BASEDON keyword and PE Programming
  • BASEDON keyword and PE Programming
  • sesa139513
    sesa139513
‎2018-09-10 11:09 PM
BASEDON keyword and Plain English Programming
BASEDON key word fail
StruxureWare Building Operation site with up to release 1.3
Below is a sample program which uses the BASEDON keyword. Also, here are the steps to use that program:
  1. Create script program using keyword BASEDON (Below)
  2. Create an input and output for the program (below program that is EntreeBase and SortieBase)
  3. Set the input Entreebase to 1,2,3,4,5 and program errors out.
  4. Set input to 6 and program runs
Numeric Input EntreeBase
Numeric Output SortieBase
Line Debut
  basedon Entreebase goto 1,2,3,4,5
  goto 6
Line 1
  SortieBase=1
  goto Suite
Line 2
  SortieBase=2
  goto Suite
Line 3
  SortieBase=3
  goto Suite
Line 4
  SortieBase=4
  goto Suite
Line 5
  SortieBase=5
  goto Suite
Line 6
  Sortiebase=6
  goto suite
Line suite
  if sortiebase<1 then Sortiebase=20
  if ts<5 then goto suite else goto Debut
Line E
  Sortiebase=10
  goto Suite
BASEDON keyword has been submitted as an issue and expected to be corrected in a future release.
Tags (5)
  • 11951
  • 20250
  • alm
  • defect
  • number