Not possible to have a zero in the beginning of an address to a M-bus device in XBuilder
  • Not possible to have a zero in the beginning of an address to a M-bus device in XBuilder
  • Jonas_Brissman
    Jonas_Brissman
‎2018-09-06 01:44 PM
Not possible to have a zero in the beginning of an address to a M-bus device in XBuilder.
For example, add an M-bus device in XBuilder. Write a secondary address (used default) with a zero in the beginning. Click OK and the zero in the beginning disappears.
  • Vista 5.1.5
  • XBuilder
This is just a display attribute in XBuilder to trim leading zeros in the address field.
Even if the zero in the beginning disappears in the address box, it will still be used when the Xenta server communicates with the M-bus device.
Write the address with a zero as it should be and that address will be used.
  • 5352