Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Create EWS between SmartStruxure and SmartStruxure Lite

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Create EWS between SmartStruxure and SmartStruxure Lite
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • Derrick_Ratliff
    Derrick_Ratliff
  • RyanSuar
    RyanSuar
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3159 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Create EWS between SmartStruxure and SmartStruxure Lite

Picard Product_Support
‎2018-09-11 04:31 AM

Issue

Create EWS between SmartStruxure and SmartStruxure Lite

Product Line

EcoStruxure Building Expert, EcoStruxure Building Operation

Environment

  • StruxureWare Building Operation site
  • SmartStruxure Lite site

Cause

Steps to create EWS (EcoStruxure Web Service) between SmartStruxure and SmartStruxure Lite

Resolution

Release requirements:

  • SmartStruxure Building Operation Release 1.3.938 and higher
  • SmartStruxure Lite Version: Schneider Electric 2.7.0 and above

Verification the Enterprise Server is running

  1. Open Building Operation Software Administrator.
    If Status shows Stopped, you must configure Building Operation. Otherwise, proceed to step 2.
  2. Ensure all Ports are correctly configured.
  3. Click Start Service and wait until application running shows in Path field.
  4. Click OK.

Building Operation is now ready to integrate with SmartStruxure Lite

  1. The following example is using Server 1 in System Tree tab.
  2. In System Tree tab, right-click on Server 1.
  3. In newly opened window, select New.
  4. In newly opened sub window, select Interface.
  5. Click on Web Service to expand.
  6. Select EcoStruxure Web Service.
  7. In Name field, enter EcoStruxure Web Service.
  8. Click Next button.
  9. In Server field, enter IP address of Multi-purpose Manager (MPM) Controller you are connecting with.
  10. In Protocol field, ensure Communication port matches that on your server.
  11. In SOAP Endpoint field, enter ews in lower case letters. Take note that from SBO version 1.5 onwards, 'SOAP Endpoint' has been renamed to 'EWS Path'.
    IMPORTANT: You must enter ews in lower case letters in step 11.
    NOTE: If you are connecting to another StruxureWare Server, you must use an account that is in the default domain for log in credentials.
  12. Click Create button.
  13. Allow database to save completely before moving on to next step.
  14. In Server Tree tab, ensure new interface shows.
  15. You are now ready to connect your MPM Controller with Building Operation. Refer below to “Procedure - Connect MPM Controller to Building Operation."

Procedure - Connect MPM Controller to Building Operation

  1. Ensure your MPM is physically connected to your workstation.
  2. In Server Tree tab, expand System folder.
  3. Expand Hardware folder.
  4. Expand EcoStruxure Web Services folder.
  5. Right-click C2G_root folder and select Host EWS Objects in sub window.
  6. Expand EcoStruxure Web Services folder.
  7. Select EcoStruxure and then select Web Services Properties Tab.
  8. Set Alarm Polling to Disabled.

Procedure - View and Watch Data Points

  1. Expand CAN2GO controller.
  2. The List View tab shows all Objects available in Device.

NOTE: EWS Consume in Building Operation server does not support connection over a ProxyServer.

Labels (2)
Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 13867
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore