Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,899
  • TAC IA Series 1,682
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2029 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 80
    • 81
    • 82
    • …
    • 102
  • Next »
Label: "TAC Vista" Show all articles

Excel date and time not able to be formatted in Vista report

Issue Vista reports running on EXCEL 2010 do not save the date format correctly. Environment Microsoft EXCEL 2010 Vista 5.1.5 and below Cause Excel 2010 is not supported on Vista 5.1.5 and below Resolution To get the date and time format to work correctly with Vista uninstall Excel 2010 and install Excel 2007. The other option is to upgrade to Vista 5.1.7 which supports Excel 2010 A possible  workaround  is to insert your trends into the Work Area of the report. That is the area to the right of the main page. Then you can copy this information to the main page and format the cells on the main page.    
View full article
Picard Product_Support
‎2018-09-06 01:46 PM

Labels:
  • TAC Vista
1058 Views

Xenta 102-B nviManOverride functionality

Issue Xenta 102-B nviManOverride allows for flow or percentage overrides. But since this controller is intended to be used along with a Belimo flow controller/actuator, how do these modes of operation differ? Environment Xenta 102-B Cause Flow control is not actually an option for this controller. Flow values will be interpreted as desired percentages of airflow. Resolution nviManOverride.state = HVO_PERCENT, nviManOverride.percent = 35% The controller fixes the Airflow output (Y1) at 35% (3.5V) nviManOverride.state= HVO_FLOW_VALUE All of the flow values are actually being treated as percentages ... there is no way to set it to a desired flow. (nviManOverride.flow X nciNomFlow / 100) is limited to 0-100% and sent to the Airflow output (Y1). Emergency Override can override these setting, as can setting the controller to slave mode (the overrides would have to be performed on the master controller in that setting). The way to release these states is to set the nviManOverride.state to any value other than HVO_PERCENT or HVO_FLOW_VALUE. Those are the only two values accounted for in the logic.
View full article
Picard Product_Support
‎2018-09-06 01:45 PM

Labels:
  • TAC Vista
890 Views

Compressor will not activate on Xenta 121-HP

Issue Compressor will not activate blocking the cooling or heating of the Xenta 121-HP. Environment Xenta 121-HP Cause A compressor temperature lockout exists in the Xenta 121-HP application. The lockout has a minimum and maximum temperature the source signal must be between for the compressor to activate. The source signal changes depending on whether the application uses a air source or a water source. Air Source - nviOutdoorTemp Water Source - nviSourceTemp Resolution Ensure that the source temperature signal is between the compressor lockout minimum and maximum.
View full article
Picard Product_Support
‎2018-09-06 01:45 PM

Labels:
  • TAC Vista
1054 Views

TGML Graphics Editor not opening with Engineering Dongle

Issue TGML graphics Editor will not open even though the Engineering Dongle is connected. Environment TGML Graphics editor Vista IV Cause The Vista IV engineering Dongle is not licensed to allow TGML Graphics Editor to open. It will only allow OGC Graphics Editor to open. This Feature was not included until Vista 5. Resolution Use a Vista 5 Engineering Dongle or download the Demo License to edit TGML files.
View full article
Picard Product_Support
‎2018-09-06 01:44 PM

Labels:
  • TAC Vista
1123 Views

Opening Vista Server hangs on "initializing server functions field bus initializations..."

Issue After launching the Vista Server program, it seems to cycle through its startup process, but stops on: "initializing server functions field bus initializations..."  Vista Server will never finish opening regardless of how long it is left to run and must be forced closed with the Task Manager. When attempting to open a LonMaker drawing, the last process displayed before hang up is: "Opening network connections". Environment LonMaker Vista Cause Corrupted LonMaker database. Possibly due to unexpected termination of the LonMaker program such as a loss of power or Ending the process from Task Manager. Resolution Attempt to open the associated LNS database through LonMaker. It will most likely fail to open. Restore last known good backup. Optionally,  send the damaged database to Echelon Support for further investigation at lonsupport@echelon.com. Field bus is referred to as LNS Server Ports in the Vista world.  If the LNS database will not open, then the Vista server cannot access it.
View full article
Picard Product_Support
‎2018-09-11 08:43 AM

Labels:
  • TAC Vista
1832 Views

How to change the online keyboard layout of a Magelis Opti PC

Issue How to change the online keyboard layout of a Magelis Opti PC. Change input language for the keyboard on Magelis Opti PC. Environment Magelis Opti PC (Touch screen PC OP panel) Cause The Magelis Opti PC runs on windows XP embedded version so you change the keyboard input the same way as any PC. Resolution Open Control Panel and click on Regional and Language settings Click on language tab- Details Add the language you need.
View full article
Picard Product_Support
‎2018-09-06 01:44 PM

Labels:
  • TAC Vista
1353 Views

Not possible to have a zero in the beginning of an address to a M-bus device in XBuilder

Issue Not possible to have a zero in the beginning of an address to a M-bus device in XBuilder.  For example, add an M-bus device in XBuilder. Write a secondary address (used default) with a zero in the beginning. Click OK and the zero in the beginning disappears. Environment Vista 5.1.5 XBuilder Cause This is just a display attribute in XBuilder to trim leading zeros in the address field. Resolution Even if the zero in the beginning disappears in the address box, it will still be used when the Xenta server communicates with the M-bus device. Write the address with a zero as it should be and that address will be used.
View full article
Picard Product_Support
‎2018-09-06 01:44 PM

Labels:
  • TAC Vista
1188 Views

Cannot view SCPTs, UCPTs, or UNVTs in XBuilder

Issue Cannot view SCPTs, UCPTs, or UNVTs in XBuilder. Warning in XBuilder: "2147483647    Warning -1     ____ will be skipped. Unrecognized SNVT type from Vista Database:0" Environment XBuilder LON Devices Xenta 102-AX Xenta 121-HP, 121-FC STR-350 Cause XBuilder can only view, read, and write to SNVTs in a LON device. Resolution There is no way to view SCPTs in XBuilder. If XBuilder is required for transferring data, a work around will have to be found. Instead of writing to SCPTsetPoints, use nviSetpoint, for example. The resulting warning in XBuilder is alerting that it cannot process the information contained in a SCPT, UCPT or UNVT, only SNVT. Therefore the "SNVT type" is unrecognized.
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Labels:
  • TAC Vista
1646 Views

Is it possible to change the default font size from its current value of 15?

Issue The default font size in the TGML Graphics Editor is 15. Can this value be changed? Environment TAC Vista - TGML Graphics Editor Cause Default Font Size in TGML Editor is 15 and it is hard coded in the software.  Resolution It is not possible to modify the default font size. When we change the font size, the TGML editor automatically remembers the last value used.
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Labels:
  • TAC Vista
1758 Views

Loytec L-VIS must be installed in an LNS Network, not a Vista Classic system.

Issue Can the Loytec L-VIS be used in a Vista Classic scenario? Environment Loytec L-VIS Cause The need to have a touch screen interface to a Vista Classic network. Resolution The L-VIS cannot be used in a Vista Classic system because it uses SNVTs to interface the Lon. LNS must be used. A solution to a Vista Classic scenario would be to touch screen PC or tablet to interface the graphics in an Xenta Webserver (5xx,7xx).
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Labels:
  • TAC Vista
1140 Views

Monitoring and configuring the space temperature alarms in a Xenta 121

Issue Triggered an alarm for a Xenta 121 if the space temperature is too high or low from the setpoint. Environment Xenta 121-FC Xenta 121-HP Zbuilder Cause The Xenta 121 controller has a low spacetemp and a high space temp alarm. These alarms are triggered for the following reasons: Low Space temp alarm - In heating mode when space temperature is lower then Setpoint - nciSpaceTempDev High Space temp alarm - In Cooling mode when space temperature is higher then Setpoint + nciSpaceTempDev These alarms can be monitored here: Low Space temp alarm - nvoSystemStatus bit 13 High Space temp alarm - nvoSystemStatus bit 14 Resolution Specify the nciSpaceTempDev by using the ZBuilder plug-in and accessing the Configuration page. On the Lon\Node screen the Space temperature deviation is editable. The default value is 3.6 deg F or 2.0 deg C. Use a value that will not trip the alarms erroneously, but still warn if there is a problem.
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Labels:
  • TAC Vista
1333 Views

Getting SQL Server Limit Alarm (4G SQL Express) in Vista using a Full Version Of SQL Server.

Issue Workstation is alarming that the SQL has reached the 4G limitation, but the Version of SQLServer is a Full version which is unlimited in size. SQL should be able to grow until the hard drive capacity is reached. There seems to be normal functionality of the SQL Server and there are not any $queues building. Environment SQL Vista 5 Cause When Vista is installed, The parameter how large SQL can be is written into the properties of $Backup_LDB. If a Free version of SQL is used, such as the one included in Vista, A limit of 4G or 3820MB is written to this Value. Even if you Install a Full Version of SQL at a later date, this Alarm Limit will remain. Resolution In Workstation, select the Vista Server, this displays the contents of the Vista Server in the Main pane. In the Main pane, double-click on the object $Backup_LDB, this displays the properties of $Backup_LDB in a new window. In the $Backup_LDB property window, Scroll to the last property, "DB Size Alarm Limit (MB)" Increase this value to a higher logical value of your choice considering limitations of the system hard drive space. Note: 1 Gb = 1024 Mb, 1 Mb = 1/1024 Gb and 1 Mb = 0.0009765625 Gb
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Labels:
  • TAC Vista
1055 Views

Active X: could not create object. Error when launching Plug-ins in NL220 or LonMaker installed on Windows 7.

Issue Plug-in will not launch. Results in error "Active X: could not create object" Environment Windows 7 32 bit Windows Vista NL220 LonMaker Vista Plug-ins Cause Needs to be run as an administrator. Resolution Verify Administrator account is logged in. Install Toolpack (or hotfix) as administrator Take note of the installation location, and go to this folder after the installation of the hotfix. The default location for these plug-in application files is: C:\LonWorks\apps\TAC Run file: TACXenta102AXPlugIn.exe, as administrator and click Deregister Plug-in, then Register Plug-in. Open NL220 or LonMaker and register the Xenta 102-AX plug-in.
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Labels:
  • TAC Vista
1611 Views

STR-150 Not Compatible With Software Version 1.1 Xenta 100 Series Controllers

Issue The STR-150 Wall Module with Display is not compatible with Xenta 100 controllers that are earlier than SW-version 1.2. The space temperature (nvoSpaceTemp) is displaying an invalid or default value (either 621.81 degrees Fahrenheit or 327.67 degrees Celsius). In newer versions of Vista the value will display "Invalid Value". Product Line TAC Vista Environment STR-150 Xenta 101-VF Xenta 102-ES Xenta 103-A Xenta 104-A Cause Software for Xenta 100 series controllers previous to version 1.2 is not compatible the STR-150 wall module. Resolution The STR-150 is only compatible with Xenta 100 series controllers that are software version 1.2 or later. If a wall module with display is required for a Xenta 100 controller with software that is older than version 1.2 there are two possible solutions: An identical Xenta controller can be purchased with the latest software version to replace the old controller. An STR-350 stat can be used and connected to the Xenta controller via SNVT bindings.
View full article
Picard Product_Support
‎2018-09-06 01:42 PM

Labels:
  • TAC Vista
2059 Views

Changing a Xenta 102-AX or MR-VAV-AX from SI to Imperial Units using an M/STAT

Issue STR-250 Wall Stat displaying °C instead of °F Environment Xenta 102-AX M/STAT MR-VAV-AX I/NET Vista Cause Device is set to incorrect Engineering Units Resolution Plug the M/STAT into the jack on the thermostat.  The initial display shows the set temperature. Press the Service button.  This prompts you to enter the service mode password.  Default password is 183.  Use the +/- keys to set each digit and the enter key to submit.  If the password is incorrect, the display will blink. If the password is correct, the first menu option – Unit Parameters (UP) – is displayed.  Press enter. Hit the select button until Engineering Units (EU) is displayed.  Press enter to view the current value. Use the +/- keys to change the value between Systeme International (Si) and Imperial Units (iu), press enter. Press the service key to escape out of the menu.  If you are finished configuring the box, escape all the way back out of the service menu before disconnecting the M/STAT.  Disconnecting in configuration mode can leave the stat displaying “00” or other incorrect numbers.
View full article
Picard Product_Support
‎2018-09-06 01:42 PM

Labels:
  • TAC INET
  • TAC Vista
1414 Views

Buttons on an I/STAT or M/STAT are not working on a Xenta 102-AX

Issue An I/STAT or M/STAT plugged into a Xenta 102-AX will display the room temperature but it is not possible to enter service mode -- none of the buttons do anything. Environment Xenta 102-AX M/STAT I/STAT Cause There are different versions of the I/STAT and M/STAT for the Xenta and I/NET product lines. Resolution For use with a Xenta 102-AX, use an I/STAT-A or M/STAT-A For use with an I/NET MR-VAV-AX use either an I/STAT or I/STAT-A, or M/STAT or M/STAT-A
View full article
Picard Product_Support
‎2018-09-06 01:41 PM

Labels:
  • TAC Vista
1325 Views

Opening Zbuilder from LonMaker causes the setpoints to revert to 10°C/50°F.

Issue When Zbuilder is opened from LonMaker the setpoints revert to default values: US - 50°F SI - 10°C Environment LonMaker 3.x Zbuilder 5.1.4 - 5.1.5 Cause If the Region format is English (United States) but the Measurement system is Metric then the value provided to Zbuilder from LNS server is handled improperly. Resolution Change the Region Settings Open the Windows Control Panel and access the Region and Language settings. Click the Additional Settings button to change the Measurement System to U.S. Change the format of the Setpoints Open the LNS browser for any Xenta 121 controller in this database. Find the scptSetPnts and right click and select Change Format. Change the format to scptSetPnts#US.
View full article
Picard Product_Support
‎2018-09-06 01:40 PM

Labels:
  • TAC Vista
1036 Views

How to Move Vista LNS Database with NL220 and L-IP to Site PC?

Issue Use L-IP and NL220 to compose Vista LNS database. How to move the database from the engineering PC to the site PC? Environment Vista 5.X.X LNS Network NL220 Loytec L-IP Cause Due to the complexity of LNS network, it is recommended to follow the steps listed below to move the LNS database and Vista database from an engineering PC to a site PC. Otherwise, it may result controllers offline, Vista database opens extremely slow or freeze. Resolution NL220+L-IP is the most common combination for LNS network. How to move the database completed on the engineering PC to the site PC? The following steps can be followed: The software needed to be installed on site PC: Vista Server, Vista ToolPack, NL220.   A NL220 dongle is needed.  (The dongle does not need to be locked to the site PC for moving database purpose; however, it is recommended to have the dongle locked to the site PC for future maintenance purpose.)   Backup the LNS database on the engineering PC. (Select “Backup Project” in the NL220.)   Make a copy of Vista database.   Copy both backups (LNS and Vista) onto the site PC. NOTE: It is recommended to keep the paths of both databases the same. Otherwise, it may results graphic pages lost.   Specify the folder path of Vista Server on site PC to the backup database.   Add the L-IP interface in the Control Panel.   Plug the NL220 dongle onto the site PC. Open NL220, create a new project and select the interface as L-IP.   Close the project, select “Restore Project” and specify it to the backup database for NL220.   Open the NL220 project again and select the System Plug-in.   Update the LNS database to Vista Server in the System plug-in again.   Select the “Commence Communication” to start the communication.   Open TAC Vista Workstation. Then the LNS interface in the Workstation should be online. NOTE: without a NL220 dongle plugged in the site PC, TAC Vista workstation should operate normally. However, it is impossible to make any change to the LNS database.
View full article
Picard Product_Support
‎2018-09-06 01:40 PM

Labels:
  • TAC Vista
1853 Views

How to download network configuration to Xenta 280/300 (with /N/P) through RS-232 port in Vista 5?

Issue When using RS-232 port to download Menta program, the neuron ID of I/O modules can't be downloaded. When downloading Menta program to Xenta 280/300 (with /N/P) through RS-232 port, the LED besides Service Pin flashes red. When plug OP onto the controller, only “No Answer” shows. Environment Vista 5 Xenta programmable controllers Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B Xenta I/O modules Cause The network configuration can't be downloaded through RS-232 port. Resolution When downloading Menta program to Xenta 280/300 (with /N/P) through RS-232 port in Vista 5, the normal method can't download the network configuration information to the controller, such like the blueprint, the neuron ID of controller and I/O modules. Then the following steps can be followed: Create the Xenta 280/300 controller in the Workstation. The LTA interface can be the Xenta Server, Loytec port or Echelon Port. It does not matter. Assign the Menta file to the Xenta 280/300 controller. Also manually type the neuron IDs of the controller and I/O modules in the Workstation. Right click on the Xenta controller and click “Edit” to open the Menta interface. Press F12 and “Online” button to download the Menta program into Xenta 280/300 controller. The controller or I/O modules should work fine now.
View full article
Picard Product_Support
‎2018-09-06 01:39 PM

Labels:
  • TAC Vista
1994 Views

Vista IV Remote Workstation Licensing Error "The object involved has disconnected from its clients"

Issue Vista IV Remote Workstation pulling the Workstation license from the server PC shows the error "The object involved has disconnected from its clients." If the alarm is acknowledged, Remote Workstation does not work. Restarting the Remote Workstation restores functionality. Environment Vista IV Remote Workstation Aladdin Privilege Administrator 2.01 Remote license hosting Cause The Aladdin Privilege Administrator 2.01 licensing tool that comes with Vista IV did not handle remote licensing of Workstation very well. If trying to read the Workstation license from the server at the remote PC, it occasionally will time out and result in this error. Resolution Install a Workstation license/dongle on the remote PC. This will prevent it from trying to read a license from the server PC and resolve the issue.
View full article
Picard Product_Support
‎2018-09-06 01:39 PM

Labels:
  • TAC Vista
1182 Views
  • « Previous
    • 1
    • …
    • 80
    • 81
    • 82
    • …
    • 102
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore