Converting a Continuum Single user system to Continuum LAN

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Converting a Continuum Single user system to Continuum LAN
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • JohnBoehmer
    JohnBoehmer

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1935 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Converting a Continuum Single user system to Continuum LAN

Picard Product_Support
‎2018-09-09 05:04 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:13 AM

Issue

What is the process for converting a Continuum Single User system to a Continuum LAN system.

Product Line

Andover Continuum

Environment

  • Continuum
  • CyberStation
  • ContinuumDB
  • SQL

Cause

Site wants to upgrade from Continuum Single User system to a Continuum LAN System.

Resolution

PRELIMINARY WORK

  1. Order Continuum Key Upgrades from all Continuum CyberStation workstations and WebClient Servers.
  2. Coordinate with customers IT department
  • Order all TCP/IP node addresses
  • Coordinate the purchase and installation of all software
  • Order all necessary domain accounts
  • Make sure all domain accounts have sufficient permissions to support the installed systems.

PREPARE THE NEW CONTINUUM DATABASE ON SQL SERVER

  • Set up your server and install SQL Server 2005 or 2008.
    • SQL must be configured with the proper collation sequence.  (See CyberStation SQL collation)
    • SQL must allow Name Pipes (See After installing Continuum 1.93 LAN, failure to initialize a new database)
  • Install CyberStation on a service Laptop or PC .
    • Disable all virus protection software
    • Disable all spyware software
    • Disable all firewall software.
    • Install Continuum CyberStation
  • Run Database Initialization on service laptop
    • Create new Continuum database..  NOTE: The new database should be given a name that differs from the existing database.
    • Create the service Laptop workstation with a unique Device ID and Network ID.
    • Launch Continuum
    • Logon and verify that Continuum appears to be running normally.

MOVE FILES FROM EXISTING SU WORKSTATION TO THE SQL 2008 SERVER

  • Backup PinFiles on original stand alone Cyberstation and move them to New Graphics Files folder on the new database server.
  • Backup Background image files on original stand alone Cyberstation and move them to the background image files folder under New Graphics Files on the new database server.
  • Backup the existing database and move it to the backup folder under SQL on the new Database server.
  • Restore backup to Continuum database in SQL on the new database server..
  • Shut down all the Cyberstation workstations that are attached to the old database.
  • Change DB Owner
    • Run query on new Continuum database
    • Enter the text SP_ChangeDBOwner Andover97
    • Execute this query.  
    • Query should return Success.
  • Run Database initialization on the service CyberStation and update the new SQL 2008 Continuum database.
  • Launch CyberStation on the service laptop and verify that the system is fully functional.
  • Shut down service laptop.

CONNECT EXISTING WORKSTION TO THE NEW DATABASE SERVER

  • Startup Existing CyberStation PC
  • Launch Database Initialization
  • Under Server, Update the new Continuum database with the same information entered via the service laptop.. 
  • Under Workstation update the server information and apply.
  • Launch Continuum.
  • Configure Graphic File Location
    • From Start Programs Continuum, run Pinpoint
    • Under the View menu select Options.
    • Enter the path on the new Continuum database server for the Graphic (Pin Files)
    • Enter the path on the new Continuum database server for the Image files
    • Enter the path on the new Continuum database server for the Background files
    • Select Check and verify that no errors appear (Red X)
  • Ideally uninstall SQL Express or MSDE or at least stop the service from running.
  • Delete the Windows Scheduled tasks: CS_Distn, CS_Hrly, CS_ Minute as these are now performed by Jobs on the SQL server.
  • Test all Continuum functionality.
  • Setup a scheduled automatic db backup routine in SQL.
  • Setup a scheduled trend log truncation routine in SQL.
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5174
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore