Cannot view SCPTs, UCPTs, or UNVTs in XBuilder
  • Cannot view SCPTs, UCPTs, or UNVTs in XBuilder
‎2018-09-06 01:43 PM
Cannot view SCPTs, UCPTs, or UNVTs in XBuilder.
Warning in XBuilder: "2147483647    Warning -1     ____ will be skipped. Unrecognized SNVT type from Vista Database:0"
  • XBuilder
  • LON Devices
  • Xenta 102-AX
  • Xenta 121-HP, 121-FC
  • STR-350
XBuilder can only view, read, and write to SNVTs in a LON device.
There is no way to view SCPTs in XBuilder.
If XBuilder is required for transferring data, a work around will have to be found. Instead of writing to SCPTsetPoints, use nviSetpoint, for example.
The resulting warning in XBuilder is alerting that it cannot process the information contained in a SCPT, UCPT or UNVT, only SNVT. Therefore the "SNVT type" is unrecognized.
Tags (2)
  • 5360
  • thermostat