Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1895 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 69
    • 70
    • 71
    • …
    • 95
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Creating Folder Structure to Organize Reports

Issue Creating Folder Structure to Organize Reports Environment SmartStruxure StruxureWare for Building Operation Report Server Cause A large number of reports may result in difficulty navigating the report tree.  The following processes allow you to sort the various created reports. Resolution Creating folders to store the saved reports.  Log into the SQL Report manager from the reports Server using the URL http://localhost/Reports   or  http://localhost/Reports_SQLEXPRESS     Open the folder you wish to add new folders to.  For this example I will use the Production reports folder.   Click "New Folder" Name the Folder and click OK NOTE: In order for the Folder to show up in the reports Server, it will have to have at least one object inside of it. You can move any report to the new folder by clicking on the drop down beside it and selecting "Move". Updating the StruxureWare reports Server to display the new folders  Connect to the StruxureWare Web Reports interface, using an account that is part of the Reports Administrators group. Click on Report Packs. At the bottom of the Screen click "Synchronize" This must be done to apply any changes made in the SQL Report Server Web interface to the StruxureWare Reports Server Saving a Reports parameters for quicker access.  You may wish to save a report to quickly run last months Trend Data. This type of saved report is referred to as a "Dashboard Report" Run the report you wish to save, using the desired parameters Above the report, click Save As In the Report name Field, type the Folder name and report name that you wish to use. NOTE you are limited to 30 characters for the report name. Be sure to check the "Dashboard report" option. Without this option checked you will be making a duplicate of the original report. The Dashboard Report option saves the parameters you have selected. Click "Save as"
View full article
Picard Product_Support
‎2018-09-10 11:49 PM

Labels:
  • EcoStruxure Building Operation
2465 Views

Energy Reports not working in 1.3 and earlier

Issue Energy Reports not working in 1.3 and earlier Product Line EcoStruxure Building Operation Environment StruxureWare Web Reports StruxureWare Reports Server Cause For 1.3 and earlier, in order for a log to be tracked as an energy report it must have a units type that indicates it is a metered signal. Resolution For any logs that do not have Units set.  Add one of the possible Unit types shown below. You should not change units on a log that is already running.  If you have entered the wrong type of units you will need to delete and re-create the logs. If this is not possible.  Use the following directions: In the System tree pane, browse to System>Report manager View the metering log filter property to see all unit types that will be interpreted as Energy logs.  The energy objects must all reside within a single Energy folder. In the event that you have already set unit on a log, you should be able to add the unit to the list in this field.  Note:  It is not necessary to include the prefix / suffix of the same unit.  That is if you are using MWh or kWh then this is covered by the unit Wh in the Meter log filter.  You must make sure that the units are defined in the monitor point (object), trend log and associated extended trend log for the values to be shown in the Energy Reports.
View full article
Picard Product_Support
‎2018-09-10 11:13 PM

Labels:
  • EcoStruxure Building Operation
1277 Views

Software Administrator shows red outline (box) on the Communication Ports (HTTP / HTTPS)

Issue Software Administrator shows red outline (box) on the Communication Ports (HTTP / HTTPS) Enterprise Server service is not starting - log displays ..The server has made to many unsuccessful attempts to start... Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Cause The Enterprise Server service will not start if the ports assigned during installation are already in use by another software package. Resolution To rectify this the port numbers in the Software Administrator need to be changed from their current value. Open the Building Operation Software Administrator Under the Communication Ports change any port that is highlighted or surrounded by a red box After making these changes select the Apply button Attempt to start the service.
View full article
Picard Product_Support
‎2018-09-10 11:08 PM

Labels:
  • EcoStruxure Building Operation
1830 Views

Minimum display is 1024x768 which is too small for proper screen size

Issue Minimum display is 1024x768 which is too small for proper screen size Environment SmartStruxure up to release 1.3 Cause Release notes for 1.3 in 9.2.1 state the Minimum display is 1024x768 which is too small for proper screen size. In the screen capture below, a simple schedule is created, and then a New Schedule Event is selected which opens the window. the window is larger than the screen size, missing the top and bottom. Resolution Adjust the screen resolution to a larger size which is suitable. Size is dependent on hardware specifications.
View full article
Picard Product_Support
‎2018-09-10 11:08 PM

Labels:
  • EcoStruxure Building Operation
1514 Views

I/NET Controller in StruxureWare Building Operation has a blue circle with a white down arrow on top of it.

Issue I/NET Controller in StruxureWare Building Operation has a blue circle with a white down arrow on top of it. Environment I/NET Integration StruxureWare Building Operation Cause Any change to the I/NET controller will result in this indication requesting an upload. Changing a configuration in a time schedule or updating a calc extension on a point are two examples of what might cause this. Please note that the Upload DOES NOT complete the same action as a Station Save in I/NET. Upload will sync the StruxureWare Database with the I/NET database. To perform a station save from StruxureWare, right click on the Controller and select "backup". Resolution Expand the I/NET Interface network object Right click on the offending controller Select Upload Wait a few seconds. A refresh of the System Tree may be required.
View full article
Picard Product_Support
‎2018-09-10 11:09 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1500 Views

BASEDON keyword and PE Programming

Issue BASEDON keyword and Plain English Programming BASEDON key word fail Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation site with up to release 1.3 Cause Below is a sample program which uses the BASEDON keyword. Also, here are the steps to use that program: Create script program using keyword BASEDON (Below) Create an input and output for the program (below program that is EntreeBase and SortieBase) Set the input Entreebase to 1,2,3,4,5 and program errors out. Set input to 6 and program runs   Numeric Input EntreeBase Numeric Output SortieBase Line Debut basedon Entreebase goto 1,2,3,4,5 goto 6 Line 1 SortieBase=1 goto Suite Line 2 SortieBase=2 goto Suite Line 3 SortieBase=3 goto Suite Line 4 SortieBase=4 goto Suite Line 5 SortieBase=5 goto Suite Line 6 Sortiebase=6 goto suite Line suite if sortiebase<1 then Sortiebase=20 if ts<5 then goto suite else goto Debut Line E Sortiebase=10 goto Suite  Resolution BASEDON keyword has been submitted as an issue and expected to be corrected in a future release.
View full article
Picard Product_Support
‎2018-09-10 11:09 PM

Labels:
  • EcoStruxure Building Operation
1958 Views

KYZ Pulse Output on a Power Meter

Issue A specification for a power meter states that it provides KYZ pulse outputs. What is a KYZ pulse output? Product Line All Product Lines Environment Utility Meter with KYZ pulse outputs Cause Some meter specification sheets may state that the device outputs KYZ pulses. Resolution KYZ is a designation given to a relay used to create pulses for electrical metering applications. It is commonly a Form C relay (SPDT). The term KYZ refers to the contact designations: K for common, Y for Normally Open, and Z for Normally Closed.
View full article
Picard Product_Support
‎2018-09-10 10:54 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
6854 Views

WorkStation crashes on a Parameter name: d error

Issue StruxureWare Building Operation WorkStation crashes randomly while working in it. The following error message is displayed. Environment Building Operation WorkStation Cause The "Value cannot be null. Parameter name: d" crash is caused by a Windows Presentation Foundation (WPF) application defect. Resolution To resolve the issue: Go to the following link http://support.microsoft.com/kb/2461678. This link will provide additional information on the defect and how to fix the problem.   Apply the hotfix that is provided underneath the section titled "Resolution".
View full article
Picard Product_Support
‎2018-09-10 10:54 PM

Labels:
  • EcoStruxure Building Operation
1606 Views

Displaying Correct Regional Units in Webstation

Issue Metric vs. Imperial Units as displayed Using Webstation Regional Settings Any device, will by default, show configured units. Regional settings must be applied to normalize all devices. Product Line EcoStruxure Building Operation Environment Webstation TGML Graphics SNVT values Cause Incorrect Units will appear in webstation if webstation regional settings are not configured correctly. Resolution Log into Webstation Select Settings > Change Regional Settings   Select the desired Language Select the desired Measurement system Click Ok NOTE: Settings are preserved via a cookie stored on the local PC. Any time cookies are deleted this will return to its default setting.
View full article
Picard Product_Support
‎2018-09-06 02:53 PM

Labels:
  • EcoStruxure Building Operation
2652 Views

Print function puts column on next page

Issue When selecting a list view, last column is always on next page Environment Release 1.2 and 1.3 Beta 3 Cause When Printing a list view, last column is always on next page.  Resolution At the moment only workaround: to add 4th "dummy" column. Then the 3 necessary columns are on the first page and the dummy is on the second.
View full article
Picard Product_Support
‎2018-09-06 02:59 PM

Labels:
  • EcoStruxure Building Operation
1472 Views

Function Block program using WDAY with day = Sunday

Issue When creating a FB program and use WDAY, change the date on the AS or ES to Sunday, the WDAY changes the day to 0 (zero). Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation and all compatible operating systems including Windows XP, Windows 7, Windows Server 2008, and virtual machine environments. Cause Create a FB program and use WDAY, then change the date on the AS or ES to Sunday, the WDAY changes the day to 0 zero. Steps to reproduce problem: Create FB Program in AS or ES Use the WDAY While using the Graphics Viewer in the AS or ES, WDAY shows correct weekday (today is 2) Change the date on the AS or ES to a Sunday i.e. 12-09-16 which is Sunday,September 16, 2012 View FB program in Graphics Viewer, which now shows 0 as if today were now 0  The WDAY FB program should show 7 which is Sunday. Monday=1 Tuesday=2 Wednesday=3 Thursday=4 Friday=5 Saturday=6 Sunday=7 Resolution This will be resolved in a future release. Currently, there is a alternative: with an XPI block, make WDAY 0 = 7.A second alternative would be to add an if-statement: if(output = 0){output = 7}  
View full article
Picard Product_Support
‎2018-09-10 10:34 PM

Labels:
  • EcoStruxure Building Operation
2243 Views

DELR / DELI block does not function as expected when connected to a PVR / PVI block in Function Block Program

Issue When a DELR or DELI block is used with a comparison operator to detect a change of value in the output of a function block, the output of the comparison operator should go ON for one scan when the source output value changes. If the source function block is a PVR or PVI this does not occur. For example: This code does not work This code works Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation version 1.3.0 or earlier Function Block Editor Cause There is a defect in StruxureWare Building Operation version 1.3.0 or earlier that causes this behaviour when writing to a public PVR or PVI block in a Function Block Program in the ES or AS directly from the Workstation. Resolution This defect has been logged with Quality Center and will be fixed in SmartStruxure version 1.4.0 Meanwhile, the workaround is to insert any compatible block immediately after the PVR or PVI.  For example: The inserted block could be an operator, an expression block or even another DELR. Although the workaround works, the preferred practice for new applications would be to replace the PVR with a RI and bind the RI to an Analog Value in the ES or AS. This defect does not occur in Menta programs in Xenta controllers, including those written in the SmartStruxure Menta Editor.
View full article
Picard Product_Support
‎2018-09-06 11:55 AM

Labels:
  • EcoStruxure Building Operation
2734 Views

How does the Execution Precedence affect the program operation?

Issue Can the Execution Precedence determine the priority of a program binding to a value? Environment SBO Function Block and Script programs Cause Clarification on the function of Execution Precedence is required. Resolution In both Function Block and Script programs there is an attribute called Execution Precedence, this can be set in the program "Properties", Basic tab. For a Function Block program:    For a Script Program: Execution Precedence determines the order that the programs will be run, the lowest numbers will be run first. In the 2 screenshots above the Function block program (Value 1) will be run before the Script program (Value 20). This can be used for applications where a calculation is done to generate a value, that is then used in a second program e.g. Calculation of a compensated setpoint, that is then used in a PID control program as the reference value. The PID program must have a higher Execution Precedence than the setpoint calculation. Execution Precedence does not affect priority. If the outputs of 2 programs are bound to a single value, both programs will be trying to control the value and give an indeterminate result.   To combine the outputs of 2 programs the programmer must use the appropriate logic to determine how the 2 signals should be combined for the application. So for Binary values use one of the logical operators: AND, OR, XOR etc, For Analog values combine the 2 results with Max, Min, Average etc as required.
View full article
Picard Product_Support
‎2018-09-06 11:59 AM

Labels:
  • EcoStruxure Building Operation
2054 Views

StruxureWare Building Operation Enterprise Server Application Error occurs at computer start up

Issue The ES crashes during startup   SE.EnterpriseServer.exe - Application Error occurs, and the Building Operation Enterprise Server service cannot be started.  Error contains "The memory could not "written"".   The port fields in software administrator shows a red indication on one or more of the ports Environment Enterprise Server Software Administrator IP ports Cause A program is already using the ports defined for the Enterprise Server     In general   You can check which program it is, by entering the following command in a command prompt, replacing ":port number" with the number you want to check, e.g. "0.0.0.0:80" for port 80: netstat -aonb | find "0.0.0.0:port number"     Now in the task manager, enable the coloumn "PID (Process Identifier)", and look for the process ID you get to the far right when running the command above. That will show what program is taking the port.       Skype   If you are running Skype on the Enterprise Server PC there could be a conflict between the default IP port settings and the IP port settings in Software Administrator. The default ports for SmartStruxure Enterprise Server are 80 and 443. By default, Skype will "use port 80 and 443 as alternatives for incoming connections" if the configured port is unavailable. When Skype is launched it appears to search for an open IP port. If it cannot find an open port within a period of time it may default to ports 80 and 443 as a backup. This behaviour appears to be intermittent.    TeamViewer In newer versions of TeamViewer this is no longer an issue, but it's good practice to select "Use UDP" in the advanced settings of TeamViewer Resolution In general, you can change the ports used by the Enterprise Server in the Building Operation Software Administrator.   If the issue is Skype do the following: In the Skype tools menu go to “Options…” Expand the “Advanced” settings on the left hand side. Click “Connection” in the Advanced section. Uncheck the setting that says "Use port 80 and 443 as alternatives for incoming connections"
View full article
Picard Product_Support
‎2018-09-06 11:55 AM

Labels:
  • EcoStruxure Building Operation
1950 Views

Setting up Java Debug Tools

Issue Various webstation or TGML issues Environment StruxureWare Web Station Vista Web Station Cause Java script may be causing problems with Webstation.  Resolution   How to turn on Java Debugging: Open Control Panel Select Java Chose the advanced tab Expand Debugging and check all boxes Expand Java console and select Show console When future errors occur you can capture the errors from the java console If you do not wish to have the console pop up, you can change the Java console back to Hide console and access the logs at this location:  C:\Users\CURRENTUSER\AppData\LocalLow\Sun\Java\Deployment\log
View full article
Picard Product_Support
‎2018-09-06 11:40 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1247 Views

binding using template does not show count

Issue When binding using templates at Release 1.1 the user is presented with the number of objects that were found, this count was missing in Release 1.2 and 1.3 Environment Site with official release 1.2 and 1.3 versions Cause When binding using templates at Release 1.1 the user is presented with the number of objects that were found:      this count was missing in Release 1.2: Resolution The Count feature will be available in upcoming release.   
View full article
Picard Product_Support
‎2018-09-06 11:16 AM

Labels:
  • EcoStruxure Building Operation
1615 Views

Values from Script programming not showing up in correct format or Units

Issue The values from a script program are not showing up in Workstation in the correct format. For example, the values are Integers instead of a floating format that provides numbers down to the decimal. A second issue is that the data type icons are incorrect. The values used by the script program are not functioning because they are being calculated using the wrong units. The screen shot below shows a section of a binding page where the "Blr 1Failed" icon shows the correct data type (digital), but "Blr 2Failed and Blr 3Failed" do not. Environment Workstation Script Editor Cause The type of point and the units can be set inside the script program. This may cause a different format to be displayed in Workstation other than what is expected. When comparing values in a script program it may be required to set units to ensure that proper comparison is done. Resolution Check the settings of the points within the Script program.   Open up the Script program by right clicking on it in Workstation and going to Edit. With the script program open, look at the point and unit types in the Variables window at the bottom. Make sure that these are the desired settings and save the program.
View full article
Picard Product_Support
‎2018-09-06 11:15 AM

Labels:
  • EcoStruxure Building Operation
1805 Views

Alarm delivery in StruxureWare: Sending Alarms to a Gmail recipient using the ES Email Notification.

Issue An Enterprise Server or Automation Server is unsuccessful at sending email notifications to a Gmail recipient.  Email messages from ES are marked as spam by Gmail SMTP service. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server (AS-P, AS-B or AS) Building Operation Workstation Gmail Cause Unable to successfully configure the ES to send an Alarm Notification to a Gmail recipient. Resolution The following describes how the ES can be set up to use Gmail for Email delivery. 1. Log into the ES; designate the Sender E-mail address and E-mail Host properties. 2. Create a notification on the ES; set the destination E-mail address and type of alarms to be included. 3. Log into destination E-mail account; notice there don’t appear to be any E-mails received. Select the “More” dropdown. 4. Select the “SPAM” folder. 5. Navigate to the E-mail Selection Tab and choose all E-mails from the correct sender. 6. Select the “Not Spam” button and from now on all email notifications will be sent to your inbox! 1. Log into the ES; designate the Sender E-mail address and E-mail Host properties. 2. Create a notification on the ES; set the destination E-mail address and type of alarms to be included. 3. Log into destination E-mail account; notice there don’t appear to be any E-mails received. Select the “More” dropdown. 4. Select the “SPAM” folder. 5. Navigate to the E-mail Selection Tab and choose all E-mails from the correct sender (SxW). 6. Select the “Not Spam” button and from now on all email notifications will be sent to your inbox!
View full article
Picard Product_Support
‎2018-09-10 10:29 PM

Labels:
  • EcoStruxure Building Operation
5847 Views

Danish &Oslash; alphabet character with upgrade from 1.3 Beta 1 to Beta 2

Issue Danish Ø alphabet character in I/NET 2.42 build 2316 while upgrade from StruxureWare Building Operation 1.3.0.724 Beta 1 to 1.3.0.802 Beta 2 Environment Windows operating system, I/NET 2.42 build 2316 loaded, StruxureWare Building Operation 1.3.0.724 Beta 1 wanting to upgrade to I/NET 2.42 build 2325 with 1.3.0.802 Beta 2 Cause Danish Ø character is not considered intelligent text. Upgrade from I/NET 2.42 build 2316 StruxureWare Building Operation 1.3.0.724 Beta 1 to 1.3.0.802 Beta 2 renders a empty database. StruxureWare Building Operation views the Danish character as unintelligent text and a filler such as a block, triangle or other symbol.   Resolution Workaround is to edit the names or characters used and replace characters not in the English alphabet. In the example below I have replaced any ambiguous characters with an X. The upgrade performs without issue. A second alternative is to upgrade I/NET to 2.42 build 2325 and StruxureWare Building Operation software to 1.3.0.802 Beta 2, which understands characters not in the English alphabet. Here I have placed Danish and Deutsch characters which upgrade without issue.
View full article
Picard Product_Support
‎2018-09-06 11:14 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1261 Views

Extended trendlogs are cleared and cannot be started after a restore

Issue Extended logs are not retrieving new values after an automation server (AS) has been restored underneath the enterprise server (ES). The problem occurs when there is an enterprise server extended log referencing an automation server extended log that is referencing a Xenta log.  Environment Workstation Extended Logs StruxureWare Building Operation Cause If an AS extended log with historical data is restored (for example after the Xenta controller that contains the Xenta log comes back online) the AS extended log can become locked up and will not record new data. When the Xenta controller goes offline and then comes back online the following sequence of events occur (Note: some values in this scenario are entered for example purposes only like the Xenta LogSize): After a restart of any kind the Xenta log will set its LastSeqNo to LastSeqNo+LogSize. This is to tell the AS extended log to do a read since it doesn't know if there are any new records; it should assume everything is new. (A key problem here is that the Xenta log will not increase its LastSeqNo until something reads from it. Normally when there is just an AS extended log and a Xenta log, the AS extended log reads and gets 3 records back. This makes everything go back to normal). The ES extended log notices that the AS extended log has been restored. The ES extended log sends a command to the AS extended log to clear the entire log and set the Last WrittenSeqNo to 101. This changes the scenario in event one from allowing the AS extended log to begin working properly. The AS extended log is only interested in new records now so it requests the LastSeqNo from the Xenta log. This value is used as the Last TransferredSeqNo in the AS extended log. When the AS extended log requests new records from the Xenta log, it answers 150 which is actually the LastSeqNo+LogSize. The Xenta log will not perform a real read to the external log to find out the actual LastSeqNo until something reads it and will not move beyond 150 because of the restart state it is in. Summary: The AS extended log won't read until the Xenta log tells the AS extended log that it has a new record and the Xenta log won't check for a new record until something reads it. Resolution Use a Trend Chart with Live Update The Xenta log can be opened in a trend chart with live update on. The chart will read every few seconds from the Xenta log causing the Xenta log to set its LastSeqNo to the value it should be. Given enough time the Xenta log will have reached the LastSeqNo where the AS extended log will start logging again. To speed this process up, the interval on the Xenta log can be set to the fastest possible scan time (10 seconds). Once the AS extended log begins collecting values again, the Xenta log can be changed back to the original settings. Note: The Xenta log will be cleared when changing the interval.   Create a New Extended Log A new AS extended log that monitors the Xenta log can also be created to correct the problem (disconnecting the old extended log). The new extended log will start reading from the beginning and start working immediately.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Labels:
  • EcoStruxure Building Operation
1453 Views
  • « Previous
    • 1
    • …
    • 69
    • 70
    • 71
    • …
    • 95
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore