No license on Windows 2003 Server (-15, 10 System Error: 10061 Winsock Connection Refused)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • No license on Windows 2003 Server (-15, 10 System Error: 10061 Winsock Connection Refused)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1703 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

No license on Windows 2003 Server (-15, 10 System Error: 10061 Winsock Connection Refused)

Picard Product_Support
‎2018-09-06 09:02 AM

Issue

On a Windows 2003 Server or Windows XP, TAC Vista is not able to locate the license server, even though everything seems to be set up correctly. You get the message "-15, 10 System Error: 10061 Winsock Connection Refused" when you try to open any TAC Vista software.

Environment

TAC Vista

Flexnet license

Windows 2003

Windows XP

Cause

The TAC Vista software is looking for the license server on the PC defined, but the license server is running using the TCP/IP v6 address and the software doesn't support that on this operating system.

Resolution

Uninstall TCP/IP version 6 and reboot the PC. Below is a description on how to do it.

 

For the IPv6 protocol for Windows XP with SP1 or later or Windows Server 2003, do the following:

  • Log on to the computer with a user account that has privileges to change network configuration.
  • Click Start, click Control Panel, and then double-click Network Connections.
  • Right-click any local area connection, and then click Properties.
  • Click Microsoft TCP/IP version 6 (for Windows XP with SP2 or later or Windows Server 2003) or Microsoft IPv6 Developer Edition (for Windows XP with SP1), and then click Uninstall.
  • When prompted to confirm the removal of the Microsoft IPv6 Developer Edition or Microsoft TCP/IP version 6 protocol, click OK.


Alternately, from the Windows XP or Windows Server 2003 desktop, click Start, point to Programs, point to Accessories, and then click Command Prompt. At the command prompt, type netsh interface ipv6 uninstall.


To remove the IPv6 protocol for Windows XP with no service packs installed, do the following:

  1. Log on to the computer with a user account that has local administrator privileges.
  2. From the Windows XP desktop, click Start, point to Programs, point to Accessories, and then click Command Prompt.
  3. At the command prompt, type ipv6 uninstall.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 17894
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore