Is it possible to have a binding to, and transfer a value to a variable that have the backup flag set?
  • Is it possible to have a binding to, and transfer a value to a variable that have the backup flag set?
  • RobertAndriolo
    RobertAndriolo
  • MikaelKrantz
    MikaelKrantz
‎2018-09-06 09:03 AM
The customer wants to have a binding and transfer a value, but also wants to have backup set on the receiving variable in the TAC Xenta device.
TAC Vista
TAC Xenta 280/300/401
Setting the Backup flag will make the variable be written into the flash memory every time the value is written.
Doing this on a value that is regularly transferred will damage the flash memory, as it has to write all the time.
The Backup flag should not be set on variables that are written to on a regular basis.
Tags (2)
  • 17829
  • object