Notifications are sent when an alarm shunt is toggled

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Notifications are sent when an alarm shunt is toggled
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • sesa150561
    sesa150561
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1868 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Notifications are sent when an alarm shunt is toggled

Picard Product_Support
‎2018-09-11 04:28 AM

Issue

Notifications (email or text file) are sent when an alarm is enabled by the shunt variable

Environment

Notifications

Cause

The Alarm object has 6 possible states that it can take

 

  • Normal - Idle state where the alarm monitors the variable.
  • Alarm - When an alarm is triggered, the state of the alarm changes from the normal state to alarm state.
  • Disabled - You can disable an alarm when the alarm is triggered by faulty reasons, the alarm toggles between the alarm state and reset state, or maintenance will trigger the alarm. A Disabled alarm can be hidden in the Alarms pane or Alarm Views. To reset the alarm, you have to show hidden alarms and then enable it. When you show disabled alarms, enabled alarms are hidden. Alarms are also disabled by using the Shunt Variable in the alarm configuration.
  • Reset - The monitored variable has returned to a value that is within the normal condition of the alarm, but the alarm has to be acknowledged by a user before the alarm returns to normal state.
  • Acknowledged - A user or user group has acknowledged the alarm.
  • Fault - If a BACnet device reports values that it knows are not trustworthy, the monitoring alarm is put in fault state.

The notification is triggered by transitioning to any of these states as selected in the "Notify on transition to" portion of the notification configuration

This means that if you wish to receive a notification on transition to the Normal state, you can check the Normal box. However, this means that not only are notified when the alarm transitions from Alarm to Normal, but from Disabled to Normal or Fault to Normal.  Some of the scenarios may be undesirable.

Resolution

There are two ways an alarm can go to Normal:

  1. Alarm to normal
  2. Disable to normal

In the Email notification main filter, you can choose to not get a notification from disarm but you might want to get a email about normal since you want to get a email when an alarm goes to normal.

To accomplish this you need to add another filter called "Previous alarm state." (This filter does not work in releases prior to 1.3 SP1.)

To add the filter Previous Alarm State:

  1. Click on the green +
  2. Check the boxes you want:
    • Acknowledge
    • Alarm
    • Normal
    • Reset
  3. Make sure Disable is not checked

This means that when the previous state was disabled (shunted), a notification will not be sent.

 

Example1: This object will always trigger a notification on Alarm.  The notification will be triggered regardless of Previous State. If the Alarm is Disabled by a shunt, then enabled, but the Monitored Variable is still out of Range, a notification will be sent.

 

Example2: This object will only trigger a notification on the Transitions from Alarm to Reset, Alarm to Normal, Acknowledged to Reset or Acknowledged to Normal. This might be desirable for a user that wished to know when an object in Alarm returns to normal operation, but not know when an alarm goes from Disabled to normal operation.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 13812
  • nuisance
  • plus
  • receiving
  • sign
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore