Issue
When Zbuilder is opened from LonMaker the setpoints revert to default values:
- US - 50°F
- SI - 10°C
Environment
LonMaker 3.x
Zbuilder 5.1.4 - 5.1.5
Cause
If the Region format is English (United States) but the Measurement system is Metric then the value provided to Zbuilder from LNS server is handled improperly.
Resolution
Change the Region Settings
Open the Windows Control Panel and access the Region and Language settings. Click the Additional Settings button to change the Measurement System to U.S.
Change the format of the Setpoints
Open the LNS browser for any Xenta 121 controller in this database. Find the scptSetPnts and right click and select Change Format. Change the format to scptSetPnts#US.