Issue
I/NET Controller in StruxureWare Building Operation has a blue circle with a white down arrow on top of it.
Environment
I/NET Integration
StruxureWare Building Operation
Cause
Any change to the I/NET controller will result in this indication requesting an upload. Changing a configuration in a time schedule or updating a calc extension on a point are two examples of what might cause this.
Please note that the Upload DOES NOT complete the same action as a Station Save in I/NET. Upload will sync the StruxureWare Database with the I/NET database. To perform a station save from StruxureWare, right click on the Controller and select "backup".
Resolution
- Expand the I/NET Interface network object
- Right click on the offending controller
- Select Upload
- Wait a few seconds. A refresh of the System Tree may be required.