Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2197 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 35
    • 36
    • 37
    • …
    • 110
  • Next »
Label: "Andover Continuum" Show all articles

Second Security Key disables one or more features of the first Security Key on the same computer

Issue CyberStation and webClient on same computer. Second Security Key disables one or more features of the fist Security Key Product Line Andover Continuum Environment Andover Continuum CyberStation Andover Continuum webClient Cause Second Security Key inserted into USB port on workstation or only one computer to use. Resolution Only one Security Key (dongle, USB Key) per workstation(PC Computer). It is required that the key be installed to run the Continuum Cyberstation or WebClient server. Never install Cyberstation and webClient on the same workstation. Even on a LAN environment, there needs to be separate computers for Cyberstation and Webclient.  Note: webClient has some services disabled to allow for a more robust web capabilities. To see what is enabled on a Security Key, check out How to identify what is enabled on a Continuum Security Key.
View full article
Picard Product_Support
‎2018-09-07 04:20 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:19 AM

Labels:
  • Andover Continuum
1744 Views

Personnel does not have access. Invalid Attempt messages stating "Personnel record is not yet active" seen in the Access Events

Issue Personnel does not have access. Invalid Attempt messages stating "Personnel record is not yet active" seen in the Access Events. Product Line Andover Continuum Environment Continuum Access Control Cause Personnel object Activation Date attribute is set to a future time. Resolution Open the Personnel object and confirm the Activation Date and Expiration Date fields are realistic. Make sure the Activation Date is in the past. Check that the time on the Controller and Cyberstations are synchronised properly. See Configure Time Zone and UTC Offset settings so that time is synchronized across your system for how.
View full article
Picard Product_Support
‎2018-09-11 07:42 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:10 AM

Labels:
  • Andover Continuum
1804 Views

WebPinpoint crashes on Failed to call piLiveData>GetLiveData(). AccdataServices has an error

Issue WebPinpoint crashes on "Failed to call piLiveData>GetLiveData(). AccdataServices has an error" on both WebServer and Client PCs. Product Line Andover Continuum Environment WebClient IIS WebPinpoint Pinpoint  Cause The asp_net account does not have permission to access the ILiveData interface. ILivedata is an internal engine that WPinpoint uses for polling points values.   Resolution In Workstation Preferences on the Web Server, increase the value of WPinPoint Continuous Polling Rate until  from crashes no longer occur.  If this is for a Windows Server 2008, Windows 7 or Windows Vista, make sure the web.config file has been edited. See also Error: "DNWacserverFactory/WACServerFactory.soap" when accessing Webclient 1.9x Pinpoint.
View full article
Picard Product_Support
‎2018-09-10 03:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:08 AM

Labels:
  • Andover Continuum
1890 Views

Xdriver enabled on Comm port, but no xdriver option list down for the comm port type

Issue Xdriver is enabled,   Open the BCX1 editor, click "options" tag, display comm port attribute as"Xdriver comm1: 00000009", but there is no "xdriver" listed from the drop down menu when click the arrow on the right of default type of the comm port. Product Line Andover Continuum Environment BCX1-CR-X, 4.500065 Cyberstation 1.81 Cause Continuum support xdriver with BCX1-CR(BCX4040) from 1.82, any version earlier than 1.82 not support xdriver with BCX1-CR controller. Resolution Upgrade all the Cyberstation to 1.9X. To determine if a controller comm port is Xdriver enabled, refer to Determine if a controller comm port is Xdriver enabled.
View full article
Picard Product_Support
‎2018-09-11 07:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:55 AM

Labels:
  • Andover Continuum
1917 Views

Database size limitation and recover options on a Single User system in Continuum

Issue Is there a limitation to the size the database can be on a Single User system in Continuum? Product Line Andover Continuum Environment Single User Continuum system MSDE database Cause Microsoft has put a limitation in the size of the MSDE database. Once you hit this limitation your Single User Continuum system will not operate properly. Resolution The size limitation is 2 Gb. It may be possible to recover after hitting this limit by removing un-needed log entries from the database, but this is not always a guarantee you will be able to recover the database. Another way to recover from this is to back up the database, if you can, and restore it to standard SQL installation. From this point you can remove any unwanted logs and shrink the database. Then you can back up the database and restore it back to the Single User system. Another way to recover from this is to back up the database, if you can, and restore it to standard SQL installation and convert the Single User system to a LAN installation. Finally if all the above do not work for your system you will have to restore from the last known good backup of the database. See Microsoft Database size Limitations and Continuum for SQL Express information.
View full article
Picard Product_Support
‎2018-09-07 12:45 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:52 AM

Labels:
  • Andover Continuum
2341 Views

Method to disable credential access on doors at different controllers from a single variable

Issue How to disable credential access on Doors at different controllers using a single variable. Product Line Andover Continuum Environment Continuum Access Control Cause Require a method of securing multiple Doors at the same time. Resolution The best way to secure a number of Doors from a single variable is to use the Door Force Lock Schedule attribute in the Door object. This is accomplished by adding a numeric to the attribute on the Options tab of the Door object; IMPORTANT: The attribute name Door Force Lock is misleading, it DOES NOT lock the door in any way, all it does is disable credential access at the door. For Area/Door Lockdown refer to the linked KB article And also on the Entry Reader or Exit Reader tabs, ticking the checkbox under either Normal and/or Comm Fail for Door Forced Lock Schedule. Setting this Door Force Lock Schedule field to a local or remote InfinityNumeric point will provide the following conditions: When the Numeric is on, access is permitted to all personnel by card swipe and/or keypad entry. (Allow use of the door.) When the Numeric is off, card reader and keypad access are denied to all personnel. (No Access) You could have this numeric located in a central controller and all the rest of the controllers reference this numeric from the Door objects. No other points or plain English is required. If you want to ensure that the updates are received, you can force the IE entry for this numeric to update on a regular interval, see Use just one schedule to control doors or access to areas across different controllers that discusses how to accomplish this.  
View full article
Picard Product_Support
‎2018-09-11 09:16 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:48 AM

Labels:
  • Andover Continuum
1935 Views

Alarm escalation in Continuum

Issue How to do alarm escalation in Continuum? Product Line Andover Continuum Environment PEAlmFunction, PERtnFunction Cyberstation Alarm Workstation PE function Cause The customer requires the ability to time how long an alarm is active, and based on its status (acknowledged-unacknowledged), escalate the active alarm, by email or other means. Should the alarm be acknowledged in time, the escalation does not occur. Resolution One method is to use the PEAlmFunction and PERtnFunction in a Workstation Program to capture the various alarm conditions off the alarm stack to trigger the activity that you want. As an example, the PEAlmFunction could be used to initiate a timer for the alarm by recording the time of the alarm and the alarm point. The PERtnFunction is then used to clear this recorded information if the alarm is acknowledged. A Workstation program is then used to constantly monitor this alarm information and comparing the recorded alarm time to the current time, if this is above the escalation time then a numeric is set to trigger another alarm that is then escalated. For details on how to configure the PEAlmFunction and PERtnFunction, consult Can Plain English interact with the Continuum Alarm Engine?
View full article
Picard Product_Support
‎2018-09-11 07:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:47 AM

Labels:
  • Andover Continuum
1859 Views

Getting "Installation Error!" with "permission was denied on the object" or "you do not have permission" from database initialization

Issue Database initialization completes with errors Product Line Andover Continuum Environment Cyberstation installation Cause When running database initialization you will need full access to all of the database. Otherwise you may see errors similar to the following: Installation Error! <[Microsoft][ODBC SQL Server Driver][SQL Server]The SELECT permission was denied on the object 'syscategories', database 'msdb', schema 'dbo'.> Installation Error! <[Microsoft][ODBC SQL Server Driver][SQL Server]Cannot drop the procedure 'dt_IsColumnDifferent', because it does not exist or you do not have permission.>   Resolution Ensure that the Andover97 account has DBO privilege to the ContinuumDB, if not run the "Change DB Owner" query to restore Andover97 as the DBO, see Unable to Initialize Continuum Database following installing no SQL instance.   The above errors relate to setting up the SQL Server Agent Jobs that are held in the MSDB part of the database. Check that Andover97 does have the user mapping to this part of the database as per the following screenshot:     Also ensure your Windows User account has the required Administrator privileges to allow full access to the SQL database and its files.
View full article
Picard Product_Support
‎2018-09-11 06:00 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:43 AM

Labels:
  • Andover Continuum
2207 Views

MFC errors when starting or running Cyberstation or Webclient

Issue MFC errors when starting or running Cyberstation or Webclient Product Line Andover Continuum Environment Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Windows 10 Windows Server 2012 Cause Microsoft Function Class (MFC) errors are typically caused by missing, damaged or altered files that an application is looking for and is having problems using. Resolution There can be a number of reason why MFC errors are being received. Here are a few causes related to Cyberstation startup. Check the Continuum compatibility matrix. If you are using a version of Windows Operating System that has not been qualified for a specific version (i.e. Windows XP SP2 with 1.93) then this can cause MFC errors. Viruses and Malware can also affect MFC files. Be sure to run both types of scans on Cyberstation, but this should be done after the Cyberstation or Webclient PC has been installed. If these types of products are active during an install, they can flag some of the files that would normally get installed as suspect and cause problems with the operation of Cyberstation even if it appeared that the installation was successful. Removing Continuum, rebooting, running scans and then disabling the active scans at the time of the Cyberstation install will often resolve these issues. Windows XP, Vista and Windows7 have restore points that you can sometimes go back to in order to restore to a point earlier where the MFC errors were not happening. As a last resort, you may need to reformat the hard drive on the PC, reinstall the Windows Operating System including the appropriate service packs and hotfixes and then install Cyberstation or Webclient. Links to other MFC related articles: MFC errors on Continuum startup after moving a database to another PC MFC error on Continuum startup or Continuum won't start on HP PC Running a listview is giving a MFC error
View full article
Picard Product_Support
‎2018-09-06 01:17 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:34 AM

Labels:
  • Andover Continuum
2265 Views

Configuration for extended logs in Continuum

Issue How to set up extended logging. Product Line Andover Continuum Environment Continuum Cyberstation Extended Log Cause Configuration of extended logging. Resolution Sample configuration for extended logging. This example would create enough entries for a 24 hour period. Create an Infinity Numeric Select the logs tab Number of entries (96) Type will be LogInstantaneous (Stores the current value of this point at the beginning of every interval) Interval will be 15 minutes (15 minutes in a 24 hour period is 96 which is what we set for the Number of entries) By default the Workstations are setup for 5 minute checks to the controllers to see if there are extended logs to enter into the database. For more in-depth configuration of extended logging, please review Extended Logs in the Continuum Online help system.  For performance and load balancing please see Extended Logging gaps, performance and load balancing.
View full article
Picard Product_Support
‎2018-09-07 06:36 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:30 AM

Labels:
  • Andover Continuum
2444 Views

Downgrade SQL 2008 to SQL 2005, What version is used?

Issue Downgrade SQL 2008 to SQL 2005 Restore from SQL 2008 to prior version. Product Line Andover Continuum, TAC INET, TAC Vista Environment SQL 2008 used by Building Management Software Cause Have database loaded on one machine using SQL 2008 and would like to move or change to SQL 2005 Resolution Golden Rule: A SQL 2008 database cannot be downgraded or restored to a SQL 2005 version. It is not possible to downgrade a database or a database backup. The SQL schema will not allow it.  For your current version of SQL: C:\Program Files\Microsoft SQL Server \80, \90, \100 Folders are the client tools. 80 = SQL Server 2000 90 = SQL Server 2005 100 = SQL Server 2008 How ever, it is not a rule. Since 2008 creates both 80, 90. The only way to find what versions are installed (besides regedit) is by the Sql Server Configuration manager.    For other SQL options related to I/NET, please visit SQL and version compatibility for Filemaster, Equalized Client, Remote Client, Limitations of SQL.
View full article
Picard Product_Support
‎2018-09-06 12:27 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:28 AM

Labels:
  • Andover Continuum
  • TAC INET
  • TAC Vista
2034 Views

No Webclient browser PC stand alone installation and what components get installed normally

Issue IT departments want to install just the client software without attaching to the webclient server and want to know if there is a way to accomplish this. Product Line Andover Continuum Environment webClient Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause Webclient deploys activex controls using several .cab file from the C:\program files\redist folder on the webclient server. These files must be delivered to the browser PCs with admin privileges on the client PC in order for webclient and webpinpoint to work. Here is a list of the .cab files and ActiveX controls that get installed AccWebUtils.cab - AccDotNetBootstrap Control, Crypto Class (Used for  regular webclient use) WebclientPinpointSetup.cab - PPBrowserMgr Control (WebPinpoint) WebclientVideo.cab - TACVideoControl.VideoControl (Viewing Video layouts) ** The other piece that doesn't get installed are the permissions for the caspol commands that must be set for zones in order to run schedules. See webClient schedules getting error 'request for permission of type' system.security.permissions or .net control error on Webclient reports related to webclient schedules and running the caspol commands 1.94 SP1 requires that Microsoft VC++ 2005 Redistributable SP1 x86 to be installed for webpinpoint, it prompts to install when accessing a graphic the first time Resolution There is no client side webClient PC installation. The method for delivering the necessary activex controls and files are triggered by the browser PCs access to the webclient server PC and then the files are delivered to the client.  Some IT departments use Microsoft  SMS or Active directory to deploy software in a locked down environment. To deploy webclient to these types of browser PCs, they would have to logon with Admin privileges to perform the one time install of these files. The only other method if the IT group has InstallShield or WISE package creation software would be to capture the browser PC installation and use the produced .msi file for client delivery. This is informational only and has not been tested by Schneider Electric.
View full article
Picard Product_Support
‎2018-09-06 11:37 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:26 AM

Labels:
  • Andover Continuum
2455 Views

Effects of Leap Years with schedules and BMS

Issue Effects of leap year with schedules and BMS Product Line Andover Continuum, TAC INET Environment I/NET Site Continuum Site Time, calendar, Gregorian Calendar Cause Leap year adjustment in calendar Resolution I/NET: I/NET will not be affected by Leap Year occurrence if DST and Time Sync is correct in the host computer. For Time Sync errors, please refer to Time Sync Error, Daylight Saving setup, please refer to Configuring Daylight Savings Time. Continuum: Continuum will not be affected by Leap Year occurrence to controllers or scheduling if the Cyberstation has the correct time. There have been no incidents in the past with regards to leap year. Leap year is no different than some months having 30 days, others having 31. More information on time sync of controllers check Time sync controllers to workstations. To sync Continuum to an external time clock read Synchronize Continuum system to external time clock.
View full article
Picard Product_Support
‎2018-09-10 08:51 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:15 AM

Labels:
  • Andover Continuum
  • TAC INET
2076 Views

Live Video or video preview is displaying as black using the Endura Continuum integration

Issue Cameras have learned in successfully but live video shows as black or the Video Administrator shows the preview as black. Product Line Andover Continuum, Pelco Environment Continuum Endura Windows XP Windows Vista Windows Server 2003 Windows Server 2008 Cause Live video is showing black because of a configuration issue. Resolution There can be a number of reasons why live video is showing as black in Continuum. Here are some steps to correct or troubleshoot this: Time between devices is not synced. Verify that the controller(InfinintySystemVariable Date), Cyberstation(DateTime Date), and the Endura system(SM) time are all synced. Video Driver or Card. To allow for Sarix cameras in 1.92 changes were made that could cause a standard VGA driver to not display video. Update the standard driver or change the video card. (Test with a different PC which uses a different card) Multicast traffic. Check that the switches on the LAN are broadcasting traffic using multicast. Run the Sherlock utility which is a free codec utility to determine the codec on the Cyberstation and send the results to Product Support. It can be found at the following web site: http://www.free-codecs.com/Sherlock_The_Codec_Detective_download.htm Ensure that the cameras were renamed from the default name in Endura (defaults to camera, but it's actually a null). Ensure that each camera has its own unique non-zero input/channel number. Both of these two items can cause the Continuum camera learn to not be successful and cause issue when trying to access video. Video.log files. Configure the video.log files per How to create a log file for troubleshooting video integration issues in Continuum. Send these files to Product Support for analysis.
View full article
Picard Product_Support
‎2018-09-07 06:51 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:25 AM

Labels:
  • Andover Continuum
  • CCTV
2607 Views

Datasheets, install guides and other information on HID Electronic Access Control products

Issue Where can I find datasheets, install guides and other documentation on the HID SmartID, iClass, HID Proximity and Indala Proximity cards and readers? Product Line Andover Continuum, Field Devices, TAC INET Environment Electronic Access Control cards and readers for Continuum and I/Net products. Cause Additional product information from HID may be required that is not available on Schneider Electric's own websites. Resolution Schneider Electric supply a subset of the full HID range of cards and readers and these are detailed in the Electronic Access Control Catalogue or see How to determine the part number for the card format required for part number information. For HID product information this can be directly downloaded from the HID Global website. This contains  datasheets, installation guides, application notes, feature lists, brochures and other documentation. HID also have a "Knowledge Center" website that allows you to search for product information and help: HID Knowledge Base. Information on the specific ranges can be obtained from the following links: SmartID: SmartID Cards iClass: iClass Readers iClass SE Readers iClass Cards HID Prox: HID Proximity Readers HID Proximity Cards Indala Prox: Indala Proximity Readers Indala Proximity Cards
View full article
Picard Product_Support
‎2018-09-10 05:06 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:19 AM

Labels:
  • Andover Continuum
  • Field Devices
  • TAC INET
3181 Views

Converting a Continuum Single user system to Continuum LAN

Issue What is the process for converting a Continuum Single User system to a Continuum LAN system. Product Line Andover Continuum Environment Continuum CyberStation ContinuumDB SQL Cause Site wants to upgrade from Continuum Single User system to a Continuum LAN System. Resolution PRELIMINARY WORK Order Continuum Key Upgrades from all Continuum CyberStation workstations and WebClient Servers. Coordinate with customers IT department Order all TCP/IP node addresses Coordinate the purchase and installation of all software Order all necessary domain accounts Make sure all domain accounts have sufficient permissions to support the installed systems. PREPARE THE NEW CONTINUUM DATABASE ON SQL SERVER Set up your server and install SQL Server 2005 or 2008. SQL must be configured with the proper collation sequence.  (See CyberStation SQL collation) SQL must allow Name Pipes (See After installing Continuum 1.93 LAN, failure to initialize a new database) Install CyberStation on a service Laptop or PC . Disable all virus protection software Disable all spyware software Disable all firewall software. Install Continuum CyberStation Run Database Initialization on service laptop Create new Continuum database..  NOTE: The new database should be given a name that differs from the existing database. Create the service Laptop workstation with a unique Device ID and Network ID. Launch Continuum Logon and verify that Continuum appears to be running normally. MOVE FILES FROM EXISTING SU WORKSTATION TO THE SQL 2008 SERVER Backup PinFiles on original stand alone Cyberstation and move them to New Graphics Files folder on the new database server. Backup Background image files on original stand alone Cyberstation and move them to the background image files folder under New Graphics Files on the new database server. Backup the existing database and move it to the backup folder under SQL on the new Database server. Restore backup to Continuum database in SQL on the new database server.. Shut down all the Cyberstation workstations that are attached to the old database. Change DB Owner Run query on new Continuum database Enter the text SP_ChangeDBOwner Andover97 Execute this query.   Query should return Success. Run Database initialization on the service CyberStation and update the new SQL 2008 Continuum database. Launch CyberStation on the service laptop and verify that the system is fully functional. Shut down service laptop. CONNECT EXISTING WORKSTION TO THE NEW DATABASE SERVER Startup Existing CyberStation PC Launch Database Initialization Under Server, Update the new Continuum database with the same information entered via the service laptop..  Under Workstation update the server information and apply. Launch Continuum. Configure Graphic File Location From Start Programs Continuum, run Pinpoint Under the View menu select Options. Enter the path on the new Continuum database server for the Graphic (Pin Files) Enter the path on the new Continuum database server for the Image files Enter the path on the new Continuum database server for the Background files Select Check and verify that no errors appear (Red X) Ideally uninstall SQL Express or MSDE or at least stop the service from running. Delete the Windows Scheduled tasks: CS_Distn, CS_Hrly, CS_ Minute as these are now performed by Jobs on the SQL server. Test all Continuum functionality. Setup a scheduled automatic db backup routine in SQL. Setup a scheduled trend log truncation routine in SQL.
View full article
Picard Product_Support
‎2018-09-09 05:04 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:13 AM

Labels:
  • Andover Continuum
1939 Views

Identify which DCOM permission are causing DCOM errors when trying to use WebClient

Issue Getting DCOM errors when trying to access WebClient and need to determine which of the various permissions have not been set properly. Product Line Andover Continuum Environment WebClient IIS Cause DCOM permissions have not been set properly. Resolution Open EventViewer, go to System Events, and note the DistributedCOM error. Open the error and find the CLSID that it is referring to. In the DCOM Config, look through all of the DCOM objects and find the one with the matching CLSID. Make sure that it has the correct permissions according the WebClient installation document. If this does not resolve the problem, you can also consult WebClient most common installation problems for further troubleshooting steps.
View full article
Picard Product_Support
‎2018-09-10 10:53 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:55 PM

Labels:
  • Andover Continuum
2752 Views

BACnet bCX schedules cannot be edited without an error

Issue BACnet bCX schedules cannot be edited without an error. Product Line Andover Continuum Environment Continuun bCX4040 Schedule Firmare v4.500082 Cause Following an upgrade to firmware v4.500082 the  Schedule end date year 2038 now enforced and schedule cannot be modified if the end (effective) date is beyond this Resolution For all schedules newly created or otherwise, the end (effective) date needs to be set to 2038 or earlier see Script Programs in Continuum compared to StruxureWare Building Operation and using floats (32 bits) and 64 bit numbers If the date is set after 2038 then an error is seen when trying to edit the schedule "An error code was returned from a BACnet operation, but the reason could not be determined."   Creating a new schedule with a date > 2038 can also give the error: " Error setting attribute 'DeviceID' An error code was returned from s BACnet operation , but the reason could not be determined " Defect was corrected in v4.500083
View full article
Picard Product_Support
‎2018-09-11 01:33 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:51 PM

Labels:
  • Andover Continuum
2494 Views

Default Device ID / Device Instance of SE7000 series BACnet controllers

Issue Without knowing the Device ID / Device Instance these devices cannot add to the MSTP network in the AS or ES. Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices Environment Automation Server Enterprise Server BACnet SE7000 Cause Only the MAC ID / Com Address is shown in the display but not the Device ID / Device Instance. Resolution SE7200x Models Default Device ID is set to: 72000 + MAC Where MAC is the current MAC address of the device. The device ID will also be upgraded as soon as there is a change to the device’s MAC. For example, when a SE7200F5045B controller with a MAC address of 41 is connected to a network, its default Device Name will be SE7200F5x45B-41 and its default Device ID will be 72041. SE73xxx Models Default Device ID is set to: 73000 + MAC Where MAC is the current MAC address of the device. The device ID will also be upgraded as soon as there is a change to the device’s MAC. For example, when a SE7300C5045B controller with a MAC address of 63 is connected to a network, its default Device Name will be SE7300C5x45B-63 and its default Device ID will be 73063. Click here for the Integration Manual. Please refer to the SE7300 series BACnet controller does not come online in StruxureWare Building Operation if SE7300 controller does not come online.
View full article
Picard Product_Support
‎2018-09-10 11:33 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:48 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
2737 Views

Error: "Unable to load the .Net control for this page." when trying to open a schedule or trend log in WebClient

Issue You get an error, "Unable to load the .Net control for this page." when trying to open a schedule in WebClient. Product Line Andover Continuum Environment webClient Cause The problem is that the .Net zone permissions are not set on the browser machines. Resolution Depending on the revision of the WebClient the procedure for correcting this on the browsing machines is different. If you are running WebClient version 1.73 or below then refer to the WebClient installation guide on setting the .Net zone permissions. If you are running WebClient version 1.74 or higher, which uses .Net 2.0, the procedure is different. Below is the procedure that will need to be performed on the browser machines at the command prompt to set the .Net Zone Permissions for .Net 2.0. The following command will add FullTrust to the Internet_Zone in DotNet 2.0: C:\WINDOWS\Microsoft.NET\Framework\v2.0.50727\caspol.exe -m -addgroup Internet_Zone -zone InterNet FullTrust -name FullTrust The following command will add FullTrust to the Trusted_Zone in DotNet 2.0 C:\WINDOWS\Microsoft.NET\Framework\v2.0.50727\caspol.exe -m -addgroup Trusted_Zone -zone Trusted FullTrust -name FullTrust This will result in output like: The operation you are performing will alter security policy. Are you sure you want to perform this operation? (yes/no) Then select Y and you should see: Added union code group with "-zone" membership condition to the Machine level. Success You should then be able to open the .Net 2.0 editors on your web.client browser machine. In some cases adding the webclient IIS PC to the trusted sites in the browser is needed Internet Explorer> Internet Options> Security> Click Trusted Sites> Click Sites Type in http://your server name/webclient and click Add (i.e your server name is specific to your install) Deselect the checkbox for 'Require server verification (https:) for all sites in this zone Click Ok, Ok Close explorer and access webclient schedules Note: Every browser PC that will be accessing schedules needs to have the caspol commands run on it. Download a batch file that can be run on each PC (Rename the .txt file to .bat and run at a DOS prompt  C:\> caspolwebclient.bat)   Note: When using 1.94 SP1 check the application pools .net version selected Name .Net Version ASP NET v4.0 4.0 ASP NET v4.0 Classic 4.0 Classic .NET AppPool 2.0 Default AppPool  2.0 WebClient  4.0 Note: If .net framework 4.5.x has recently been installed on browser PCs, see Webclient Cannot open .net editor with .NET Framework - 'There was an error trying to create the .NET control for this page'.
View full article
Picard Product_Support
‎2018-09-07 12:44 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:44 PM

Labels:
  • Andover Continuum
2189 Views
  • « Previous
    • 1
    • …
    • 35
    • 36
    • 37
    • …
    • 110
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore