Opening Vista Server hangs on "initializing server functions field bus initializations..."
  • Opening Vista Server hangs on "initializing server functions field bus initializations..."
  • Sacco
    Sacco
‎2018-09-11 08:43 AM
  • After launching the Vista Server program, it seems to cycle through its startup process, but stops on: "initializing server functions field bus initializations..."  Vista Server will never finish opening regardless of how long it is left to run and must be forced closed with the Task Manager.
  • When attempting to open a LonMaker drawing, the last process displayed before hang up is: "Opening network connections".
  • LonMaker
  • Vista
Corrupted LonMaker database.
Possibly due to unexpected termination of the LonMaker program such as a loss of power or Ending the process from Task Manager.
  1. Attempt to open the associated LNS database through LonMaker. It will most likely fail to open.
  2. Restore last known good backup.
  3. Optionally,  send the damaged database to Echelon Support for further investigation at lonsupport@echelon.com.
Field bus is referred to as LNS Server Ports in the Vista world.  If the LNS database will not open, then the Vista server cannot access it.
  • 5337