Extended trendlogs are cleared and cannot be started after a restore

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Extended trendlogs are cleared and cannot be started after a restore
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1455 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Extended trendlogs are cleared and cannot be started after a restore

Picard Product_Support
‎2018-09-06 03:10 PM

Issue

Extended logs are not retrieving new values after an automation server (AS) has been restored underneath the enterprise server (ES). The problem occurs when there is an enterprise server extended log referencing an automation server extended log that is referencing a Xenta log. 

Environment

  • Workstation
  • Extended Logs
  • StruxureWare Building Operation

Cause

If an AS extended log with historical data is restored (for example after the Xenta controller that contains the Xenta log comes back online) the AS extended log can become locked up and will not record new data.

When the Xenta controller goes offline and then comes back online the following sequence of events occur (Note: some values in this scenario are entered for example purposes only like the Xenta LogSize):

  1. After a restart of any kind the Xenta log will set its LastSeqNo to LastSeqNo+LogSize. This is to tell the AS extended log to do a read since it doesn't know if there are any new records; it should assume everything is new. (A key problem here is that the Xenta log will not increase its LastSeqNo until something reads from it. Normally when there is just an AS extended log and a Xenta log, the AS extended log reads and gets 3 records back. This makes everything go back to normal).
  2. The ES extended log notices that the AS extended log has been restored. The ES extended log sends a command to the AS extended log to clear the entire log and set the Last WrittenSeqNo to 101. This changes the scenario in event one from allowing the AS extended log to begin working properly.
  3. The AS extended log is only interested in new records now so it requests the LastSeqNo from the Xenta log. This value is used as the Last TransferredSeqNo in the AS extended log. When the AS extended log requests new records from the Xenta log, it answers 150 which is actually the LastSeqNo+LogSize. The Xenta log will not perform a real read to the external log to find out the actual LastSeqNo until something reads it and will not move beyond 150 because of the restart state it is in.

Summary: The AS extended log won't read until the Xenta log tells the AS extended log that it has a new record and the Xenta log won't check for a new record until something reads it.

Resolution

Use a Trend Chart with Live Update

The Xenta log can be opened in a trend chart with live update on. The chart will read every few seconds from the Xenta log causing the Xenta log to set its LastSeqNo to the value it should be. Given enough time the Xenta log will have reached the LastSeqNo where the AS extended log will start logging again.

To speed this process up, the interval on the Xenta log can be set to the fastest possible scan time (10 seconds). Once the AS extended log begins collecting values again, the Xenta log can be changed back to the original settings.

Note: The Xenta log will be cleared when changing the interval.

 

Create a New Extended Log

A new AS extended log that monitors the Xenta log can also be created to correct the problem (disconnecting the old extended log). The new extended log will start reading from the beginning and start working immediately.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 8394
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore