Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,851
  • TAC IA Series 1,825
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 149
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 478
    • 479
    • 480
    • …
    • 508
  • Next »

StruxureWare Building Operation Runtime Compatibility available during Upgrades

Issue Is it supported to access an Automation Server 1.4.0 with the Workstation 1.4.1? Are there any problems and what features are supported when accessing a 1.4.0 Automation Server with WorkStation 1.4.1? Environment Enterprise Server / Workstation 1.4.1 Automation Servers 1.4.0, 1.3 with SP1 and SP2 Cause Understanding of the new Runtime Compatibility mode available in 1.4.1 available during system upgrades Resolution Building Operation supports runtime compatibility between servers running two versions on a single system, during an upgrade process. Version 1.4.1 servers are runtime compatible with version 1.3 SP1 and 1.3 SP2 servers. The system is able to exchange runtime information between 1.4.1 servers and 1.3 SP1 or 1.3 SP2 servers. However, configuration changes cannot be made from an upgraded WorkStation via an upgraded Enterprise Server to a non upgraded Automation Server, such as creating, configuring, and deleting objects. There is also no runtime compatibility for WebStation. Runtime compatibility means you can delay the upgrade of some Automation Servers running version 1.3 SP1 or 1.3 SP2 while upgrading the Enterprise Server, WorkStation, Reports Server, and some Automation Servers to version 1.4.1. You cannot make any configuration changes on an Automation Server running the 1.3 SP1 or 1.3 SP2 version with WorkStation and Enterprise Server running the 1.4.1 version. However, you can make the changes using a parallel WorkStation running a 1.3 SP1 or 1.3 SP2 version that is connected to the Automation Server running the 1.3 SP1 or 1.3 SP2 version. Full compatibility is supported on Automation Servers running the 1.4.0 version   Additional detail is available on the Online Help http://help.sbo.schneider-electric.com/topics/show.castle?id=9807&locale=en-US&productversion=1.4&a=1 Supported Features: Navigate You can navigate in the system tree of an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. However, object and property types removed in the 1.4.1 version compared to the 1.3 SP1 or 1.3 SP2 version are not be displayed in the system tree. Search You can perform an object or property search on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. However, object and property types removed in the 1.4.1 version compared to the 1.3 SP1 or 1.3 SP2 version are not be displayed in the search list. View Events You can view detailed information and perform commands on events on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. The 1.4.1 Enterprise Server will also store events from an Automation Server running 1.3 SP1 or 1.3 SP2 version. View Trend Logs and Trend Charts You can view trend log lists and trend charts on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. Extended trend log lists in the server running 1.4.1 version are functional and be able to retrieve values from a server running the 1.3 SP1 or 1.3 SP2 version. View Graphics You can navigate to and view a graphic on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server at 1.4.1 version. Graphic variable values can be changed with Graphics Editor, but configuration data cannot be changed. View Alarms You can view detailed alarm information from an Automation Server running the 1.3 SP1 and 1.3 SP2 version, with WorkStation and Enterprise Server at 1.4.1 version. Also actions on alarms can be performed, such as assigning or disabling an alarm and enabling a Change-state logging. View Dynamic Values You can navigate to and view dynamic values in the Watch pane from an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. However, because there is no way to navigate to and view objects or properties that have been removed in the 1.4.1 version, such dynamic values cannot be viewed. Transfer Values You can transfer values from an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with an Enterprise Server or Automation Server running the 1.4.1 version and the other way around. Change and Force Variables You can change and force variables using properties on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. Lead and Shadow relationships Lead and Shadow relationships work for all objects with the runtime compatibility support. Backup You can make a backup of an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. Log on to the Enterprise Server and then make a backup of the Automation Server running the 1.3 SP1 or 1.3 SP2 version. You can also log on directly to the Automation Server running the 1.3 SP1 or 1.3 SP2 version with WorkStation running the same 1.3 SP1 or 1.3 SP2 version, and then make a backup of the Automation Server.
View full article
Picard Product_Support
‎2018-09-11 08:32 AM

Labels:
  • EcoStruxure Building Operation
2460 Views

Unable to load an attribute to all doors in Continuum ACX

Issue All the doors under an ACX5720 can not be loaded with an attribute. The system status value goes back to "Nodatabase" after reloading the ACX controller. Some doors no longer open on a card swipe. The event type is "Invalid attempt" and the message event is "No Destination Area." When reloading the controller (or just a door object) the error below is seen in the distribution properties: "UNABLE TO RELOAD ATTRIBUTES FOR (**DOOR NAME**). UNABLE TO RELOAD OBJECT. ERROR TEXT UNDEFINED (TBD) 0X00002001. AN ERROR WAS DETECTED WHILE ATTEMPTING TO SET AN ATTRIBUTE IN A REMOTE INFINITY OBJECT" Product Line Andover Continuum Environment ACX5720/5740 Continuum 1.94 Cause The channel configuration may not be correct. Resolution Set all the channel numbers to 0 for the door Select the door separately Send it to the controller If there is no error when sending the door to the controller, then reset the all the channel numbers correctly. Change the value of systemstatus to "Normal" Reload the ACX controller  
View full article
Picard Product_Support
‎2018-09-06 09:56 AM

Labels:
  • Andover Continuum
2462 Views

Tacos not responding when starting Workstation

Issue  Tacos not responding when starting Workstation Environment Vista Tacos.exe Cause If a trendlog is manually on but does not have a value to log, it can cause Tacos to crash (not responding). Resolution Go to the TAC Vista Installation folder Find the file named TACaddon01.DLL Rename TACaddon01.DLL to TACaddon01OLD.DLL and start Vista Server and Workstation again. Search for all trendlogs and make sure they have a point to read from, if not set them to manually off.
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • TAC Vista
969 Views

Valve mounting position in pipe work

Issue Is it possible to mount a valve in any direction in a pipe work? Environment general Valves general actuators Cause Mounting a valve/actuator in the incorrect position may cause damage to actuator. Resolution The positioning options of the valve are based on the recommendations on how to mount the actuator. Please see the actuator data sheet for recommendations. 
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • Field Devices
1454 Views

Unable to save a OGC Standard graphic page in vista 5.1.x

Issue When you edit a OGC standard graphic and then attempt to save you get the error "Cannot save graphic object. Cause: FILE-service not available" Environment Vista 5.1.x Cause The OGC standard graphic does have this unknown issue on some sites. Resolution To allow the edit of the OGC edit the standard graphic and save out of the database. The open with the OGC editor and make the changes that are required and save back into the vista database.
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • TAC Vista
900 Views

SHD100/SHD101 Humidity Sensor - Maximum Air Velocity

Issue What is the Maximum Air Velocity that can pass across a SHD100/SHD101 Humidity Sensor? Environment SHD100 SHD101 Cause Some applications has a high velocity that needs to be measured. Resolution The flow rate is only critical at higher humidity. Furthermore, it also depends on the porosity of the filter. At humidity less than 95% r.H. up to an air velocity to 15 m/s there should be no problem.
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • Field Devices
1030 Views

During installation and commissioning of a MNL-800, a component labeled MFC21 on the backplane was damaged. Is it necessary to replace the backplane?

Issue During installation and commissioning of a MNL-800, a component labeled MFC21 on the backplane was damaged. Is it necessary to replace the backplane? It seems like the MNL-800 is still completely functional.  It's reading all of its inputs and the program logic is controlling the outputs accordingly. Environment MNL-800 Cause The issue is typically a ground loop between full-wave and half-wave devices or power supplies connected to the UIs and / or AOs.  MFC21 is a Multi-function Ceramic protection capacitor / varistor component connected between the internal +15 VDC and earth ground (not common).  This and the other 28 varistors on the base board provide various forms of protection.  MFCs have burned out in situations that contain one or more transformers and a combination of full-wave / half-wave devices. Connections (common) between these devices can cause undesired ground loops (especially where transmitters are involved). It may also be related to how the transformers are wired (e.g. 24H / 24G or one side tied to earth ground).  The MNL-800 is a full-wave power supply device. Resolution Review the power wiring of all connected I/O. Replacing the backplane is ideal because it will provide proper protection for the next voltage spike. Without a functional MFC21, the logic card may get damaged.
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • TAC IA Series
992 Views

The Enterprise Network Server is licensed for 3 subordinates but when trying to add one it faults with the message "exceeded device limit of three"?

Issue The Enterprise Network Server is licensed for 3 subordinates but when trying to add one it faults with the message "exceeded device limit of three"? Environment G3 Enterprise Network Sever Cause If stations had been added to the Niagara Network in the Enterprise Network Server and then deleted the subordinate count in the license does not reset. Resolution Restart the station and the subordinate count in the license will be reset to the correct number and allow the addition of more stations if the limit has not been reached.
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • TAC IA Series
816 Views

A Niagara R2 / ASD integration has two ASD services but serial tunneling only works with one service.

Issue A Niagara R2 / ASD integration has two ASD services but serial tunneling only works with one service. Environment Niagara 522 or higher Cause Both services cannot support tunneling simultaneously. Resolution Enable tunneling on one ASD service at a time.  Leaving both services enabled for tunneling will only allow the first ASD service to allow a tunnel connection.  A station restart may be required.
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • TAC IA Series
848 Views

The Triac (V) outputs on the TAC Xenta 120-FC device goes ON, but never OFF

Issue The Triac (V) outputs on the TAC Xenta 120-FC device goes ON, but never OFF. In this case, it can open the valve, but the device could not close the valve. Environment TAC Xenta 121-FC TAC Xenta 121-HP Cause If the device is powered with 24 VDC, the Triac will not work properly. According to the datasheet, the TAC Xenta 121-device should always be powered by AC, not DC. Triac is an acronym for Triode for Alternating Current, and could only be working with AC power supply. Resolution Correct the power supply to the device to use AC, not DC.
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1405 Views

Error 0x00001402 (Reached end of the list).

Issue A Plain English program is becoming disabled.  The controller error log logs the following error. 0x01402 (Reached end of the list). Environment Continuum Plain English Error b3 i2 Cause 0x00001402 (Reached end of the list) is a Plain English error.  This error most often occurs when a program is calling a Plain English Function that contains no byte code.. Resolution Edit each InfinityFunction in the controller to determine which function is empty (contains no programming).
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1738 Views

Why aren't the MSTP Devices coming in to SBO when upgrading site from Continuum?

Issue Some MSTP Devices show up when learned but other are not coming in. They worked fine on the Continuum install with the same MSTP network. Environment Automation Server Cause The AS has a maximum of 50 MSTP nodes and the b3 controllers that are not coming in are above this NodeId. Resolution Change the b3's NodeId's to a value below 50. 1. Use the Continuum system to change the Id by deleting the device object from the database, recreating it with the new NodeId. 2. Clear the controller to factory default.
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • EcoStruxure Building Operation
932 Views

Port no's used by the MPM controllers

Issue What firewall port no's used by the MPM controllers need to opened on a PC or router Environment Routers Firewall Cause What port numbers are required to be opened on a router or firewall? Resolution For browser to MPM communication, port number 80 (TCP) needs to be open. For BACnet over IP communication, port number 47808 (UDP) (configurable in the MPM) needs to be open. For Modbus over IP communication (future), port number 502 (TCP) needs to be open.
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • EcoStruxure Building Expert
1301 Views

Batch printing Personnel badges in EpiBuilder, EpiSuite or GuardDraw

Issue Customers at times need to be able to batch print badges Environment Continuum Windows XP Windows 7 Windows Server 2003 Windows Server 2008 Cause There's a need to know how the EpiBuilder, EpiSuite and GuardDraw batch mechanism works to utilize the batch printing feature Resolution To Batch print: Open a personnel object and select Make/Edit badge and then from within the Make/Edit badge window select File>Batch Print Cards You cannot select specific cardholder numbers to batch print like 101-110, you have to start with 1 and select a range from there. 1-10 which will print 10 card holder records that are marked as not printed by EpiSuite. EpiSuite indexes its cards for batch printing.  The Index number that Episuite uses does not match our card number.  As an example say you have 10 cards with card numbers 1-10 and you send cards 1-5 as a batch to the printer.  When you want to print the next 5 cards, Episuite does not see them as cards 6-10 but as cards 1-5 again.  This is due to EpiSuite own indexing scheme. If a card has already been marked as printed it won’t show up in the batch.  The order is determined by the index in the database.  Most likely the order in which the cards were created. To print a card again: Bring up the cardholder in Make/Edit badge> Tools> Set Card Unprinted ImageWare solution: Imageware offers a product called Guard Card/GuardTool as an add-on module. It can use the Microsoft Access for EPI Database by importing the data from the ContinuumDB. The personnel requiring updated badges are in this db and then this tool can be used to setup a batch print specifying a template. EPI software would then match personnel to one of the 4 templates and batch print them.  Note: Product Support has not used Guard Card/Guard Tool and does not support it. Contact ImageWare with any questions http://www.iwsinc.com/
View full article
Picard Product_Support
‎2018-09-11 08:36 AM

Labels:
  • Andover Continuum
1744 Views

Cannot access DOS applications such as XPSI or PSI from within Network 8000 HOST system

Issue Error message displayed when booting the Network 8000 HOST computer indicating that the DOS file system cannot be initialized or a message displayed indicating that QDOS file is busy.  If these type of messages are displayed while the HOST system is booting, the DOS applications including PSI will not be available from within the HOST system. Product Line Other, TAC IA Series Environment Network 8000 HOST Software versions 6.x or 7.x Cause During bootup, the HOST software initialization checks for the presence of a PC-DOS partition on the computer's hard drive. If this PC-DOS partition is found, the command files needed to access PC-DOS are created or modified based on the partition number containing the PC-DOS operating system.  If the system is physically rebooted by power cycling or a power fail occurs, one or both of the PC-DOS control files may be left in an unusable state. Resolution The following steps can be used to correct this issue. Exit the Host by entering a q at the Host Login. At the QNX Login enter superman for both user and password. At the $ prompt enter the following four commands, pressing the Enter key at the end of each command: chattr /cmds/start_dfs s=-b chattr /net_8000_cmds/mount_xdos s=-b frel / cmds/start_dfs frel /net_8000_cmds/mount_xdo Re-boot the HOST
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • TAC IA Series
973 Views

Bindings to PVB and PVR blocks are lost when upgrading AS.

Issue Bindings to PVB and PVR blocks in function block programs are lost after upgrading from 1.3 to 1.4.1. Environment StruxureWare Building Operation 1.4.1 Cause Text from Release notes for 1.4.1, page 38 10.2.2 Bindings to Public Variables and Public Constants in Function Blocks Bindings to Public Constants and Public Variables will be lost after upgrade from 1.3 to 1.4.1. The names of these Public Constants and Public Variables will be listed in the Conversion log produced by the 1.4.1 Device Administrator at the upgrade. Resolution After upgrade to 1.4.1 do the following: Locate the Public Constants and the Public Variables listed in the Conversion log. Select the Function Block Program that includes Public Constants or the Public Variables listed in the Conversion log and open the Edit Bindings View. Lost bindings will be displayed with: "Invalid- Variable not allowed to have a reference" Make a note of these bindings. Quit the Bindings View. Select and Edit the Function Block Program(s) that include the Public Constants or Public Variables, move a Function Block slightly to enable an insignificant change of the program to be discovered by the compiler. Save the Function Block program (the program then compiles again). Open the Binding View and re-bind the lost bindings. You will now also be able to select in which direction the value should be transferred. Save the bindings.
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • EcoStruxure Building Operation
1312 Views

What is the UI input impedance of a MNL-10Rxx / -15Rxx / -20Rxx controller configured as voltage input?

Issue Specifying engineer wants to know the input impedance of the voltage inputs on the MNL-10Rxx / 15Rxx / 20Rxx controllers.  This information is not in the data sheet. Environment MNL-10Rxx controller MNL-15Rxx controller MNL-20Rxx controller Cause Job specification requirement Resolution The minimum input impedance for a MNL-10Rxx /-15Rxx / -20Rxx  UI configured as a voltage type input is 20K ohms.
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • TAC IA Series
782 Views

Function Block Editor does not open

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue Function Block Editor does not open. Product Line EcoStruxure Building Operation Environment SmartStruxure Function Block Editor Cause There could be many reasons but in one of the case we found a malware called "sprotector.dll" somehow trying to hook into the Function Block Editor dll's. This malware is then crashing and prevents Function Block Editor from starting. SProtector.exe is typically added when you install another free software (video recording/streaming, download-managers or PDF creators) that had bundled into their installation this program. Resolution Reinstall this computer's Operating System completely, if that's not an option you can read more about how to remove "sprotector" here: http://malwaretips.com/blogs/sprotector-exe-virus-removal/
View full article
Picard Product_Support
‎2018-09-07 10:22 AM

Labels:
  • EcoStruxure Building Operation
1651 Views

CRN certificate for DWA pockets

Issue Is there any CRN (Canadian Registration Number) available for the Satchwell DWA pockets used for STP sensors? Environment Satchwell DWA Pocket STP Cause For some applications, a CRN number is requested for components that are part of a pressurized system.  Resolution Unfortunately, no CRN numbers or certificates are available for the DWA pockets.
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • Field Devices
970 Views

Distribution Server MFC error, Application has stopped

Issue CX Controller and children i2 devices moved from one DB to another via ASCII dump file. Now when reloading the CX without the children i2 devices getting MFC error on reload of Controller when the IE table is being reloaded. Environment CyberStation CX controller I2 Infinet devices Cause Because all the controllers have been moved to a new DB the information in the  IE table in the I2 devices is invalid. Resolution Must reload the CX including its children i2 devices, this will ensure that a new IE table is sent to all devices as the devices will be reset and reloaded.
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • Andover Continuum
1615 Views
  • « Previous
    • 1
    • …
    • 478
    • 479
    • 480
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of