounce a noisy sensor signal.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2861 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to de-bounce a noisy sensor signal.

Picard Product_Support
‎2018-09-10 07:09 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:45 AM

Issue

Some sensors such as the SCR110-H CO2 produce a noisy signal even when wired according to the documented instructions.

The following is a trend chart of the unfiltered raw signal from the sensor.

Environment

Automation Server

Continuum controllers

TAC Xenta

Cause

Noisy signal is typically caused by common ground wiring of AC power.

Resolution

SOLUTION #1

  • Signal noise can usually be eliminated by using an isolated transformer to power the sensor separately as opposed to using a common transformer that powers up several pieces of equipment.

SOLUTION #2

  • For sensors that support  AC and DC input voltage, signal noise can usually be eliminated by using DC instead of AC power source to power the sensor.

SOLUTION #3

  • Implement a Slew Rate to filter out the noise. As of version 1.7.1, StruxureWare Building Operation does not have a built-in slew rate functionality. Nevertheless, a custom slew rate can be implemented using Script programming.
  • See HowToDebounceANoisySensorSignal.pdf

SOLUTION #4

  • Add a filter (FILT) in a Function Block program after the signal input

Description: The function block is a discrete time first order software filter. The filter time constant is specified in seconds with the Time Const parameter. The initial block output value is zero.

The filter algorithm is

y(k) = y(k-1) +1/1+T/h(u(k)-y(k-1))

where y(k) and u(k) are the filtered and unfiltered values at time k, respectively,h is the sampling interval (i.e. the application program cycle time), and T is the filter time constant. If the time constant is less than or equal to zero, no filtering is done. To obtain a good filter function, the time constant should be set significantly greater than the application program cycle time. This filter algorithm is based on a straightforward backward difference approximation of the continuous time derivative operator.

SOLUTION #5

  • Ensure you are not using older versions of the IO Firmware. As detailed in TPA-SBO-17-0006.00 the firmware should be at least V2.015 in the modules and is available on the Download Center.
Labels (3)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC Vista
Attachments
Tags (3)
  • Find more articles tagged with:
  • 18428
  • fluctuations
  • PeterLarsen24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore