Issue
The Enterprise Network Server is licensed for 3 subordinates but when trying to add one it faults with the message "exceeded device limit of three"?
Environment
G3 Enterprise Network Sever
Cause
If stations had been added to the Niagara Network in the Enterprise Network Server and then deleted the subordinate count in the license does not reset.
Resolution
Restart the station and the subordinate count in the license will be reset to the correct number and allow the addition of more stations if the limit has not been reached.