How to understand the SNVT nvoAlarmStatus in TAC Xenta 151-D
  • How to understand the SNVT nvoAlarmStatus in TAC Xenta 151-D
  • Benji
    Benji
  • MikaelKrantz
    MikaelKrantz
‎2018-09-06 08:38 AM
In the TAC Xenta 151-D, the nvoAlarmStatus handles the test of the dampers, but the translation of the status is not documented
TAC Xenta 151-D
nvoAlarmStatusis used to report the actual status of the fire damper tests.
nvoAlarmStatus is a SNVT_state with the use of the following bits:
nvoAlarmStatus.bit0 = 1   OBJECT1_CLOSE_TIME_TOO_LONG
nvoAlarmStatus.bit1 = 1   OBJECT1_CLOSE_TIME_TOO_SHORT
nvoAlarmStatus.bit2 = 1   OBJECT1_OPEN_TIME_TOO_LONG
nvoAlarmStatus.bit3 = 1   OBJECT1_OPEN_TIME_TOO_SHORT
nvoAlarmStatus.bit4 = 1   OBJECT2_CLOSE_TIME_TOO_LONG
nvoAlarmStatus.bit5 = 1   OBJECT2_CLOSE_TIME_TOO_SHORT
nvoAlarmStatus.bit6 = 1   OBJECT2_OPEN_TIME_TOO_LONG
nvoAlarmStatus.bit7 = 1   OBJECT2_OPEN_TIME_TOO_SHORT
nvoAlarmStatus.bit8 = 1   OBJECT1_SET_CLOSE_TIME_FAILED
nvoAlarmStatus.bit9 = 1   OBJECT1_SET_SELFTEST_OK
nvoAlarmStatus.bit10 = 1  OBJECT1_SET_SELFTEST_FAILED
nvoAlarmStatus.bit11 = 1  OBJECT2_SET_CLOSE_TIME_FAILED
nvoAlarmStatus.bit12 = 1  OBJECT2_SET_SELFTEST_OK
nvoAlarmStatus.bit13 = 1  OBJECT2_SET_SELFTEST_FAILED
Labels (2)
  • 18648