Issue
When trying to download a b3866 device, receive an Untranslated BACnet Error.
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Workstation
- Building Operation Automation Server (AS, AS-P, AS-B)
- BACnet b3 or Infinet i2 Controller
Cause
Infinet ID 0 or duplicate Infinet Id
Resolution
Export the objects in the controller.
Delete the b3866 (or other b3 or i2) controller. Re-learn the controller.
Manually assigned the Infinet ID to the next one available.
Software reset the b3/i2.
Download the b3/i2. Back up to flash.
Import the objects.
Download the b3./i2. Back up to flash.