How to Move Vista LNS Database with NL220 and L-IP to Site PC?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Move Vista LNS Database with NL220 and L-IP to Site PC?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa145087_brid
    sesa145087_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1852 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Move Vista LNS Database with NL220 and L-IP to Site PC?

Picard Product_Support
‎2018-09-06 01:40 PM

Issue

Use L-IP and NL220 to compose Vista LNS database. How to move the database from the engineering PC to the site PC?

Environment

  • Vista 5.X.X
  • LNS Network
  • NL220
  • Loytec L-IP

Cause

Due to the complexity of LNS network, it is recommended to follow the steps listed below to move the LNS database and Vista database from an engineering PC to a site PC. Otherwise, it may result controllers offline, Vista database opens extremely slow or freeze.

Resolution

NL220+L-IP is the most common combination for LNS network. How to move the database completed on the engineering PC to the site PC? The following steps can be followed:

  1. The software needed to be installed on site PC: Vista Server, Vista ToolPack, NL220.
     
  2. A NL220 dongle is needed.  (The dongle does not need to be locked to the site PC for moving database purpose; however, it is recommended to have the dongle locked to the site PC for future maintenance purpose.)
     
  3. Backup the LNS database on the engineering PC. (Select “Backup Project” in the NL220.)
     
  4. Make a copy of Vista database.
     
  5. Copy both backups (LNS and Vista) onto the site PC.
    NOTE: It is recommended to keep the paths of both databases the same. Otherwise, it may results graphic pages lost.
     
  6. Specify the folder path of Vista Server on site PC to the backup database.
     
  7. Add the L-IP interface in the Control Panel.
     
  8. Plug the NL220 dongle onto the site PC. Open NL220, create a new project and select the interface as L-IP.
     
  9. Close the project, select “Restore Project” and specify it to the backup database for NL220.
     
  10. Open the NL220 project again and select the System Plug-in.
     
  11. Update the LNS database to Vista Server in the System plug-in again.
     
  12. Select the “Commence Communication” to start the communication.
     
  13. Open TAC Vista Workstation. Then the LNS interface in the Workstation should be online.
    NOTE: without a NL220 dongle plugged in the site PC, TAC Vista workstation should operate normally. However, it is impossible to make any change to the LNS database.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5467
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore