Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to Remove the Routing Tables in a Device or PC

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Remove the Routing Tables in a Device or PC
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3421 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Remove the Routing Tables in a Device or PC

Product_Support
‎2018-09-11 04:34 AM

Last Updated: ContentModerator Explorer ‎2025-09-25 02:44 AM

Issue

  • Remove the Routing tables from I/NET and Xenta 527 devices
  • Host conflict or station conflict error messages displayed at the I/NET Host.
  • Incorrect Links, Hosts and IP addresses that do not exist in your Network are shown when penetrating Network Configuration.

Product Line

Other, TAC INET, TAC Vista

Environment

  • I/NET IP Routers
  • Xenta 527

Cause

Host or station conflict errors can be caused by old information stored in a routing table. From time to time, it may be necessary to purge that information and allow the tables to be rebuilt automatically.

The only way that routing tables can become corrupted is if a laptop was used to connect to the system from a different Network or from the Outside. Once connected, its IP table is broadcasted to the other devices like PCs and NPRs, thus populating the table with entries that does not belong or is non-existent for this location or system. 

Resolution

Managing I/NET Routing Tables

 

I/NET Host Workstation

View the I/NET Routing Table

  • See Viewing the routing tables on a PC using I/NET Seven for complete instructions.

Delete a Single entry in the I/NET Routing Table

  1. Go to Start > Run
  2. Type Telnet and hit Enter
  3. Type open, hit the space bar, then enter the IP address of the PC
  4. Press Enter
  5. When the login comes up, type csi, hit enter
  6. Type LA  and hit enter to list all routing table entries
  7. Type ipdel xxx.xxx.xxx.xxx with xxx.xxx.xxx.xxx being the IP address of the device you wish to delete
  8. Press enter

Clearing the I/NET Routing Table

  1. Shutdown the I/O Server
  2. Open Windows Explorer
  3. Browse to C:\INET Seven Data (or C:\Program Files\INET Seven)
  4. Delete the .dat files (you may want to save a backup to another location)
  5. Delete the routing table from any device listed as a Reference Host or the table will repopulate
  6. Start I/NET

Other Method:

See Bogus Links, Hosts and IP's in Netcon for instructions on using the delall command in Telnet

 

 

Xenta 527-NPR; Xenta 913; Xenta 527 Web Server (See Clear the IP routing tables of a Xenta 913)

 Viewing the I/NET Routing Table

  1. View Connecting a serial cable to a Xenta 5/7/9xx controller to configure HyperTerminal to communicate to the Xenta Device.
  2. Log into the Xenta Device as the root user
  3. At the dsh/> type “inet ip”
  4. Press enter

Deleting a Single entry in the I/NET Routing Table

  1. View Connecting a serial cable to a Xenta 5/7/9xx controller to configure HyperTerminal to communicate to the Xenta Device.
  2. Log into the Xenta Device as the root user
  3. At the dsh/> type “inet ipdel” then the IP address of the device you wish to delete
  4. Press enter

Clearing the I/NET Routing Table

  1. View Connecting a serial cable to a Xenta 5/7/9xx controller to configure HyperTerminal to communicate to the Xenta Device.
  2. Log into the Xenta Device as the root user
  3. At the dsh/> type “inet delall”
  4. Press enter
  5. Type “inethost” and press enter
  6. Verify or set the Reference Hosts
  7. Clear the routing table from any referenced device to ensure old data is not repopulated
  8. Restart the Controller to re-populate the routing table

 

You can also realize this through the web page of Xenta device. Open the web page of Xenta controller, browse to Utilities-I/NET-I/NET Command Line, and type the command below or above. The result is the same as using HyperTerminal, which is also an easier way.

Typing “inet help” or “inet” gives every I/NET option within the controller

  • inet - I/NET Help
  • ip - Display IP table list
  • ls - Display Link/Station table list
  • cp - Display Compressed table list
  • gp - Display Global Point table list
  • mm - Message masking
  • all - Display all lists
  • ipadd - Add an IP address to the tables
  • ipdel - Delete a single ip record
  • delall - Delete all ip records

 

NPR-2000

Viewing the I/NET Routing Table

  1. Go to Start>Run then type “Telnet” and hit Enter
  2. Type open hit the space bar then enter the IP address of the NPR
  3. Press Enter
  4. When the login comes up, type csi
  5. hit enter
  6. Type “LA”  and hit enter to list all routing table entries

Deleting a Single entry in the I/NET Routing Table

  1. Go to Start>Run then type “Telnet” and hit Enter
  2. Type open hit the space bar then enter the IP address of the NPR
  3. Press Enter
  4. When the login comes up, type csi
  5. hit enter
  6. Type “LA”  and hit enter to list all routing table entries
  7. Type “ipdel xxx.xxx.xxx.xxx” with xxx.xxx.xxx.xxx being the IP address of the device you wish to delete
  8. Press enter

Clearing the I/NET Routing Table (See Bogus Links, Hosts and IP's in Netcon)

 Go to Start>Run then type “Telnet” and hit Enter

  1. Type open hit the space bar then enter the IP address of the PC
  2. Press Enter
  3. When the login comes up, type csi
  4. hit enter
  5. Type “LA”  and hit enter to list all routing table entries
  6. Type “delall” and hit enter to clear the table

 

Appendix A: I/NET Telnet Commands Glossary:

  • Help – Displays all available commands in the NPR or I/O Server.  Note there are some differences between the NPR and I/O Server.
  • ipadd a.b.c.d – Adds the IP to the routing tables.
  • ipdel a.b.c.d – Deletes the IP from the routing tables.
  • gpadd LLSSPPBBTT XX | a.b.c.d – Adds a global point link or global point IP to the routing tables.
  • delall – Deletes “all” local routing table entries.
  • setpass password – Change the telnet login password (6 characters max).
  • +cpdel LLLL SS – Deletes the specified link/site address from the CP table.
  • +debug gp on|off – Turns global point debugging on or off.
  • +reboot – Reboots the NPR.
  • +wdog – Reports watchdog errors.
  • +wdogrst – Clears the watchdog errors.
  • +Dx – Toggle debug output to COM3.  x=0/1; 0 = off, 1=on.
  •  

List Commands:

  • +LR – IP Stack routing table.
  • LI – IP routing table.
  • LM – IP routing masks.
  • LL – Link/Station routing table.
  • LG – Global point routing table.
  • +LC – Compressed routing table.
  • +LS # - Compressed routing table: station to site maps for the specified link #.
  • LA – All routing tables.
  • LU – System metrics.
  • *LD – Dial maps.
  •  + = NPR only
  • * = Host PC only

 

Appendix B: Method for Clearing Routing Tables at a Large Site

See Possible solution to doing a Telnet session with a system wide firewall setup.

 

Appendix C: Suggested Reference Host Settings

 

Click here to be linked to the TAC INET Seven Getting Started.
Click here to be linked to the TAC INET Seven Operator Guide.

 

A Reference Host is any TAC I/NET workstation, NPR, or Xenta 527/527-NPR that will serve as a source of IP addresses. Any of these devices attached to an Ethernet LAN can be used as a Reference Host.

Each time I/O Server is started on a workstation, it provides the workstation’s IP address to each remote host designated as a Reference Host. I/O Server also requests and receives a list of all host IP addresses that are known to the remote host at that time. I/O Server must be running on the remote host for this address exchange to occur. I/O Server compiles and maintains a list of all the remote hosts that it learns about. Ultimately, all hosts in the network will know the IP addresses of all the other hosts.

Ideally, you should determine 1 or at most 2 devices to serve as your Reference Host.  This device would ideally be a Xenta Server or an NPR, but a Host workstation that has I/O Server running 100% of the time will work as well. 

All devices on the system will use this as a single Reference Host. No others are needed.  When the device comes online it will contact the Reference Host and get the site’s Routing Table.  The Reference Host can have an empty routing table. 

Once the Routing Table is shared, Reference Hosts are no longer needed.  You can leave the single entry in place. This will allow a quick recover, in the event of a critical system failure.

Here are a few reasons for using multiple Reference Hosts:

  • Temporarily add a new device as a Reference Host on the Sites Reference Host or a workstation to aid in bringing it online
  • A large site may desire to have 2 Reference Hosts in case one is offline when a device comes online.
  • An I/NET site that spans multiple locations may wish to declare a local Reference Host for each building and a network Reference Host

     

Labels (2)
Labels:
  • TAC INET
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 12759
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore