Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

What to select when downloading the NXE file?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What to select when downloading the NXE file?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • DavidFisher
    DavidFisher
  • PeterLarsen
    PeterLarsen
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1384 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What to select when downloading the NXE file?

Picard Product_Support
‎2018-09-06 09:46 AM

Issue

Have to download a new NXE file, and I have now 4 possibilities:

  1. Keep current configuration in device
  2. Download current configuration to device
  3. Download default configuration to device
  4. Upload configuration from device.
     

So, what happens when I select the different lines?

The 4 options available when commissioning a Xenta 100 Series device as well as performing a NXE download are misleading.

Environment

SmartStruxure 1.4.1 and 1.5

LonWorks Interface

Cause

Current descriptions of the four choices are not clear when the Device Application (NXE) file is downloaded at the same time as configuration parameters to the device. The 4 actions are executed after the NXE download.  Before downloading or uploading the device configuration, carefully consider the effects of overwriting the current device configuration in the LonWorks device or Building Operation server.

Resolution

When the Device application file check box is selected during the Commissioning of a LonWorks device the following is true for each of the four options:

  1. Keep current configuration in device
    The NXE file is downloaded, but as the NXE also contains the default parameters which will place the configuration in the device back to default. This causes a mismatch between Building Operation database and the properties in the device. To get the device to work you must perform a Download the device configuration.
  2. Download current configuration to device
    The NXE file is downloaded, and the configuration is then downloaded from the Building Operation database to the device. The device works OK after the download.
  3. Download default configuration to device
    As the text says, the Default configuration is downloaded after the NXE file is downloaded, and also loaded into the Building Operation database.
  4. Upload configuration from device
    The NXE file is downloaded, but as the NXE also contains the default parameters, the configuration in the device will go back to default. After the NXE file is downloaded, the configuration in the device (which now is the default configuration) is automatically uploaded to the Building Operation database. If this option is picked your device will be set back to the default setting along with your Building Operation database after the download. This option should not be selected as any configuration made to the device will be lost.

The 4 actions are executed after the NXE download.  Before downloading or uploading the device configuration, carefully consider the effects of overwriting the current device configuration in the LonWorks device or Building Operation server.

Future plans (beyond 1.5) are to move the Device Application file (NXE) download to a separate dialog window to perform this function. 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 15361
  • 24333
  • defect
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore