Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,839
  • TAC IA Series 1,822
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 329
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1837 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 67
    • 68
    • 69
    • …
    • 92
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Sigma Transition to EcoStruxure Building Operation - Sigma Logging operation

Issue EcoStruxure Building Operation - Sigma logging does not work. Product Line EcoStruxure Building Operation, Sigma Environment Building Operation Enterprise Server Satchwell Sigma Cause Sigma logging has been transitioned to EcoStruxure Building Operation, but does not work. Resolution  The Procedure is as follows; Import the log data sets from Sigma to EcoStruxure Building Operation. Highlight "Log Sets" in the system tree under the Sigma Interface and select to "Send log sets" To confirm that the controller has started logging, select the appropriate controller, and choose "Diagnostics" and "Log Set Statistics" where you can see the statistics which include the log set/object details. To upload the logging, highlight the required log set and select "Retrieve Logged values". To review the uploaded data, highlight the required log value and view it as required Once that the logging in the Sigma controllers is working correctly to EcoStruxure Building Operation, logging from the Sigma server should be disabled.
View full article
Picard Product_Support
‎2018-09-06 09:08 AM

Last Updated: Sisko DavidChild Sisko ‎2020-07-08 06:13 AM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
1525 Views

LNS plugins for SmartStruxure are not included in the release.

Issue Missing LNS plugins for  EcoStruxure Buildings Operation Workstation Product Line EcoStruxure Buildings Operation Environment Building Operation Workstation Cause Plugins for EcoStruxure Buildings Operation are not included in these releases. Resolution Download the TAC Vista 5.1.9 tool pack and this will install the 100 series controller plugin and Z-Builder programming tool. Once this is installed EBO will be able to access these plugin when used with Open LNS. Download the TAC Vista 5.1.9 Toolpack - Software from Exchange Extranet. Direct Download also provided. 
View full article
Picard Product_Support
‎2018-09-11 09:21 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2020-06-23 11:28 PM

Labels:
  • EcoStruxure Building Operation
2454 Views

Configuring the Engage Mobile app

Issue What are the basics steps when setting up the Engage Mobile application to use it for the first time? Product Line EcoStruxure Building Operation Environment Building Operation Room Controller (RPC) Cause The Engage mobile application enables control of room temperature, fan speed, lights, and blinds/shades directly from a smartphone. A user can manage these settings when the application is connected to the RP-C controller. Resolution Below are the basic steps when setting up the Engage Mobile application to use it for the first time:  First create and configure the Occupant App Menu object. Make sure Bluetooth is enabled for the RP-C. Download the Engage mobile application and connect to the RP-C Available on App Store and Google Play To see details for every step please see video:  
View full article
Janeway Jonas_Brissman Janeway
‎2020-06-22 06:00 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2020-06-22 06:39 PM

Labels:
  • EcoStruxure Building Operation
2306 Views

Local Variables Pane in Script Editor is not displaying local variables

Issue The Local Variables Pane in the Script Editor is not displaying local variables or arrays. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause The Local Variables Pane can only be used in debug mode, i.e. when pressing Start and then either Step or trace (Trace On) through the script. When the Script Editor is not in debug mode the Local Variables Pane is empty. Note that the debugger is not available at all when editing scripts in the RP-C or MP-X, or when using Script Event Programs.  Resolution Click Start in the Debug tool list at the top of the Script Editor (or press F5) to start debugging. The local variables will now be visible in the Local Variables pane. If you have arrays you can expand them by clicking the plus sign. Next use the Step button (or press F10) to step through the program. The values of the local variables will change as the script is executed line by line. ClickTrace On to automatically step through the program. ClickTrace Off to stop the automatic stepping. For troubleshooting purposes, values can also be updated directly by editing the entry in the Value column in the Local Variables pane. 
View full article
Janeway PeterEdvik Janeway
‎2020-06-22 04:33 PM

on ‎2020-06-22 04:33 PM

Labels:
  • EcoStruxure Building Operation
1365 Views

Autocomplete window is off screen in Script Editor

Issue When there are multiple displays, and the script editor is in the right window, the autocomplete popup window goes off-screen. *note* this only happens in full screen Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause The issue depends on which way you assign the two monitors in the Windows settings or how you have the monitor cables hooked in the docking station/laptop. Resolution Swap the physical monitor plugs on the PC or docking station, allowing Windows to recognize your monitors synchronously from left to right Go into your Windows monitor settings and drag each screen to its proper position and hit apply.
View full article
Commander JonGreen Commander
‎2020-06-22 04:11 PM

on ‎2020-06-22 04:11 PM

Labels:
  • EcoStruxure Building Operation
898 Views

Poor data communications, communications failure or packet being corrupted

Issue Poor communications, communications failure or packet being corrupted Product Line Andover Continuum,EcoStruxure Building Expert,EcoStruxure Building Operation,Satchwell MicroNet,Satchwell Sigma,TAC INET,TAC Vista Environment Communications networks, BACnet MSTP, LON FT10, Infinet, Modbus RTU, Ethernet EMC (Electromagnetic compatibility) VSD Variable Speed Drive, VFD Variable Frequency Drive, Inverter Drive Cause Electrical Interference from Inverter (variable speed drives or VSD) Radiated or Induced RFI (Radio Frequency Interference) Resolution A VSD has the potential to create a large amount of electrical noise, to avoid causing issues it is vital they are installed as the manufacturer's instructions.  (Other devices also have this potential) Our systems are often used to control VSDs on fan motors, so if poor communications is found during the commissioning process, then try stopping all the fans in the area then re-testing the communications. A recent example was seen where LON FT10 communication was working ok until some VSDs were started, at this point LON devices and Object went offline intermittently. When all the VSDs were stopped the communication become completely stable. It was then possible to find which VSD was causing the problem and correct the VSD installation. In this case a LON analyzer would also have helped diagnose the issue.
View full article
Picard Product_Support
‎2018-09-06 09:15 AM

Last Updated: Sisko DavidChild Sisko ‎2020-06-19 06:39 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
2007 Views

BACnet devices not found but are visible in other applications

Issue BACnet devices not found but are visible in other third party BACnet applications An update may cause devices to go offline Product Line EcoStruxure Building Operation Environment BACnet IP Network Building Operation EnterpriseServer Building Operation Automation Server (AS, AS-P, AS-B) Cause According to BACnet routing rules, each BACnet Device should have a unique BACnet Instance ID and each BACnet Network should have a unique BACnet Network ID  When a BACnet interface is created on an EBO Server, a BACnet IP network is created with default Network ID of 1. This is a local Network address and in not published on the network, it is therefore not a problem if this is duplicated with other EBO Servers. On many site this will remain at 1 for multiple EBO servers with no problems. If a third party BACnet device uses a published Network ID that is identical to the EBO local Network ID, then it will be ignored. There will be a "Duplicate of local network"  System Alarm and line similar to below in the trace log "nsp.pin.BACnet Device <device name>claims to be router to Network #1234 but that is a local network (BACnetMain)" Resolution If the EBO Server is not finding a BACnet device on a different network type (via BACnet routing like MSTP or virtual IP) then it could be the Network ID is identical to the local EBO Server Network ID. If this is the case, then simply change the EBO local Network ID and retest. BACnet Devices on the same IP network, including those on different IP subnets and linked via BBMD or Foreign Devices are not BACnet routed and therefore will not have this issue (no BACnet Network ID route is involved) Some earlier versions of EBO did not ignore these duplicate Network IDs, thus when up grading some devices could go offline. The workaround would be the same. The correction to the BACnet operation occurred in v1.9.3 and v2.0.2
View full article
Dave_Shore Schneider Alumni (Retired)
‎2020-06-19 06:01 AM

Last Updated: Sisko DavidChild Sisko ‎2020-06-19 06:01 AM

Labels:
  • EcoStruxure Building Operation
4539 Views

Living Space Sensor goes offline when upgrade RP-C firmware

Issue Living Space Sensore goes offline after upgrading SmartX Controller firmware from 2.0x to 3.01 or later Product Line EcoStruxure Building Operation Environment Building Operation Room Controller (RPC) v3.01 or later Building Operation SmartX Living Space Sensor Cause Living Space Sensor RJ-45 connector is plugged into Room Bus port on RPC. Resolution Move RJ-45 connector from Room Bus port to Sensor Bus port.
View full article
Picard David_Purser Picard
‎2020-06-18 01:17 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2020-06-18 03:44 PM

Labels:
  • EcoStruxure Building Operation
2074 Views

The value of DateTime will different depending on how the variable is declared

Issue The value of DateTime will different depending on how the variable is declared Differences between DateTime declared as a local variable and as input, output or public in Script program Product Line EcoStruxure Building Operation Environment Building Operation WorkStation Script Editor Cause Local and bound variables will initialize differently Resolution Local DateTime variables are local and known only to the Script program or function, and are initialized to the current local date-time value of the sever in which they  execute. Binding variables, including Input, Output and Public variables, are not effected by the Script engine by default. The EBO system uses the 1/1/1970 date as default and the Script simply uses that. If a different initial value is required then one can be set in the script
View full article
Picard Product_Support
‎2018-09-06 09:11 AM

Last Updated: Sisko DavidChild Sisko ‎2020-06-18 02:19 AM

Labels:
  • EcoStruxure Building Operation
1725 Views

Controller memory usage for logging

Issue How to calculate total memory required for controller to store logging information for the required duration. Product Line EcoStruxure Building Operation, Andover Continuum Environment NetController (CX9900, CX9940, CX9680, bCX9640) InfinetController (i2xxx) BACnet Controller (bCX4040, bCX9640, b3xxx) Cause Need to know how much memory is needed per point to determine the maximum number of entries and minimum interval time that the controller can use. Resolution The general equation of calculating memory use for controller logging is as below; * Memory usage per point = { 8bytes + (4bytes * NumberOfLog) } In addition to that, each controller requires minimum 1~2KB of freemem after the controller logging memory allocated.  Regarding the log interval, if the point is being logged for controller only, you can set the interval in seconds unit.   But if you configure the point for ExtendedLog as well, the logging interval should be in minute unit. Again, if there many objects with one minute interval for Extended Logging, it will affect the performance of the Cyberstation and also increases the size of ContinuumDB dramatically in short period of time. In this case, consider increasing the log interval to 5 ~ 15 minutes for Extended Logging.
View full article
Picard Product_Support
‎2018-09-06 01:28 PM

Last Updated: Sisko DavidChild Sisko ‎2020-06-16 12:13 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
2110 Views

Open TGML links in a new window/tab in Workstation

Issue Is it possible to open TGML links in a new window or tab in Workstation? Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause The user wants to keep the current graphic open and open a new graphic/calendar/function etc so that both can be viewed simultaneously. Resolution Hold down SHIFT key whilst clicking on the link.
View full article
Picard Product_Support
‎2018-09-06 11:06 AM

Last Updated: Sisko DavidChild Sisko ‎2020-06-10 07:44 AM

Labels:
  • EcoStruxure Building Operation
2937 Views

Operator Panel on the Automation Server Classic

Issue Pins 4 through 7 across the top of the Automation Server are labeled as "Operator Panel" although there is not an Operator Panel part available. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server (AS) Cause There is no explanation of what the AS Operator Panel contacts are for? On front of AS:  Operator Panel Terminals Term 4 RET Internally connected to ground Term 5 10V 10 VDC max. 120 mA Term 6 Tx/Rx+ RS-485 communication Term 7 Tx/Rx- RS-485 communication Resolution At one time there were plans to create an Operator Panel so terminals were reserved on the Automation Server for local OP connection, however, these plans were not implemented. The next generation Automation Server Premium (AS-P) does not have the Operator Panel label, and today most operators use Webstation or Workstation.
View full article
Picard Product_Support
‎2018-09-10 10:09 PM

Last Updated: Sisko DavidChild Sisko ‎2020-06-05 06:57 AM

Labels:
  • EcoStruxure Building Operation
1938 Views

No longer possible to drag the application into the "Include types" box while doing a search

Issue Unable to drag and drop the Application folder into the include types box while performing a search of application files.   Product Line EcoStruxure Building Operation Environment Building Operation Workstation v3.0.x  Building Operation Workstation v3.1.x  Cause Searchable interface not implemented on the Application folder (nor on other devices like b3). This is a known issue in v3.0.x and v3.1.x Resolution Rather than using the left mouse button to drag the application folder, right-click the application folder to drag and drop into the include types box. This is to be fixed in 3.2.1.x.
View full article
Commander JonGreen Commander
‎2020-06-04 11:33 AM

Last Updated: JohnBoehmer Schneider Alumni (Retired) ‎2020-06-04 11:37 AM

Labels:
  • EcoStruxure Building Operation
786 Views

The Status of a Windows service continually indicates Starting or Stopping

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Sometimes as an administrator, you may need to kill a service which is stuck at starting or stopping in order to avoid having to reboot a server in the middle of the day. Or even after the reboot, the service will not start. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Licensing Server Security Expert Windows Services Access Expert Windows Services (on-premise only) Cause Sometimes the service times out and gets stuck in a loop due to fallback protocols within the service Resolution Find out the name of the service To do this, go into services and double click on the service which has stuck.   Make a note of the “Service Name”. Find out the PID of the service Open an elevated command prompt and type in: "sc queryex servicename" (where servicename is the name of the service you obtained from Step 1). Make note of the PID Kill the PID From the same command prompt type in: "taskkill /f /pid [PID]" (Where [PID] is the service number).   If it is successful you should receive the following message: "SUCCESS: The process with PID XXXX has been terminated."     Be careful of what you are killing though. If you kill a critical windows service you may end up forcing the machine to reboot on it own.   If the service returns back into this state you may need to increase the time allotment for the service to start.   Global (entire system): Open Windows Registry: Start -> Run -> regedit.exe File --> Export --> make a backup of the current registry Navigate to HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\Control\ Right click on the right page ---> New ---> DWORD call the new DWORD "AutoStartDelay" Set AutoStartDelay in milliseconds (decimal). E.G. 240000 is 240 seconds. Per-service: Open Windows Registry: Start -> Run -> regedit.exe File --> Export --> make a backup of the current registry Navigate to HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\Services\<servicename> To increase the default delay of 120 seconds, right click the registry key and add new key AutoStartDelay (DWORD (32-bit)) Set AutoStartDelay in milliseconds (decimal). E.G. 240000 is 240 seconds.
View full article
Commander JonGreen Commander
‎2020-06-04 10:51 AM

on ‎2020-06-04 10:51 AM

Labels:
  • EcoStruxure Access Expert
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
1392 Views

Unable to assign output channels on a some b3 series controller under an AS

Issue Unable to assign output channels on a some b3/i2 series controller under an AS. CCT(Continuum Conversion Tool) unable to assign channel with error "Could not find channel" in the conversion report. When creating an output channel, that is out of range, the workstation error is "Could not find channel" eg. if output channels 15 or 16 (on b3810) are assigned Product Line EcoStruxure Building Operation Environment AS ES b3, i2 Expansion Module xPD04, XPD02, xPA04, xPA02 Cause b3/i2 series expansion channels are software limited in line with the maximum xP module capacity The maximum b3/i2 expansion current available is 180mA, so some combinations of 2 xP modules are not supported, see below   Resolution Both input and output channels are limited in line with the allowable xP expansion units that can be added. For example a maximum of 6 xP output channels can be added to b3/i2920, b3/i2810, b3/i2814, b3/i2850, b3/i2851 & b3/i2853 controllers, (2 xPD/A04 Output modules is above the maximum power supply to xP units from the b3/i2 series controllers)                                   Output Channels               On board                               xP Modules    b3920     1 to 16                                   18 to 22 b3810     1 to 8                                      9 to 14 b3814     1 to 8                                      9 to 14 b3850     1 to 4 (5 reserved)                  6 to 11 b3851     1 to 4 (5 reserved)                  6 to 11 b3853     1 to 4 (5 reserved)                  6 to 11 NOTE Continuum did not limit the channel numbers, thus unsupported configuration could be installed and in some cases these may work. This can cause an issue during an upgrade/conversion.
View full article
Picard Product_Support
‎2018-09-06 12:28 PM

Last Updated: Janeway PeterEdvik Janeway ‎2020-06-04 06:23 AM

Labels:
  • EcoStruxure Building Operation
2560 Views

It takes a long time to open properties for a Xenta signal in Webstation

Issue When a TGML graphic is opened from Webstation and the user right clicks on a value in the graphic to open properties, it can take up to 20 seconds before the properties dialog is displayed. During the 20 seconds the working area is just grey. Product Line EcoStruxure Building Operation Environment Building Operation Webstation 2.0.4 and earlier versions Cause This problem only occurs when the signals in the graphic resides in a TAC Xenta; The problem has not been observed with Modbus or BACnet signals, and is only present in Webstation, not in Workstation. Resolution This issue is fixed in EBO 3.0. There is also a hotfix for version 2.0.4. It is labelled 2.0.4.5801. Contact you local technical support organisation if you need the hotfix.
View full article
Janeway Jonas_Brissman Janeway
‎2020-06-04 06:14 AM

on ‎2020-06-04 06:14 AM

Labels:
  • EcoStruxure Building Operation
773 Views

Engage App BLE Filtering

Issue When "Engage App BLE Filtering" set to "True" in an RP-C it is not possible to connect to the RP-C via Bluetooth using eComission SmartX controller mobile application. How do I set "Engage App BLE Filtering" to "False"? Product Line EcoStruxure Building Operation Environment Building Operation eCommissioning Tool Cause A factory reset of an RP-C will set "Engage App BLE Filtering" to "True". The "Engage App BLE Filtering" is also set to "True" when upgrading the RP-C from firmware version 2 to version 3. Resolution The only way to set "Engage App BLE Filtering" to "False" is to use the  eCommission SmartX Controllers mobile application connected to the RP-C using an IP connection.  
View full article
Janeway Jonas_Brissman Janeway
‎2020-06-04 04:59 AM

on ‎2020-06-04 04:59 AM

Labels:
  • EcoStruxure Building Operation
1411 Views

Function Block example or Macro Block

Issue Need program example of Macro Block for Function Block program. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause Macro Block Library is intended as an example and may need to be adjusted to the actual application. Resolution A Macro Block Library is included in the installation of the Function Block Editor. Inside the Function Block Editor, right click in an empty space and select Load Macro. If you do not see the Macro Block Library directly, please navigate to  C:\ProgramData\Schneider Electric EcoStruxure\Building Operation 3.1\WorkStation\Function Block Editor Here, you can select Macro Library Function block to find different Macro Blocks:                  Macro Block Library Macro Block Library for TAC Xenta series Macro Block Library Xenta700 Macro Block Library For TAC Xenta 700 series Macro Library Function Block Macro Block Library For Function Block Editor Process Models Process Models Library For TAC Xenta series Process Models Function Block Process Models Library For Function Block Editor Process Models Xenta700 Process Models Library For TAC Xenta 700 series User Library Reserved location for user made Macro Block The first three folders in the list above (Macro Block Library, Macro Block Library Xenta700 and Macro Library Function Block) each contain the following sub folder structure: Air handling Control Function Calculation Common Efficiency Energy Psychrometric Heating Control Function Miscellaneous Function SNVT Timers The other four folders contain macro blocks without any sub folder structure, i.e. they are located directly in the folders.
View full article
Kirk MikaelKrantz Kirk
‎2020-05-05 06:52 AM

Last Updated: Janeway PeterEdvik Janeway ‎2020-06-04 04:07 AM

Labels:
  • EcoStruxure Building Operation
3039 Views

AS-P Missing Heatsinks

Issue Some AS-P controllers do not have a heatsink installed where others do. Product Line EcoStruxure Building Operation. Environment Building Operation Automation Server Cause Originally the design of the AS-P was to be universal and comply with various standards with one design. The standards that have a strict temperature requirement on components are related to Smoke Control and Access Control. In 2019 we decided to streamline the production of AS-P and only use the heatsink on those versions where it is required. AS-P with heatsink installed. AS-P without heatsink installed. Resolution The AS-P SMK and AS-SSC versions will still have the heatsink all other models after week 50 of 2019 will come without heatsinks. Products without heatsinks can be identified by a suffix on the individual box that the product came in. A suffix -A is with heatsink and suffix -B is without a heatsink, as shown below.
View full article
Spock PeterLarsen Spock
‎2020-05-28 07:27 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2020-05-28 07:30 PM

Labels:
  • EcoStruxure Building Operation
1066 Views

Display local server time PE Script example

Issue Provide a solution for displaying local server time Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Enterprise Server Cause Request to display local server time Resolution Example code below can be inserted into a PE Script to allow display of local server time from within the workstation. By converting the time into a string the display of the information is not affected by any localization that is attempted by the client. *************************** datetime output ServerTime, ClientDisplayTime string output DisplayTimeString, DisplayTimeString2 String ampm numeric h1, h2 numeric Adjustment ' Time Adjustment: UTC Offset, DayLight Savings Time Adjustment = 4*3600 ServerTime = Time 'Set the desired Client Display Time ClientDisplayTime = ServerTime + Adjustment 'Set String to ServerTime print ServerTime to DisplayTimeString h1 = TimePiece(hour, ServerTime) if h1 = 24 then h1 = 12 if h1 > 12 then  h2 = h1-12  ampm = "PM" else  h2 = h1  ampm = "AM" Endif print TimePiece(month, ServerTime);"/" ;~       TimePiece(dayofmonth, ServerTime);"/";~       TimePiece(year, ServerTime),~       h2;":"; ~       TimePiece(minute, ServerTime);":";~       TimePiece(second, ServerTime), ampm to DisplayTimeString2 ****************************
View full article
Picard Product_Support
‎2018-09-06 10:14 AM

Last Updated: Sisko DavidChild Sisko ‎2020-05-28 03:26 AM

Labels:
  • EcoStruxure Building Operation
1796 Views
  • « Previous
    • 1
    • …
    • 67
    • 68
    • 69
    • …
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of