RP-C with static IP configured has an unexpected IP address after restart.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • RP-C with static IP configured has an unexpected IP address after restart.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • Gary
    Gary

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3334 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

RP-C with static IP configured has an unexpected IP address after restart.

Gary Schneider Alumni (Retired)
‎2021-08-05 07:11 AM

Last Updated: Sisko DavidChild Sisko ‎2021-08-05 07:14 AM


Issue

When changing IP settings, the change needs to be activated, before the RP-C uses the new settings.

Product Line

EcoStruxure Building Operation

Environment

Building Operation Room Controller (RP-C)

Cause

RP-C configured with static IP goes off-line or has an unexpected IP address after restart.

Resolution

If the RP-C is hosted as Dynamic but it is required to be provided with a static IP address.

01.jpg

RP-C IP settings can be changed to Static and saved.

However, this doesn’t save the new settings to the RP-C controller, they are only saved at the automation server level.

02.jpg

Therefore, if a power cycle is carried out, the RP-C is still set to Dynamic and gets an IP from the router, although it shows as static in workstation and the Ecommissioning tool.

Note: If the router is not setup as a DHCP server, the RP-C may not come back on-line, because the RP-C is looking to be provided with an IP address by the DHCP server.

03.jpg

 

Any changes to the IP settings of an RP-C made in the workstation, need to also be activated in the RP-C controller.
This is done by right mouse clicking on “IP Network Settings” selecting “IP Commands” then “Activate changes”

04.jpg

Now when seen in device discovery window the IP address is the static IP address configured and not the one collected from the DHCP server.

05.jpg

If changes are made to the IP settings using the Ecommissioning tool, prior to hosting the RP=C, the same applies, activating the changes must be done by selecting “Device restart” and selecting “Activate IP Changes” followed by “restart”.

 10.jpg

Additional information is available by logging into the Ecostruxure Building Help page.

https://ecostruxure-building-help.se.com/bms/Topics/show.castle?id=12275&locale=en-US&productversion...

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • GaryMontague21
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore