Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,854
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 11
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 461
    • 462
    • 463
    • …
    • 509
  • Next »

Does the damper actuators (MDxx) have any controller functionality built in?

Issue When retrofitting a site from brand x to Schneider Electric products, the controlling equipment my be designed differently between brands. Environment MD5 MD10 MD20 MD40 AF LF Damper actuator Cause Built in controller functionality. Resolution The MD/AF/LF series damper actuators does not have any built in controller functionality. All control signals must be provided from another source.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Field Devices
832 Views

Language Pack for each release of SmartStruxure

Issue Language Packs are required for each new release of SmartStruxure Environment EcoStruxure Building Operation Cause On each Change of revision, Maintenance, Service Pack, Hotfix or New Release requires the need for new Language Package Resolution The Language Pack is built for each specific version of Building Operation. There must be a language pack specifically built for each build, i.e., for 1.5.0.3003 you need a language pack built for that specific hotfix 1.5.0.3003 version. Example: One language pack is needed for Building Operation 1.5 and another language pack is required for Building Operation 1.5.1. Language Packs are available on the Exchange Extranet   For further information on Language Packages and how to install then refer to the Online Help Topic; Language Packages For more information on creating specific Language packages, please contact your corresponding regional category manager via the following email addresses: Americas: Americas.EcoStruxureBuilding@schneider-electric.com  EMEA: EMEA.EcoStruxureBuilding@schneider-electric.com  Asia Pacific: AsiaPac.EcoStruxureBuilding@schneider-electric.com
View full article
Picard Product_Support
‎2018-09-11 04:27 AM

Labels:
  • EcoStruxure Building Operation
1421 Views

Prevent a user to acknowledge certain alarms?

Issue Is it possible to prevent a user to be able to acknowledge certain alarms? Environment StruxureWare version 1.3 SP1 Cause It is possible to prevent a user group from acknowledge any alarms via the "Command permissions" in the Software permissions but when doing that the users can not acknowledge any alarms.   Resolution  To prevent a user from acknowledge certain alarms is to make the alarm, "read only" in the Software permissions for this user. 
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • EcoStruxure Building Operation
980 Views

Showing Outdoor air temperature on STR350

Issue How to show the Outdoor temperature on STR350? Environment STR350 Cause By the use of the variable nviOutdoorTemp, it is possible to show the outdoor temperature on the STR350 device. The outdoor temperature will be shown when you press the selection button. Resolution Make a binding for the outdoor temperature to the variable nviOutdoorTemp on the STR350 device.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • TAC Vista
914 Views

What is the working range for a thermistor temperature sensor?

Issue What is the temperature reading range for the STP500? Environment All Continuum controllers STP500 range STX500 range STD500 range Cause Clarification on read range required. Resolution When connected to a Continuum controller the operating temperature range is: -30°F to +230°F, -34°C to +110°C For readings outside this range, an active sensor with a 4-20mA or 0-10V output should be used.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
  • Field Devices
937 Views

An Epibuilder Plugin is necessary for some badging devices to work

Issue For EpiDesigner or EpiBuilder to work with some devices a plug-in needs to be purchased. Environment Continuum EpiBuilder EpiDesigner Windows XP Windows 7 Windows Server 2003 Windows Server 2008 Cause Epibuilder will not communicate with some approved devices without purchasing a special plug-in. Resolution ImageWare is the third party company that Continuum integrates with for badging and there are a number of devices that require a plug-in to work. Check the following web page for a list of tested and supported items and if the device indicates plug-in, then purchasing a plug-in is required. https://support.iwsinc.com/about/support/epi_builder/ The plug-in can be purchased through a ImageWare partner. https://www.iwsinc.com/partners/ Schneider Electric does not sell the plug-ins and has no access to any serial numbers that may be prompted for during the installation.
View full article
Picard Product_Support
‎2018-09-11 02:30 AM

Labels:
  • Andover Continuum
1219 Views

B4920 analog inputs read 8.6-8.9 volts instead of 10 volts for full scale

Issue analog input shows 8.6-8.9 volts instead of 10 volts Environment B4920 Cause The pull up resistor when disabled will drop the top end voltage slightly Resolution Pull up resistor on = 10 volts top scale Pull up resistor off = 8.6-8.9 volts top scale (by design) 
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
1087 Views

Personnel Profiles are adding areas that are not included in the profile.

Issue Users are adding areas to a person which should be blocked by a security level. Environment Continuum V1.93, V1.94 Cause Object level security is allowing the personnel profile to attach areas that should be blocked. Users with limited access to the sites areas are having additional areas added when applying a profile. No problems are encountered if no object level security is applied to the areas. Resolution This issue is resolved in V1.94 SP1 release of Cyberstation.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
966 Views

What LDAP sources can the Personnel Import Utility interface to?

Issue Do we support LDAP sources other than Microsoft Active Directory? Such as interfacing to Oracle Databases, OpenLDAP, Apple LDAP, etc… Environment Continuum Personnel Import Utility Cause Customer wants to use an LDAP source other than  Microsoft Active Directory. Resolution The only LDAP scenario that has been tested for was interfacing with Microsoft Active Directory, no other LDAP source has been tested or qualified at this time. Other LDAP sources may work but as these have not been qualified we have no way of knowing for sure.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
1139 Views

Can Personnel be deleted or disabled in Continuum utilizing the PIU and a third party system?

Issue Can Personnel be deleted or disabled in Continuum utilizing the PIU and a third party system? Environment Continuum Personnel Import Utility LDAP Cause Not sure what can be accomplished with the PIU to manage Personnel changes. Resolution The Personnel Import Utility, with the help of a transformation file, can be used to disable Personnel records in Continuum. This can be accomplished with an interface using LDAP, CSV, or XML. One method would be to use the expiry date field to disable Personnel Access.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
1281 Views

How to use values from a modbus device in a Xenta 7xx menta program

Issue How to use values form a modbus device in a Xenta 7xx menta program Environment TAC Xenta 731, TAC Xenta 721, TAC Xenta 711, TAC Xenta 701 TAC Xbuilder Cause Need to bring in values from a modbus device to a Menta application in the Xenta server. Resolution Create a PVR (or PVB,PVI depending of datatype of the signal you are bringing is) and make it public in the Menta application. Create a connection object in Xbuilder, connect the "from" to the modbus signal, connect the "to" to the PVR block. Now the value from the modbus device will be represented in the Menta application by the PVR block.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • TAC Vista
2049 Views

Is it possible to run Continuum in the video server box?

Issue Site is using Pelco video server that runs in the same OS as Continuum, to minimize cost they want to run Continuum in the video server machine. Environment CyberStation Various Pelco video servers Cause Cost Resolution While it is technically possible to have Continuum run in the same machine as the Video server it is not recommended. Some of the possible problems that may arise are... 1. Performance issues 2. Compatibilities issues, some files required by both Continuum and the video server may have different version requirements.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • Andover Continuum
954 Views

Forta series actuators with IP65

Issue Is it possible to order a Forta actuator with IP class 65? Environment Forta series actuator M400 M800 M1500 M3000 Cause Some environments are requiring a higher than normal IP rating. Resolution Unfortunately the design of the Forta actuators are only IP classed to IP54. No IP65 version is available. An additional weatherproof bag may be added to cover the actuator. However, such bags needs to be purchased from other sources as they are not part of our portfolio.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • Field Devices
906 Views

STR1xx spare parts availability

Issue Sometimes internal parts of the STR1xx wall modules are broken due to excessive force on the adjustment wheel. Environment STR1xx 004600100 STR100 004600110 STR100 004600200 STR101 004600300 STR102 004600700 STR103 004600400 STR104 004600500 STR106 STR106-B STR106-3 004600600 STR107 Cause Internal spare parts request Resolution Unfortunately, we do not have any spare parts listed for the STR10x wall modules.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • Field Devices
940 Views

Max Close Off pressure

Issue How do I find the max Close Off pressure for a certain valve/actuator combination? Environment Valves Actuators Cause The max defined Close Off pressure is important when choosing the correct valve/actuator combination for an installation. Resolution The max Close Off pressure is defined in charts or graphs in each valve series data sheet.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • Field Devices
1163 Views

Controller TAC213

Issue TAC213 is obsolete and needs replacement Environment TAC213 0803097005 Cause Obsolete controller needs replacement Resolution TAC213 is obsolete since many years. No replacement product is available.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • Field Devices
  • TAC Vista
983 Views

"ERROR: Non-activation-capable daemon activation invoked with non-client-request event type"

Issue The license log from the license server can occasionally display the following message: "ERROR: Non-activation-capable daemon activation invoked with non-client-request event type" Environment Vista and Flexnet Licensing Cause There is no known cause. Typically, it is logged once daily in the Debug.log file right after midnight. Resolution Acresso support has recognised this as a bug in FLEXnet. There is no implication that this error message impacts your license server usage or performance. This error is benign and not known to cause licensing problems.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1228 Views

Logs in the UNC are not archiving to the Enterprise Server

Issue Logs in the UNC are not archiving to the Enterprise Server Environment I/A Series R2 Universal Network Controller (UNC) and Enterprise Server Cause The UNC station and the Enterprise Server station have their LogService 'archiveMode' property set to 'archive_disabled'.  Resolution Change the LogService 'archiveMode' in both the UNC station and the Enterprise Server station.  1. Set the UNC station's LogService 'archiveMode' to 'archive_remote'. The 'archiveAddress' property should have 'Supervisor' checked.  2. Set the Enterprise Server station's LogService 'archiveMode' to 'archive_local'. (The “archive_local” selection is valid only if the station is running the DatabaseService) The following have to be also correct in order for log archiving to happen: AddressBook entries should be properly setup in the Enterprise Server and UNC stations. Refer to Page 1-15 and 1-16 of the Niagara Standard Programming Reference for further information.  Supervisor checkbox in the UNC's LogService 'archiveAddress' property should be checked. In the Niagara Log Object properties, the 'archiveSetup' property should have 'nearFull' or 'daily' checked. It is recommended that both of these be checked. 
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • TAC IA Series
866 Views

Not possible to log on to Enterprise Server from Workstation when regional settings are Arabic or Saudi Arabia

Issue When using a Windows 7 PC with regional settings set to Arabic or Saudi Arabia it is not possible to log on to ES from Workstation Environment StruxureWare Building Operation Workstation 1.3 Cause On a Windows 7 PC with .NET 4.0 installed if the regional settings are Arabic or Saudi Arabia a user cannot log on to the Enterprise Server from Workstation. This is not a problem with Webstation. Resolution This is only an issue with Windows 7 with .NET 4.0 which is the currently supported configuration (April 2013). The solution is to upgrade to .NET 4.5 or if required use Windows XP SP3 operating system. This has been tested on released version 1.3 and also 1.3.0 SP1 (build 1.3.0.10104-SP1).
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • EcoStruxure Building Operation
1320 Views

DC1100 / DC1400 with more than 2 boilers

Issue Can the DC1100 / DC1400 serve more than 2 boilers Environment DC1100 DC1400 Cause Can the DC1100 / DC1400 serve more than 2 boilers? Resolution The DC1100 or DC1400 is primarily designed for a 1 or 2 boiler installation. However in the case of 3 boilers. Note, 2 additional relays are required: Wire Boiler 1 to Boiler 1 terminals. Wire Boiler 2 to Boiler 2 terminals. Wire the coil of the 1st 230Vac relay to Boiler 1 terminals. Wire the coil of the 2nd 230Vac relay to Boiler 2 terminals. Either wire the relay contacts in parallel or in series, the feed for each contact will be wired from the Boiler 1 and Boiler 2 terminals respectively on the controller, the output of the relay contacts will be wired to Boiler 3. This is a workaround and does have its disadvantages: Boiler 3, when wired in parallel will always be a Lead Boiler and will do more work or when wired in series it will always be a Lag Boiler and will do the least work. In the case of 4 boilers: Wire the boilers in pairs to each boiler output on the controller. Note, the boilers will lead or lag in pairs. In the case of 5 boilers: Adapt both the solutions above.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • Field Devices
2443 Views
  • « Previous
    • 1
    • …
    • 461
    • 462
    • 463
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of