Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2029 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 100
    • 101
    • 102
  • Next »
Label: "TAC Vista" Show all articles

TAC Menta, mainloop overrun then having many Alarm blocks and more than one ERR block.

Issue TAC Menta could give mainloop overrun then having an application with many Alarm blocks and more than one ERR block. Environment TAC Xenta 280/300/401 TAC Menta Cause When the ERR block is executed, it goes through all Alarm blocks to check status, having more than one ERR block makes this loop to be run more than once. Resolution There sould be a maximum of one ERR block per application.
View full article
Picard Product_Support
‎2018-09-06 09:03 AM

Labels:
  • TAC Vista
1405 Views

Is it possible to have a binding to, and transfer a value to a variable that have the backup flag set?

Issue The customer wants to have a binding and transfer a value, but also wants to have backup set on the receiving variable in the TAC Xenta device. Environment TAC Vista TAC Xenta 280/300/401 Cause Setting the Backup flag will make the variable be written into the flash memory every time the value is written. Doing this on a value that is regularly transferred will damage the flash memory, as it has to write all the time. Resolution The Backup flag should not be set on variables that are written to on a regular basis.
View full article
Picard Product_Support
‎2018-09-06 09:03 AM

Labels:
  • TAC Vista
1616 Views

No license on Windows 2003 Server (-15, 10 System Error: 10061 Winsock Connection Refused)

Issue On a Windows 2003 Server or Windows XP, TAC Vista is not able to locate the license server, even though everything seems to be set up correctly. You get the message "-15, 10 System Error: 10061 Winsock Connection Refused" when you try to open any TAC Vista software. Environment TAC Vista Flexnet license Windows 2003 Windows XP Cause The TAC Vista software is looking for the license server on the PC defined, but the license server is running using the TCP/IP v6 address and the software doesn't support that on this operating system. Resolution Uninstall TCP/IP version 6 and reboot the PC. Below is a description on how to do it.   For the IPv6 protocol for Windows XP with SP1 or later or Windows Server 2003, do the following: Log on to the computer with a user account that has privileges to change network configuration. Click Start, click Control Panel, and then double-click Network Connections. Right-click any local area connection, and then click Properties. Click Microsoft TCP/IP version 6 (for Windows XP with SP2 or later or Windows Server 2003) or Microsoft IPv6 Developer Edition (for Windows XP with SP1), and then click Uninstall. When prompted to confirm the removal of the Microsoft IPv6 Developer Edition or Microsoft TCP/IP version 6 protocol, click OK. Alternately, from the Windows XP or Windows Server 2003 desktop, click Start, point to Programs, point to Accessories, and then click Command Prompt. At the command prompt, type netsh interface ipv6 uninstall. To remove the IPv6 protocol for Windows XP with no service packs installed, do the following: Log on to the computer with a user account that has local administrator privileges. From the Windows XP desktop, click Start, point to Programs, point to Accessories, and then click Command Prompt. At the command prompt, type ipv6 uninstall.
View full article
Picard Product_Support
‎2018-09-06 09:02 AM

Labels:
  • TAC Vista
1703 Views

A generic error occurred in GDI+

Issue When editing a TGML error A generic error occurred in GDI+ appears Product Line EcoStruxure Building Operation, TAC Vista Environment TAC Vista StruxureWare Building Operation TGML Graphic editor Cause This issue occurs after you install security update 3045171. You experience a crash when you use Windows GDI+ to create text outline-based path objects on a computer that is running Windows 7 Service Pack 1 (SP1) or an earlier version of Windows. Resolution Download the patch below from Microsoft https://support.microsoft.com/en-us/kb/3065979 It has been noted that this patch do not solves all the issues, if you still have issues with other applications uninstall the security update KB3045171.
View full article
Picard Product_Support
‎2018-09-11 12:49 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
2390 Views

Schneider Electric Heat Meter Multical 602 - Pulse output card

Issue Selection and installation of a pulsed output module. Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell Sigma, TAC Vista Environment Heat Meter Multical 602 Pulsed output module No pulses Cause Installed card does not give output pulses. Resolution Selection of the output card. The Schneider Electric part number is MAPULSETOPC and this is the equivalent to Kamstrup part number 602-0C This card will provide 2 pulse outputs for energy and volume, CE and CV respectively. Normally, energy (CE) is connected to 16-17 and volume (CV) to 18-19, but other combinations can be selected via the PC program METERTOOL, also used to select pulse duration 32 or 100 ms. The MAPULSETOPC is actually a top module, which means that it is fitted into the top piece of the MC602 calculator, basically the inside LCD cover. This is released by pressing downwards in the middle of the plastic piece on the left, and at the same time pushing the top module towards the left.
View full article
Picard Product_Support
‎2018-09-06 08:41 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • TAC Vista
2037 Views

How to understand the SNVT nvoAlarmStatus in TAC Xenta 151-D

Issue In the TAC Xenta 151-D, the nvoAlarmStatus handles the test of the dampers, but the translation of the status is not documented Environment TAC Xenta 151-D Cause nvoAlarmStatusis used to report the actual status of the fire damper tests. Resolution nvoAlarmStatus is a SNVT_state with the use of the following bits: nvoAlarmStatus.bit0 = 1   OBJECT1_CLOSE_TIME_TOO_LONG    nvoAlarmStatus.bit1 = 1   OBJECT1_CLOSE_TIME_TOO_SHORT   nvoAlarmStatus.bit2 = 1   OBJECT1_OPEN_TIME_TOO_LONG     nvoAlarmStatus.bit3 = 1   OBJECT1_OPEN_TIME_TOO_SHORT    nvoAlarmStatus.bit4 = 1   OBJECT2_CLOSE_TIME_TOO_LONG    nvoAlarmStatus.bit5 = 1   OBJECT2_CLOSE_TIME_TOO_SHORT   nvoAlarmStatus.bit6 = 1   OBJECT2_OPEN_TIME_TOO_LONG     nvoAlarmStatus.bit7 = 1   OBJECT2_OPEN_TIME_TOO_SHORT    nvoAlarmStatus.bit8 = 1   OBJECT1_SET_CLOSE_TIME_FAILED nvoAlarmStatus.bit9 = 1   OBJECT1_SET_SELFTEST_OK        nvoAlarmStatus.bit10 = 1  OBJECT1_SET_SELFTEST_FAILED    nvoAlarmStatus.bit11 = 1  OBJECT2_SET_CLOSE_TIME_FAILED nvoAlarmStatus.bit12 = 1  OBJECT2_SET_SELFTEST_OK        nvoAlarmStatus.bit13 = 1  OBJECT2_SET_SELFTEST_FAILED     
View full article
Picard Product_Support
‎2018-09-06 08:38 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1064 Views

Configuring a minimum off time for a TAC Xenta 121-HP

Issue It is desired to configure a minimum off time, so when the compressor stops in e.g. heating mode, it will not start again before a minimum time has elapsed in the same mode. This setting is not available in the device. Environment TAC Xenta 121-HP Cause There is no setting for minimum stop time when in the same mode, there is only a minimum stop time between modes. Resolution As a workaround, set the "Activate at" value to something other than zero (say 10%), so that you can use the "Hysteresis" at 10%, and this way get a delay. This way you will get a delay in the most cases, a little time before the controller reacts.
View full article
Picard Product_Support
‎2018-09-06 08:38 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1101 Views

Renewing OpenLNS CT Annual Maintenance

Issue Why isn't the OpenLNS a full, un-limited license? Environment OpenLNS OpenLNS CT Cause Renewing OpenLNS CT Annual Maintenance You can renew your annual maintenance for OpenLNS Server and OpenLNS CT before they expire. Renewing your OpenLNS and OpenLNS CT annual maintenance enables you to continue installing software updates and upgrades. If you do not renew the products’ maintenance, you can still use the products; however, you will not be able to upgrade it with updates or upgrades released after your annual maintenance expired. You cannot renew your annual maintenance after it has expired. Once it has expired, you must purchase a new activation key to be able to install any updates or upgrades released after your maintenance expired. To renew your annual maintenance, purchase an OpenLNS Commissioning Tool Professional One-Year Maintenance Renewal (Echelon model number 93800) or an OpenLNS Commissioning Tool Standard One-Year Maintenance Renewal (Echelon model number 93810). Echelon will process your order, and your maintenance coverage will be extended so that you can continue updating and upgrading OpenLNS and OpenLNS CT for an additional year. Resolution If paying the annual maintenance fee, you have access to updates and upgrades. Not paying still means that the program could be used, however it could not be updated with the latest patches.
View full article
Picard Product_Support
‎2018-09-06 07:39 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1570 Views

TAC Vista Conversion Tool converts TAC Xenta I/O modules from LonWorks units to SlaveSpeak devices

Issue TAC Xenta I/O modules that are added as LonWorks units in TAC Vista, are converted to Xenta I/O modules belonging to a Xenta Base unit (SlaveSpeak devices) in EcoStruxure Building Operation, after conversion using TAC Vista Conversion Tool. Product Line EcoStruxure Building Operation, TAC Vista Environment Vista Server TAC Vista Conversion tool Xenta Xenta I/O-modules Cause In TAC Vista, the Xenta I/O modules are normally located on the same subnet as the Xenta Base unit, and belong to the Xenta Base unit, communicating as SlaveSpeak devices. If a Xenta I/O module is located on another subnet than the Xenta base unit, it could instead be added as a LonWorks Unit in Vista, and therefore communicating via LonWorks bindings to the Xenta base unit using SNVTs. Vista Conversion Tool does not handle this configuration. In the conversion tool, all Xenta I/O modules are expected to be connected directly to a Xenta base unit, located on the same Subnet, and are therefore always treated as SlaveSpeak devices. Resolution After running the Vista Conversion tool, you have to re-build the LonWorks Bindings between the Xenta I/O module and the Xenta Base unit manually in EBO, as the Conversion Tool does not handle the actual configuration setup.
View full article
Guinan MikaelKrantz Guinan
‎2019-03-22 06:21 AM

on ‎2019-03-22 06:21 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
2093 Views
  • « Previous
    • 1
    • …
    • 100
    • 101
    • 102
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore