Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,845
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1842 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 88
    • 89
    • 90
    • …
    • 93
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

BACnet folder does not appear under Hardware folder on AS after backup is restored.

Issue After restoring a backup set to an AS, MSTP communication is lost and no BACnet folder appears under the System Hardware folder. Environment AS System Time Backup Restore Cause System time was not set in the AS prior to restoring the backup. Resolution Set system time prior to restoring the backup. The BACnet folder may be restored if the AS system time is set subsequent to restoring the backup and the AS is warmstarted.
View full article
Picard Product_Support
‎2018-09-06 09:17 AM

Labels:
  • EcoStruxure Building Operation
998 Views

Monitoring an external variable outside of SmartStruxure Lite to trigger a lua script

Issue At times it is necessary to monitor an external variable to trigger action in SmartStuxure Lite Environment Smart Struxure Lite Smart Struxure Continuum AS MPM Windows 7 Windows Server 2008 Cause Need the ability to trigger actions from an external variable to run a lua script Resolution Use a lua script in your MPM that copies the value of ME.PG#_ENABLE.value to an Analog/binary value. This value can then be seen from the AS or BCX through bacnet and you can have the AS or BCX do different functions depending on that value
View full article
Picard Product_Support
‎2018-09-06 09:17 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
1212 Views

Triggered Time Stamp behavior

Issue @TriggeredTimeStamp does not always report the last time an object transitioned to an off-normal state. Environment Alarms Substitution Codes Event Notifications. Cause Both the Normal and the Reset alarm states represent conditions where the alarmed object has assumed an acceptable value and is not in alarm Reset = The object has returned to a normal state but the return to normal notification has not been acknowledged. Normal = The object has returned to a normal state and the return to normal notification has been acknowledged. The TriggeredTimeStamp value is updated only when the object transitions from a Reset Alarm State to an Alarm Alarm state. The TriggeredTimeStamp value is not updated when the object transitions from an Alarm Alarm State to a Reset Alarm state. If an object goes into alarm and that alarm event is never again acknowleged, the Triggered Time Stamp will continue to reflect that initial alarm transition time regardless of how many times the object goes into and out of an alarm state. Resolution In order to get the Triggered Time Stamp to update, the notification must be acknowleged so that the alarm can return to a Normal state (rather than Alarm State = Reset) before it transitions to Alarm. 
View full article
Picard Product_Support
‎2018-09-06 09:16 AM

Labels:
  • EcoStruxure Building Operation
1949 Views

B3 device is offline after deploying successfully from PCS

Issue An offline edit in PCS deploys successfully. When viewed in Workstation, the Automation Server is online, but all b3s are offline. Product Line EcoStruxure Building Operation Environment SmartStruxure 1.50 PCS AS 1.5 BACnet interface Cause The b3s have a BACnet Device ID which is different from that assigned to b3s in PCS. The BACnet device ID can not be modified in PCS after it has been assigned. Resolution It is best to modify the BACnet Device ID in Continuum: Use a BCX4040. Connect with b3 devices one by one or together Bring b3s online in Continuum Workstation Modify the BACnet Device ID for each b3 to the BACnet Device ID assigned in PCS Go back to SBO Workstation. b3s should be online.
View full article
Picard Product_Support
‎2018-09-06 09:16 AM

Labels:
  • EcoStruxure Building Operation
1105 Views

Valent RTUs with LynxSpring BACnet MSTP controllers go offline about every 30 minutes.

Issue After about 30 minutes of communicating fine they will go off line in the AS. Environment BACnet, AS v1.41 Cause Time sync service running on the Lynxspring JACEs Resolution Restarting the Lynxspring controllers temporarily resolves the offline problem. Turning OFF the time sync service running on the Lynxspring JACEs permanently resolved the offline problem. 
View full article
Picard Product_Support
‎2018-09-06 09:16 AM

Labels:
  • EcoStruxure Building Operation
1335 Views

Issues with port 80 after WebReport installed on same machine as ES

Issue Issues with port 80 after  WebReport installed on same machine as ES Environment ES WebReport Cause Port 80 conflict Resolution If you installed everything on the same machine and you didn't change the port on the ES you need to make some changes to avoid port 80 contention First change the ES port from 80 to something else like 8080    Open StruxureWare Building Operation Software Administrator    Change the default port from 80 to 8080    Stop and Restart the Service    Open StruxureWare Building Operation Workstation    Be sure to log in using @localhost:8080 instead of @localhost:80 Then you need to reconfigure WebReport to let I know the ES is using port 8080, this is normally specified during installation, there is an utility that lets you change it very easily which can be downloaded from the community.  
View full article
Picard Product_Support
‎2018-09-06 09:15 AM

Labels:
  • EcoStruxure Building Operation
1168 Views

A PCS deploy fails and an error message comes up with the text "Xif nnn could not be found"

Issue A PCS deploy fails and an error message comes up with the text "Xif nnn could not be found" Environment Project Configuration Server (PCS) StruxureWare Building Operation 1.5 and newer Cause An import originating from a live system that has LON network containing network variables on the local node becomes a potential risk in PCS, but will import correctly as long as no local node variables are deleted. There is not currently support for dynamic update of changes on the local node in PCS. Resolution Leave an import containing Local Node variables unchanged, if importing to PCS
View full article
Picard Product_Support
‎2018-09-06 09:15 AM

Labels:
  • EcoStruxure Building Operation
1131 Views

Web Reports showing wrong values in meter consumption reports

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue When viewing a meter consumption report, the values shown in the report does not match the values in the extended trendlog in SmartStruxure Environment SmartStruxure 1.5 and below Web Reports Cause Generally this will happen if the meter is reset and that time the last value of that meter will set a BaseValue. To calculate the total consumption of the meter we are adding the BaseValue to the offset. This means that the value shown will be the logged value + the offset. In some cases however you would want to completely reset the log and just show the same values that are represented in the extended trendlog. It has been identified, that a defect causing a trend logging a 0 after each restart triggers this reset. Request the latest hotfix for 1.5 from Product Support in order to avoid this happening in the future.   Note: This issue (Defect #26360) has been fixed in 1.6.1 release. Resolution 1. Open "SQL Management Studio" and connect to the database "StruxureWareReportsDB" 2. Locate the log you want to reset using this query: SELECT * FROM tbLoggedEntities 3. Note the ID of the log you want to reset 4. Reset the log using the following query, replacing xxxx with the ID of the log DECLARE @id INT SET @id = xxxx UPDATE tbLoggedEntities SET BaseValue = 0 WHERE ID = @id UPDATE tbLogTimeValues SET FloatValue = OdometerValue WHERE ParentID = @id ##WARNING## The above script will reset BaseValue to 0 this may impact on any previous Meter Readings.  Please contact Product Support to discuss this if you have concerns before applying this script.
View full article
Picard Product_Support
‎2018-09-11 01:49 PM

Labels:
  • EcoStruxure Building Operation
1742 Views

How to relinquish a priority on multiple BACnet objects from a list view or search

Issue How to relinquish a priority on multiple BACnet objects from a list view or search. Product Line EcoStruxure Building Operation Environment Workstation Automation Server Enterprise Server Cause Need to relinquish a value in the priority stack for multiple points at once. Resolution In the list view or search select all of the objects in question (IMPORTANT: Only objects of the same class type should be selected) Open the property grid by clicking the red check mark. Go to the Command tab and remove the value from the priority that is to be relinquished then save the change NOTE: As of 1.5 the above steps work ONLY for objects of analog type. In the screen shot above: Use back space to remove the 1, leaving the field blank Save the change SBO will relinquish priority 16 on all the objects selected in the list view or search. 
View full article
Picard Product_Support
‎2018-09-11 01:39 PM

Labels:
  • EcoStruxure Building Operation
1865 Views

Which versions of SIGNAL can be migrated to SBO?

Issue Which versions of SIGNAL can be migrated to SBO? Environment SIGNAL Cause The migration manual does not identify which versions are accepted. Resolution Two versions of SIGNAL can be backed up and migrated to SBO:  Version 4.4.1 (for Windows 95/98) and Version 5.0.0 (for Windows XP).
View full article
Picard Product_Support
‎2018-09-06 09:13 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
883 Views

Why is the i2/ b3887 RAM memory not saved on power failure?

Issue i2887/ b3887 Cool starts on Power failure Environment i2887, b3887 i2887-L-230, b3887-L-230 i2887-L-115, b3887-L-115 Cause The i2887 and b3887 do not have a RAM battery backup. Resolution The i2/b3887 is one of the range of low cost i2/b3 controllers that does not have a RAM backup battery. It has no concept of a Warm start that would save working values in the RAM. It does however have Flash Memory that allows the controller to save all of its points and programs. After a power outage these points / programs will be copied into RAM and start running from their first line (if they are Autostart) in what is called a Cool Start. Its ACCRestartMode mode will be ACCCoolStartOnly.   Other i2/b3 controllers that do have a RAM backup battery will allow the ACCRestartMode to be changed as required.
View full article
Picard Product_Support
‎2018-09-06 09:12 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
982 Views

Extended Trend Logs stop updating in ES

Issue The Extended Trend Logs stop updating in Enterprise Server.  When the ES is rebooted the trend logs resume. Product Line EcoStruxure Building Operation Environment Enterprise Server Cause The Extended Logs Maximum transfer interval is set too low causing it to trigger again before it has managed to finish the last read. Resolution Increase the Maximum transfer interval setting of the Extended Log.
View full article
Picard Product_Support
‎2018-09-06 09:12 AM

Labels:
  • EcoStruxure Building Operation
1987 Views

ES or AS crashes when editing a Script function and never comes back up

Issue When editing a Script program, the Automation Server or Enterprise Server crashes when clicking "Save." After that, the connection is never restored to the server. The server needs to be formatted, software reloaded, and a backup restored to it. Product Line EcoStruxure Building Operation Environment SmartStruxure 1.0.0 to 1.5.0 Cause In SmartStruxure 1.5.0 and earlier, publics were not supported in Script functions although they could be used. If used, the server will crash in some cases and render the database unusable. Resolution The workaround is to not use publics in Script functions in the affected versions. The issue is solved from version 1.6 RC.
View full article
Picard Product_Support
‎2018-09-06 09:11 AM

Labels:
  • EcoStruxure Building Operation
901 Views

Manually add individual components to a Component Library

Issue Manually add individual components to a Component Library Environment TGML Graphics Editor Cause Components are sometimes stored as a file type TGMLCOMPONENT File with the extension .tgmlcomponent file. Resolution Open the Graphics Editor and Select a Component Category you wish to add components to Open Windows Explorer and browse to the .tgmlcomponent files. Drag the file(s) from Windows Explorer to the the TGML Graphics Editor Component Category window. Click OK or press enter to acknowledge each file as it is added.
View full article
Picard Product_Support
‎2018-09-06 09:11 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1836 Views

Modbus communication stops and doesn't start again until the COM port is configured again in the Automation Server

Issue The Modbus communication stops from time to time, and never gets back until the COM port is reconfigured. The device is still online; it is only the values that will not update. This is usually only an issue if Modbus groups are used. Product Line EcoStruxure Building Operation Environment SmartStruxure 1.5 Automation Server Cause If a trendlog with a very long sample time (e.g. 1 hour) is set to log a point and nothing else is bound to the Modbus device, all values from the device will be updated at the same interval as the trendlog. This is solved in newer versions. Resolution Add a single Modbus point to a new Modbus group. Set the group poll rate to the same as the Device poll rate. To enable polling of the Modbus point, add an alarm that will not activate. This will result in polling of the device at the group poll rate.
View full article
Picard Product_Support
‎2018-09-06 09:11 AM

Labels:
  • EcoStruxure Building Operation
1529 Views

Limit of Function block under a Local node

Issue How many Function block can i add under a Local node Environment Struxureware Server (1.6) Cause Struxureware was built around that 50 function block should be supported under a local node Resolution Struxureware was built around that 50 function block should be supported under a local node however we never added a limit so you can add more, this is however not supported.
View full article
Picard Product_Support
‎2018-09-06 09:11 AM

Labels:
  • EcoStruxure Building Operation
975 Views

Report Server Agent historical reads fail intermittently

Issue The historical reads will fail from time to time due to process data failure Environment Report Server 1.6.0 and below Cause This is due to the ValueAfter and ValueBefore column in the tbEvents table of Reports db. ValueAfter and ValueBefore Columns were designed as float datatype, When the Reporting Agent tries to convert the NeuronId of a LonWorks device (which is one of the data for ValueAfter and Valuebefore Columns) as a float then this issue occurs. Due to this Reporting Agent will trigger the ES Read again. Resolution With the change of ValueAfter and ValueBefore to nVarChar datatype, the issue gets solved. These changes are included in Web reports 1.6.1. 
View full article
Picard Product_Support
‎2018-09-06 09:09 AM

Labels:
  • EcoStruxure Building Operation
1103 Views

'TotalHistoricalRecords read so far' counter does not match the number of records read.

Issue 'TotalHistoricalRecords read so far' counter in the reporting agent log does not match the number of records read. Below is an example taken from a Reporting agent log: INFO 2014-12-09 10:41:18 - TotalHistoricalRecords read so far = 59 INFO 2014-12-09 10:41:18 - The log has IncludeInReports = true INFO 2014-12-09 10:41:18 - Trend LoggArray.FirstRecordInSource= 1 INFO 2014-12-09 10:41:18 - Trend LoggArray.LastRecordInSource= 9797 INFO 2014-12-09 10:41:18 - Last record stored in reports database = 9780 INFO 2014-12-09 10:41:18 - Getting records from server: start sequence = 9781, Number of recordsrequested = 17 INFO 2014-12-09 10:41:18 - TotalHistoricalRecords read so far = 75 In this case 17 records are requested: 9797-9780 = 17. Counter for 'TotalHistoricalRecords read so far' = 59 before getting logs. After getting logs, 'TotalHistoricalRecords read so far' = 75. 75-69 = 16.  Environment SmartStruxure WebReports Enterprise Server  Cause This is caused by 'null' values in the extended trend log being read. Any value that equals 'null' in the extended trend log will not be added to the WebReports SQL database. Resolution None. The product is working correctly.
View full article
Picard Product_Support
‎2018-09-06 09:09 AM

Labels:
  • EcoStruxure Building Operation
1159 Views

All Script programs in the AS have status unloaded

Issue All Script programs in the AS have status unloaded. How do I get them working again? Environment Struxureware Building Operation 1.5. Cause A script program had an output binding that was linked to a PVR block in a Function block program. It looks like on the server boot up, the script engine tries to start up before the function block engine does and when an output of a script sees that the binding is null, it throws an exception and shuts down the script engine. This only seems to be a problem when binding a script programs output to any PV type in a function block program. Resolution  Bind to a Numeric output instead of a PVR block in the function block program.
View full article
Picard Product_Support
‎2018-09-06 09:09 AM

Labels:
  • EcoStruxure Building Operation
3258 Views

Cannot log into SQL Server Management Studio after changing the sa password.

Issue After changing the sa password in SQL Server Management Studio, subsequent logon attempts fail. Environment SQL Server 2008 Cause It appears that SSMS retains the last saved password in its cache when the Remember Password checkbox is selected, even when the new password is entered into the password field. Resolution Deselect the Remember Password checkbox and login to SSMS. 
View full article
Picard Product_Support
‎2018-09-06 09:08 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1219 Views
  • « Previous
    • 1
    • …
    • 88
    • 89
    • 90
    • …
    • 93
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of