Configuring a minimum off time for a TAC Xenta 121-HP
  • Configuring a minimum off time for a TAC Xenta 121-HP
  • Benji
    Benji
  • MikaelKrantz
    MikaelKrantz
‎2018-09-06 08:38 AM
It is desired to configure a minimum off time, so when the compressor stops in e.g. heating mode, it will not start again before a minimum time has elapsed in the same mode.
This setting is not available in the device.
TAC Xenta 121-HP
There is no setting for minimum stop time when in the same mode, there is only a minimum stop time between modes.
As a workaround, set the "Activate at" value to something other than zero (say 10%), so that you can use the "Hysteresis" at 10%, and this way get a delay.
This way you will get a delay in the most cases, a little time before the controller reacts.
Labels (2)
  • 18671