How to use values form a modbus device in a Xenta 7xx menta program
TAC Xenta 731, TAC Xenta 721, TAC Xenta 711, TAC Xenta 701
TAC Xbuilder
Need to bring in values from a modbus device to a Menta application in the Xenta server.
Create a PVR (or PVB,PVI depending of datatype of the signal you are bringing is) and make it public in the Menta application.
Create a connection object in Xbuilder, connect the "from" to the modbus signal, connect the "to" to the PVR block.
Now the value from the modbus device will be represented in the Menta application by the PVR block.