BACnet bCX schedules cannot be edited without an error
  • BACnet bCX schedules cannot be edited without an error
  • CraigEl
    CraigEl
  • PaulFr
    PaulFr
  • Dave_Shore
    Dave_Shore
‎2018-09-11 01:33 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:51 PM
BACnet bCX schedules cannot be edited without an error.
Andover Continuum
Continuun bCX4040 Schedule Firmare v4.500082
Following an upgrade to firmware v4.500082 the  Schedule end date year 2038 now enforced and schedule cannot be modified if the end (effective) date is beyond this
For all schedules newly created or otherwise, the end (effective) date needs to be set to 2038 or earlier see Script Programs in Continuum compared to StruxureWare Building Operation and using floats (32 bits) ...
If the date is set after 2038 then an error is seen when trying to edit the schedule
"An error code was returned from a BACnet operation, but the reason could not be determined."
Creating a new schedule with a date > 2038 can also give the error:
" Error setting attribute 'DeviceID' An error code was returned from s BACnet operation , but the reason could not be determined "
Defect was corrected in v4.500083