What is the UI input impedance of a MNL-10Rxx / -15Rxx / -20Rxx controller configured as voltage input?
  • What is the UI input impedance of a MNL-10Rxx / -15Rxx / -20Rxx controller configured as voltage input?
  • sesa116868
    sesa116868
‎2018-09-06 09:54 AM
Specifying engineer wants to know the input impedance of the voltage inputs on the MNL-10Rxx / 15Rxx / 20Rxx controllers.  This information is not in the data sheet.
MNL-10Rxx controller
MNL-15Rxx controller
MNL-20Rxx controller
Job specification requirement
The minimum input impedance for a MNL-10Rxx /-15Rxx / -20Rxx  UI configured as a voltage type input is 20K ohms.
  • TAC IA Series
  • 14909