BACnet b3 controllers - Backup to Flash operation.
  • BACnet b3 controllers - Backup to Flash operation.
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
‎2018-09-06 09:47 AM
Backing up b3 controllers to flash.
BACnet
b3 controllers
Backup to Flash
B3 Backup to Flash does not operate as expected.
The b3 controller Backup to Flash operates as follows;
System variables that indicate the status of Flash / Backup.
  • StatusBackup – Indicates if backup is needed, has been done, or is in progress.
  • StatusFlash - Indicates that the flash is empty, valid or has failed.
  • LastBackup – Indicates the time and data of the last backup.
Backup to Flash Operation.
  • Downloading a controller will clear the flash memory.
  • Resetting a controller will clear the flash memory.
  • A download to a controller which fails, will clear the flash memory.
  • Setting the controller "RestartMode" variable to Cool Start, will reload the controller from flash memory on power up, assuming there is a valid backup available..
  • Downloading a single object to the controller does not clear the flash memory.