Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

StruxureWare Building Operation Enterprise Server Application Error occurs at computer start up

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • StruxureWare Building Operation Enterprise Server Application Error occurs at computer start up
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RyanSuar
    RyanSuar
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1908 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

StruxureWare Building Operation Enterprise Server Application Error occurs at computer start up

Picard Product_Support
‎2018-09-06 11:55 AM

Issue

The ES crashes during startup
 
  • SE.EnterpriseServer.exe - Application Error occurs, and the Building Operation Enterprise Server service cannot be started. 
  • Error contains "The memory could not "written"".

 

The port fields in software administrator shows a red indication on one or more of the ports

Environment

Enterprise Server

Software Administrator

IP ports

Cause

A program is already using the ports defined for the Enterprise Server
 
 
In general
 
You can check which program it is, by entering the following command in a command prompt, replacing ":port number" with the number you want to check, e.g. "0.0.0.0:80" for port 80: netstat -aonb | find "0.0.0.0:port number"
 
 
Now in the task manager, enable the coloumn "PID (Process Identifier)", and look for the process ID you get to the far right when running the command above. That will show what program is taking the port.
 
 
 
Skype
 
If you are running Skype on the Enterprise Server PC there could be a conflict between the default IP port settings and the IP port settings in Software Administrator. The default ports for SmartStruxure Enterprise Server are 80 and 443. By default, Skype will "use port 80 and 443 as alternatives for incoming connections" if the configured port is unavailable. When Skype is launched it appears to search for an open IP port. If it cannot find an open port within a period of time it may default to ports 80 and 443 as a backup. This behaviour appears to be intermittent. 

 

TeamViewer

In newer versions of TeamViewer this is no longer an issue, but it's good practice to select "Use UDP" in the advanced settings of TeamViewer

Resolution

In general, you can change the ports used by the Enterprise Server in the Building Operation Software Administrator.

 

If the issue is Skype do the following:

  1. In the Skype tools menu go to “Options…”
  2. Expand the “Advanced” settings on the left hand side.
  3. Click “Connection” in the Advanced section.
  4. Uncheck the setting that says "Use port 80 and 443 as alternatives for incoming connections"

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 11149
  • dump
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore