Active X: could not create object. Error when launching Plug-ins in NL220 or LonMaker installed on Windows 7.
  • Active X: could not create object. Error when launching Plug-ins in NL220 or LonMaker installed on Windows 7.
  • Sacco
    Sacco
‎2018-09-06 01:43 PM
Plug-in will not launch. Results in error "Active X: could not create object"
  • Windows 7 32 bit
  • Windows Vista
  • NL220
  • LonMaker
  • Vista Plug-ins
Needs to be run as an administrator.
  1. Verify Administrator account is logged in.
  2. Install Toolpack (or hotfix) as administrator
  3. Take note of the installation location, and go to this folder after the installation of the hotfix.
    The default location for these plug-in application files is:
    C:\LonWorks\apps\TAC
  4. Run file: TACXenta102AXPlugIn.exe, as administrator and click Deregister Plug-in, then Register Plug-in.
  5. Open NL220 or LonMaker and register the Xenta 102-AX plug-in.
  • 5380