How to create a new database or purge a full SQL (i.e. it has hit the limit of 2G) in Vista IV

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to create a new database or purge a full SQL (i.e. it has hit the limit of 2G) in Vista IV
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2611 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to create a new database or purge a full SQL (i.e. it has hit the limit of 2G) in Vista IV

Picard Product_Support
‎2018-09-07 01:20 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:45 AM

Issue

How to create a new database or purge a full SQL (i.e. it has hit the limit of 2G)

Product Line

TAC Vista

Environment

TAC Vista 4.X

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

Log data has filled the 2GB limit of the SQL database.

Resolution

How to purge a full SQL (if you've hit the limit of 2G)

Before deleting the database or creating a new one:

Check the $queues/insertevents and $queues/insertlogvalues folders in the Vista database. This folder may contain "queued" files waiting to be written into the SQL database. If these queues have significant amount of data stored as a result of the SQL being full, you may delete these files if the data is not needed. If the data is needed, it will be written to the new SQL Database when Vista starts.

In some cases, the $queue folders may be so large that even creating a new database won't allow the Vista Server to run. If this is the case and the $queued items are not needed, delete them from their directories. If you find that there is an abundant amount of queued files it may be easier to delete them using DOS.

This can be done by navigating using the "cd" and "cd.." command prompts to c:\TAC\Vista\VistaDb\$queues. There you will find \insertevents and \insertlogvalues. You can clear both directories using the "del" command.

It is recommended to stop the SQL Server and DSS Writer before attempting to delete any queued files. You can stop the SQL Server by double-clicking on the icon in the task bar and choosing to "Stop". You can locate the DSS Writer by right-clicking on My Computer and selecting "Manage". Navigate to "Services and Applications\Services" directory and look for "TAC DSS Writer Service". Right click on this service and select Stop.

If the data is not needed:

Simply go to ...Microsoft SQL Server/MSSQL$TACVISTA/Data and delete the old database. Before doing so, you may need to stop the SQL Server.  Then following steps in "If the data is needed" section below.

If the data is needed:

The simplest way to get a fresh DB is to create one. This is done using TAC Vista SQL Setup which can be downloaded from the Buildings Business Extranet: Global. Make sure that you download the SQL Setup for your Vista product version.
In the Vista SQL Setup program, select your SQL Server - pcname\TACVISTA, Chose Windows Authentication if Vista is managing the Database (recommended in the Vista Install), "Login", enter the name of the database (perhaps "NEWtacdatalog" to be created, and select the login pcname\TACA_pcname, and "Create".

This will create a new database to which you can now point the Vista Server. In Vista Server Setup, under the SQL Tab, change the database to this newly created database, click "OK".

You can keep the old database to export for viewing or if you plan on upgrading to SQL Enterprise and merging the data in the future.

 

NOTE: Sometimes when this is done without first detaching or deleting the database from the SQL, the DSSwriter or TACA user stops working. Detach/Delete the database with SQL Management Studio Express and reinstall the system to solve this.
 

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3005
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore