How to set up extended logging.
Andover Continuum
  • Continuum Cyberstation
  • Extended Log
Configuration of extended logging.
Sample configuration for extended logging.
This example would create enough entries for a 24 hour period.
  1. Create an Infinity Numeric
  2. Select the logs tab
  3. Number of entries (96)
  4. Type will be LogInstantaneous (Stores the current value of this point at the beginning of every interval)
  5. Interval will be 15 minutes (15 minutes in a 24 hour period is 96 which is what we set for the Number of entries)
By default the Workstations are setup for 5 minute checks to the controllers to see if there are extended logs to enter into
the database. For more in-depth configuration of extended logging, please review Extended Logs in the Continuum Online help system.
 For performance and load balancing please see Extended Logging gaps, performance and load balancing.